For diagnostic purposes, you can try back-flushing the liquid line, the condenser and the high pressure line. Disconnect each at both sides/ends.

If any are clogged, replace it. Plan on replacing the condenser as a likely step anyway. If it or the high pressure line is clogged, they will need to be replaced as neither can be effectively cleaned out.


 
Reply
Old Jun 19, 2023 | 04:13 PM
  #17  
HearseDriver's Avatar
HearseDriver
Tuned
10 Year Member
Liked
Loved
Community Favorite
Joined: Feb 2015
Posts: 323
Likes: 12
From: Tulare, CA
I have a dumb question for you. Is/was your truck operated in a dirty or dusty environment? The previous owner of my truck owned orchards and drove the truck through them a LOT. The dirt & dust plugged up the evaporator cooling fins. I don't know if this is your problem or not or can even be related to your issues. I do know it's not too difficult to check. The inner fender well has to come out and the evaporator case then splits in half to check. I did check mine not too long after I bought it to check on it and wash off the evap core. I do know if the evaporator is plugged the high side will be through the roof but that's all I know (or was told anyway) This info might not do you any good but it doesn't hurt to ask an A/C person.
 
Reply
Old Jun 19, 2023 | 04:18 PM
  #18  
sirdiealot's Avatar
sirdiealot
Thread Starter
|
Trailering
Joined: Jan 2021
Posts: 15
Likes: 0
Yeah I checked that yesterday . It was clean literally looked like it had just been cleaned
 
Reply
Old Jun 19, 2023 | 06:19 PM
  #19  
rvpuller's Avatar
rvpuller
Moderator
Veteran: Coast Guard
20 Year Member
Photogenic
Photoriffic
Joined: May 2004
Posts: 6,517
Likes: 917
From: Home Base Nebraska
Club FTE Gold Member
If you can flush through the evaporator and condenser and they are both externally clean and with a new orfice, can't remember if they have a filter dryer that should also be changed. Then your problem is the valves inside the compressor are bad. Bad valves will cause low suction pressure and high head pressure depending on what one failed.

Denny

 
Reply
Old Jun 19, 2023 | 06:22 PM
  #20  
DBGrif91's Avatar
DBGrif91
Cargo Master
15 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jul 2009
Posts: 2,541
Likes: 54
From: Des Moines
Originally Posted by sirdiealot
Well that didn’t fix it , after flushing the evaporator out and pulling a vacuum for 30 min I put in 33-35 oz of Freon while I was putting it in the pressure was at 45 low side 350 on the hi side , as soon as I finished the low side slowly dropped down to a -3 vacuum . I replaced the orifice tube again also . On the back side of the orifice (closest to evap) the line had frost on it but the large line coming out was not cold and the air wasn’t cold . Is that Saying the evap is plugged even after I flushed it ? Or is it something else plugged ?
What color was the orifice tube? OT’s are color coded - your truck should have had a red one - if the tube you first removed was any other color then it’s not the correct one.

In a properly charged and correctly operating system, the evaporator outlet line and the compressor suction line off the accumulator will both be relatively the same temperature.

The frost on the evaporator side of the orifice tube might be an indication that the incorrect tube is installed. If it is the correct tube, then most likely the evaporator is plugged.
 
Reply
Old Jun 20, 2023 | 04:14 PM
  #21  
sirdiealot's Avatar
sirdiealot
Thread Starter
|
Trailering
Joined: Jan 2021
Posts: 15
Likes: 0
It was a red tube
 
Reply
Old Jun 20, 2023 | 10:28 PM
  #22  
sirdiealot's Avatar
sirdiealot
Thread Starter
|
Trailering
Joined: Jan 2021
Posts: 15
Likes: 0
Ok this evening me and my 16yr old son unhooked the hoses to the condenser, evaporator and compressor isolating them and flushed them out . We then added 7 ozs of pag oil . It was a guess how much I lost when flushing out everything but it calls for 9 ozs of pag oil to total . We then pulled a vacuum of 29ish lbs for about a hour and 15 min on entire system . Let it set for another 20 min and no loss of vacuum . We added 3 12 oz cans I’d Freon , the system calls for 2 lbs 10 oz of Freon (42 oz’s ) at the I hooked up the 4th can and started to add the 1/2 of it and my son tripped on a hose and I went over to check on him. While I was doing that it emptied the 12 oz can so it now has 3 lbs of Freon in it . The compressor will run for 5 seconds and shut off for 2 seconds . Pressure on low side goes from 20-50 in that 5 seconds then takes 2 seconds to drop to 20 again . High side pressure goes from 175 -250 in that time period . Air is cooler but not cold . Do I need to take out the 6 ozs of Freon , or add more lol . I took a video of the gauges but not sure if or how I can share it here
 
Reply
Old Jun 21, 2023 | 12:15 PM
  #23  
DBGrif91's Avatar
DBGrif91
Cargo Master
15 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jul 2009
Posts: 2,541
Likes: 54
From: Des Moines
Where are you finding the capacity? In your first post you said it takes 34 oz - now you say it takes 42 oz.

According to prodemand.com it takes 45 oz.

If there’s no label under the hood, check the capacities and specifications page in the owner manual.

There is a little “wiggle room” on the capacity because the accumulator can store a certain amount of extra refrigerant, but if it’s significantly overcharged, the clutch on/off time and cooling effect you describe is an indicator of an overcharged system.

Verify the capacity before adding or removing from the system.

Originally Posted by sirdiealot
Ok this evening me and my 16yr old son unhooked the hoses to the condenser, evaporator and compressor isolating them and flushed them out . We then added 7 ozs of pag oil . It was a guess how much I lost when flushing out everything but it calls for 9 ozs of pag oil to total . We then pulled a vacuum of 29ish lbs for about a hour and 15 min on entire system . Let it set for another 20 min and no loss of vacuum . We added 3 12 oz cans I’d Freon , the system calls for 2 lbs 10 oz of Freon (42 oz’s ) at the I hooked up the 4th can and started to add the 1/2 of it and my son tripped on a hose and I went over to check on him. While I was doing that it emptied the 12 oz can so it now has 3 lbs of Freon in it . The compressor will run for 5 seconds and shut off for 2 seconds . Pressure on low side goes from 20-50 in that 5 seconds then takes 2 seconds to drop to 20 again . High side pressure goes from 175 -250 in that time period . Air is cooler but not cold . Do I need to take out the 6 ozs of Freon , or add more lol . I took a video of the gauges but not sure if or how I can share it here
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-1

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-2

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-3

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-4

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-5

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-6

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-7

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-8

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-9

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
Old Jun 21, 2023 | 01:30 PM
  #24  
sirdiealot's Avatar
sirdiealot
Thread Starter
|
Trailering
Joined: Jan 2021
Posts: 15
Likes: 0
Under the hood is where I found the 42oz . The first number I said it took I was going by what my son looked up . I should have double checked him but I didn’t .
 
Reply
Old Jun 22, 2023 | 09:18 AM
  #25  
rvpuller's Avatar
rvpuller
Moderator
Veteran: Coast Guard
20 Year Member
Photogenic
Photoriffic
Joined: May 2004
Posts: 6,517
Likes: 917
From: Home Base Nebraska
Club FTE Gold Member
Originally Posted by sirdiealot
Ok this evening me and my 16yr old son unhooked the hoses to the condenser, evaporator and compressor isolating them and flushed them out . We then added 7 ozs of pag oil . It was a guess how much I lost when flushing out everything but it calls for 9 ozs of pag oil to total . We then pulled a vacuum of 29ish lbs for about a hour and 15 min on entire system . Let it set for another 20 min and no loss of vacuum . We added 3 12 oz cans I’d Freon , the system calls for 2 lbs 10 oz of Freon (42 oz’s ) at the I hooked up the 4th can and started to add the 1/2 of it and my son tripped on a hose and I went over to check on him. While I was doing that it emptied the 12 oz can so it now has 3 lbs of Freon in it . The compressor will run for 5 seconds and shut off for 2 seconds . Pressure on low side goes from 20-50 in that 5 seconds then takes 2 seconds to drop to 20 again . High side pressure goes from 175 -250 in that time period . Air is cooler but not cold . Do I need to take out the 6 ozs of Freon , or add more lol . I took a video of the gauges but not sure if or how I can share it here
The only way to adjust your oil level is to flush the system and drain all the oil out of the compressor then add the recommended amount. A normally operating system has very little oil vapor out in the system, the oil belongs in the compressor not out in the system. A oil logged system will never operate properly and it will destroy the compressor because it can't compress fluids. Don't guess know for sure.

Denny
 
Reply
Old Jun 22, 2023 | 12:15 PM
  #26  
DBGrif91's Avatar
DBGrif91
Cargo Master
15 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jul 2009
Posts: 2,541
Likes: 54
From: Des Moines
FYI, oil is circulated through the system with refrigerant - it doesn’t just remain in the compressor except for 2-3 ounces, if that much. That’s why it’s recommended to add oil after the condenser, evaporator or accumulator are replaced - because it’s expected a certain amount of oil is trapped in them. The idea is to have at least some oil at every point in the system to ensure that the compressor stays adequately lubricated.

While it’s true that excessive oil can affect system operation, the accumulator is designed to store additional oil and meter it back to the compressor as refrigerant is pulled in. I’d have to find my old notes to be sure, but I recall learning that it takes something in the neighborhood of 1.5 times oil capacity to affect an accumulator based system.

Given the OP’s description, I think it’s unlikely that it’s overcharged on oil.

Originally Posted by rvpuller
The only way to adjust your oil level is to flush the system and drain all the oil out of the compressor then add the recommended amount. A normally operating system has very little oil vapor out in the system, the oil belongs in the compressor not out in the system. A oil logged system will never operate properly and it will destroy the compressor because it can't compress fluids. Don't guess know for sure.

Denny
 
Reply
Old Jun 23, 2023 | 05:11 AM
  #27  
Kbs117's Avatar
Kbs117
5th Wheeling
Joined: Oct 2012
Posts: 28
Likes: 3
Oil logged

Originally Posted by DBGrif91
FYI, oil is circulated through the system with refrigerant - it doesn’t just remain in the compressor except for 2-3 ounces, if that much. That’s why it’s recommended to add oil after the condenser, evaporator or accumulator are replaced - because it’s expected a certain amount of oil is trapped in them. The idea is to have at least some oil at every point in the system to ensure that the compressor stays adequately lubricated.

While it’s true that excessive oil can affect system operation, the accumulator is designed to store additional oil and meter it back to the compressor as refrigerant is pulled in. I’d have to find my old notes to be sure, but I recall learning that it takes something in the neighborhood of 1.5 times oil capacity to affect an accumulator based system.

Given the OP’s description, I think it’s unlikely that it’s overcharged on oil.
I see this all the time on older vehicles. The system has too much oil and cannot function. BLow everything clean again, (i use 91% rubbing alcohol and compressed air) and put it back together and add only freon. The compressor will have all the oil in it, the system needs. The oil is so thick it's slowing down the freon going through the orifice tube, causing the low side vacuum and the high side pressure. I get 20 a year in here doing it. Normally it destroys the compressor from high pressure, or blows the high pressure line. Some systems have a pop off valve on the compressor that will open at 600 psi and vent freon into the atmosphere. You almost had it the last time you blew everything clean, until you added the 9 Oz of oil back into the system. Your compressor is full of oil, it has all the system needs. Blow everything else clean and put 40 Oz freon in, and it will freeze your *** off.
 
Reply
Old Jun 23, 2023 | 03:32 PM
  #28  
rvpuller's Avatar
rvpuller
Moderator
Veteran: Coast Guard
20 Year Member
Photogenic
Photoriffic
Joined: May 2004
Posts: 6,517
Likes: 917
From: Home Base Nebraska
Club FTE Gold Member
Originally Posted by Kbs117
I see this all the time on older vehicles. The system has too much oil and cannot function. BLow everything clean again, (i use 91% rubbing alcohol and compressed air) and put it back together and add only freon. The compressor will have all the oil in it, the system needs. The oil is so thick it's slowing down the freon going through the orifice tube, causing the low side vacuum and the high side pressure. I get 20 a year in here doing it. Normally it destroys the compressor from high pressure, or blows the high pressure line. Some systems have a pop off valve on the compressor that will open at 600 psi and vent freon into the atmosphere.
​You almost had it the last time you blew everything clean, until you added the 9 Oz of oil back into the system. Your compressor is full of oil, it has all the system needs. Blow everything else clean and put 40 Oz freon in, and it will freeze your *** off.
Not much to add.
.
Denny
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
LAMADMAN
1999 - 2003 7.3L Power Stroke Diesel
20
Jun 23, 2023 05:20 AM
off2fsh
Excursion - King of SUVs
3
Mar 25, 2021 11:25 AM
F-250 WARHORSE
1987 - 1996 F150 & Larger F-Series Trucks
11
Jul 13, 2014 10:33 PM
samthelion
1987 - 1996 F150 & Larger F-Series Trucks
13
Jul 28, 2013 02:35 PM
Sport98
Explorer, Sport Trac, Mountaineer & Aviator
5
Jan 21, 2004 12:59 AM




All times are GMT -5. The time now is 05:15 PM.

story-0
Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-05-30 18:33:59


VIEW MORE
story-1
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-2
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-3
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-4
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-5
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-6
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-7
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-8
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-9
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE