I just love seeing how some of these conversations go sideways so fast.

In my new shop I'm doing the wiring so I'm tending to over do what I have. Labor and Industries has dictated that all my power in the shop must be in armor and metal boxes.

100 amp service tied into the house's input with a new 100 amp breaker. 1 1/2" conduit buried at 24" with #2 SER cable to feeder in the shop.

Lighting is 18, 4' LED shop lights with each line of 6 off of it's own dedicated 15 amp breaker. 12-2 in armor as required in Washington state L&I.

Front and back security lights off of their own 15 amp breakers and 12-2 in armor.

Electric outlets are wired with a max of 3 off of a 20 amp breaker. Again 12-2 in armor.

I have an 80 gallon commercial 5 HP compressor that I'm wiring on a dedicated hardwire with a disconnect switch between the breaker and the motor. I'll use 10 wire for that circuit. I'll pour a separate 6" pad and also make a separate enclosure outside of the shop so I don't have the noise.

I'm also adding a 50 amp RV plug for my trailer which will also have it's own 50 amp breaker 10-3 in armor.

I don't have a need for a drier or welder in the shop yet so that's not being done at least for now.

I have started on my CCTV and Ethernet to the shop, 3/4" conduit again at 24"

Maybe overkill but better safe than sorry.

If it's not enough I will listen and fix it.
 
Reply
Old Feb 7, 2021 | 06:08 AM
  #32  
JWA's Avatar
JWA
Fleet Owner
15 Year Member
Liked
Loved
Community Favorite
Joined: Aug 2010
Posts: 21,253
Likes: 1,656
From: Reynoldsburg, Ohio
^^^Your approach in general is the same path I'd go---I've heard that sort of approach as a "code + 1" scenario. Over the longer term your use of somewhat "better" than the minimum standard will serve you well I'm sure. Doing it once the right way would be the only way I'd want to go about this.

Having been in 100 or so different semi-commercial garages I've noticed a significant lack of electrical outlets as well as man doors---they're just never located in good locations IMHO. I guess my thoughts are convenience and practicality over one-time initial expense.
 
Reply
Old Feb 7, 2021 | 06:31 PM
  #33  
muhford's Avatar
muhford
Fleet Mechanic
10 Year Member
Liked
Loved
Community Favorite
Joined: Mar 2014
Posts: 1,269
Likes: 129
From: Missouri
Originally Posted by EDC8008
I just love seeing how some of these conversations go sideways so fast.
In my new shop I'm doing the wiring so I'm tending to over do what I have. Labor and Industries has dictated that all my power in the shop must be in armor and metal boxes.
100 amp service tied into the house's input with a new 100 amp breaker. 1 1/2" conduit buried at 24" with #2 SER cable to feeder in the shop.
Lighting is 18, 4' LED shop lights with each line of 6 off of it's own dedicated 15 amp breaker. 12-2 in armor as required in Washington state L&I.
Front and back security lights off of their own 15 amp breakers and 12-2 in armor.
Electric outlets are wired with a max of 3 off of a 20 amp breaker. Again 12-2 in armor.
I have an 80 gallon commercial 5 HP compressor that I'm wiring on a dedicated hardwire with a disconnect switch between the breaker and the motor. I'll use 10 wire for that circuit. I'll pour a separate 6" pad and also make a separate enclosure outside of the shop so I don't have the noise.
I'm also adding a 50 amp RV plug for my trailer which will also have it's own 50 amp breaker 10-3 in armor.
I don't have a need for a drier or welder in the shop yet so that's not being done at least for now.
I have started on my CCTV and Ethernet to the shop, 3/4" conduit again at 24"
Maybe overkill but better safe than sorry.
If it's not enough I will listen and fix it.
When they installed your new sub panel did they drive two 5/8" ground rods? (Or whatever code is in your area) Properly grounding a sub panel is very important.

Other notes. LEDs draw very little power and you could probably have them all on 1 breaker. Ethernet is generally ran in 1" conduit, but 3/4" will work fine. And what do you mean by, "12-2 in armor?"

Also, make sure you pigtail your receptacles. The two extra screws are not to be used.
 
Reply
Old Feb 8, 2021 | 06:53 AM
  #34  
johnday's Avatar
johnday
Cargo Master
15 Year Member
Liked
Loved
Community Favorite
Joined: Oct 2010
Posts: 2,762
Likes: 536
From: barton city mi
Originally Posted by muhford
Also, make sure you pigtail your receptacles. The two extra screws are not to be used.
Is this a new requirement?
 
Reply
Old Feb 8, 2021 | 02:57 PM
  #35  
muhford's Avatar
muhford
Fleet Mechanic
10 Year Member
Liked
Loved
Community Favorite
Joined: Mar 2014
Posts: 1,269
Likes: 129
From: Missouri
I don't know if it's new or not. It's rather important though. Using all 4 screws will make the receptacle part of the circuit and it will burn up.
 
Reply
Old Feb 8, 2021 | 05:04 PM
  #36  
johnday's Avatar
johnday
Cargo Master
15 Year Member
Liked
Loved
Community Favorite
Joined: Oct 2010
Posts: 2,762
Likes: 536
From: barton city mi
Originally Posted by muhford
I don't know if it's new or not. It's rather important though. Using all 4 screws will make the receptacle part of the circuit and it will burn up.
Understand what you're saying, makes sense.
 
Reply
Old Feb 9, 2021 | 10:58 PM
  #37  
EDC8008's Avatar
EDC8008
Fleet Mechanic
10 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Dec 2015
Posts: 1,521
Likes: 412
From: Washington Coast
Originally Posted by muhford
When they installed your new sub panel did they drive two 5/8" ground rods? (Or whatever code is in your area) Properly grounding a sub panel is very important.

The Code here only called for one 5/8 ground rod so that's what I put.

Other notes. LEDs draw very little power and you could probably have them all on 1 breaker. Ethernet is generally ran in 1" conduit, but 3/4" will work fine. And what do you mean by, "12-2 in armor?"

I thought about the LEDs might be good with just the one breaker so easy to change right now, thanks for the suggestion.

Yes I'm making sure that all of my Ethernet is in a dedicated 3/4" conduit (only running one cable to the shop) and 12" away from the power which is in 2" conduit.

When I got my permit originally L&I here let me know all my wiring had to be in metal conduit (armor) in the building with all metal boxes. So when I bought my wire I got it all the same, #12 gauge conductor, 2 conductors plus ground already in the conduit. I may have used the wrong description.

Also, make sure you pigtail your receptacles. The two extra screws are not to be used.
Yepper, been there and done that already.


 
Reply
Old Oct 15, 2022 | 04:31 AM
  #38  
Norcal01's Avatar
Norcal01
5th Gear
Joined: Jan 2016
Posts: 5
Likes: 0
A receptacle used as a disconnect must be horsepower rated & the wiring must be sized from the tables in NECcould article 430 for a 5 HP single phase motor rated for 230V , table 430.248 lists the amperes as 30.8, after adding 125% that is 35A so the minimum circuit is 35A which requires 8 AWG if NM cable ""Romex®" is used or if THHN/THWN conductors then 10 AWG*, is permitted, unless somebody is willing to buy a high dollar pin & sleeve** receptacle / plug there is no code compliant way to cord and plug connect a 5 HP single phase motor, it's cheaper to hardwire & use a fusible or non-fusible pullout AC disconnect, anyone using a 3-wire dryer or range cord & receptacle for anything other then those appliances, is not code compliant either, they are non-grounding dual voltage 125/250V rated devices, prior to the adoption of the 1996 NEC it was permitted to ground the frames of clothes dryers & cooking equipment to the neutral of those appliances, now that is only permitted in existing installations, and that was the only code compliant use of those devices.


* there are different rules that apply to motors, & air conditioning equipment that allow 10 AWG THWN conductors to be used for 35A, it does not apply to general purpose branch circuits though, and do not apply to NM sheathed cable, they must be sized from the 60°C column of table 310.15(B)(16)

**A pin and sleeve receptacle, back box, & plug could cost $400-500 dollars.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

10 Ugly Ford Trucks That We Still Kinda Love

 Joe Kucinski
story-1

10 Things Every Truck Owner NEEDS (2026 Edition)

 Michael S. Palmer
story-2

Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-3

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-4

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-5

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-6

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-7

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-8

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-9

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
Old Oct 15, 2022 | 04:40 AM
  #39  
Norcal01's Avatar
Norcal01
5th Gear
Joined: Jan 2016
Posts: 5
Likes: 0
Originally Posted by johnday
Is this a new requirement?
Unless someone has local amendments, back wiring is code compliant, but on cheap residential grade devices the maximum size wire is 14AWG, for back wiring, pigtailing is good practice though, buying higher quality receptacles that use a pressure plate tightened by a screw is good practice also, rather then use push and pray connections.
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
taneum
1973 - 1979 F-100 & Larger F-Series Trucks
13
Dec 23, 2012 09:42 PM
cbzdel
1999 - 2016 Super Duty
2
May 23, 2012 08:21 AM
BIG-COUNTRY
Garage & Workshop
4
Dec 24, 2005 01:05 PM
knightshield
Garage & Workshop
18
Mar 7, 2004 03:24 AM




All times are GMT -5. The time now is 03:17 AM.

story-0
10 Ugly Ford Trucks That We Still Kinda Love

Slideshow: 10 ugly Ford trucks that we still kinda love.

By Joe Kucinski | 2026-06-03 09:51:16


VIEW MORE
story-1
10 Things Every Truck Owner NEEDS (2026 Edition)

Slideshow: the best gifts for dads & grads

By Michael S. Palmer | 2026-06-03 15:43:58


VIEW MORE
story-2
Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-06-03 11:38:36


VIEW MORE
story-3
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-4
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-5
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-6
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-7
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-8
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-9
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE