Since your fuel source is enclosed in a relatively small 75 or so cubic foot space, I think you should treat the exhaust as if it were in a hazardous environment, regardless of make up air volume, which would require an explosion proof exhaust fan. Additionally you may want to consider filtering your intake air to remove as much dirt and contamination from outside as possible which will prolong engine life and combustion efficiency.
 
Reply
Old Dec 19, 2011 | 11:29 PM
  #17  
Bdox's Avatar
Bdox
Fleet Owner
Joined: Sep 2005
Posts: 28,609
Likes: 18
From: Lake Tahoe, Nevada
Club FTE Silver Member

Unless that is an automatic fire extinguisher, I would locate it away from the hut in case it's hot.
 
Reply
Old Dec 20, 2011 | 10:47 AM
  #18  
Beechkid's Avatar
Beechkid
Moderator
20 Year Member
Liked
Loved
Community Favorite
Joined: Aug 2002
Posts: 6,099
Likes: 379
From: Southern California
Club FTE Gold Member
Originally Posted by frederic
I didn't post pictures yet but I replaced the bathroom fan ductwork and outside vents with two 10" square vents as an air intake. The fan on top sucks air through them, across the generator's engine and genhead, and out the top.

I ran it yesterday with the subpanel fully loaded as it would be during a power failure - to big UPS systems that power my server farm, the fridge, the coffee making in "brew now" mode, the furnace, and the sump pumps. I got one of the sump pumps to "work" by putting a hose in the sump well, and the furnace I got to stay on for the hour long test by setting the thermostat to 99 degrees.

The air coming out of the fan on top was somewhat warm, but not as warm as I would have expected. Of course it was 35 degrees outside and that certainly helped, but as a first test things were good. It's supposed to be upper 50's later this week so I'll repeat the test and see what happens.

I installed a fire extinguisher today, I figured that was a good idea, "just in case".
That is all good, but flammabe vapors are both heavier & lighter than air, meaning even with all the roof mounted vents it will not allow the flammable vapors to vent off fat the bottom- just like a water heater room, you must have venting 6" from the top & bottom.
 
Reply
Old Dec 27, 2011 | 10:03 PM
  #19  
lxlmariuslxl's Avatar
lxlmariuslxl
Senior User
15 Year Member
Joined: Mar 2009
Posts: 132
Likes: 1
From: Wake Forest
Originally Posted by Bdox
Duct fans, available is several sizes, are quiet and move masses of air. They are good pushing or pulling.

I put a 10" duct fan on my 9 x 13 bathroom and it pulled so much air it would pull the door shut. Went down to an 8". Still strong but doesn't make your ears pop.
Thats some Tim The Tool man stuff right there haha
 
Reply
Old Dec 28, 2011 | 10:57 AM
  #20  
Beechkid's Avatar
Beechkid
Moderator
20 Year Member
Liked
Loved
Community Favorite
Joined: Aug 2002
Posts: 6,099
Likes: 379
From: Southern California
Club FTE Gold Member
Originally Posted by lxlmariuslxl
Thats some Tim The Tool man stuff right there haha
Just remember, those fans are not rated for use where flammable vapors are or could be present (Class 1 Division 1 or 2 certified)....they will produce a spark or even a static charge which is more than enough to ignite accumulated vapors.
 
Reply
Old Dec 28, 2011 | 12:11 PM
  #21  
lxlmariuslxl's Avatar
lxlmariuslxl
Senior User
15 Year Member
Joined: Mar 2009
Posts: 132
Likes: 1
From: Wake Forest
Originally Posted by Beechkid
Just remember, those fans are not rated for use where flammable vapors are or could be present (Class 1 Division 1 or 2 certified)....they will produce a spark or even a static charge which is more than enough to ignite accumulated vapors.
I paint cars for a living and that is a must!!!Ive heard crazy stories about guys blowing up their shops b/c of the wrong fans
 
Reply
Old Jan 8, 2012 | 11:17 PM
  #22  
frederic's Avatar
frederic
Thread Starter
|
Post Fiend
Joined: Oct 2003
Posts: 6,214
Likes: 13
From: New Jersey
Okay, just a catch-up. Thank you for the feedback... very much appreciated.

I ran the generator yesterday for an hour, with the load I intend to power with this fully on, and the inside temperature of the genshed hovered around 80 degrees, with the outside temperature only being 47. A 33 degree increase in temperature in a lot of BTU for sure, because the fan is sucking most of it out. I may close up the vents on the back of the shed and move them to the floor underneath the generator to encourage less trapping of heat. It might also be where I measured the heat which was in the far back corner opposite the side where the exhaust port is. This kind of stuff is not my forte (thermodynamics, airflow, et al) and I free admit that. I'm more of a monkey ;-)

The fan isn't stamped, certified or marked as an explosion proof fan however it's a synchronous motor which doesn't have brushes, so there's no sparks in the housing to ignite fuel vapor. Unless I'm missing something, that should be okay, right? Not necessarily from an "official" standpoint, but in concept at least?

Aside from the kinds of concerns you'all kindly pointed out, there is one design flaw on my part which didn't become apparent until yesterday - there's a skinny little tree about a foot away from the generator hut and it worked out the exhaust port blows right on that tree. So, the bark was cinged after an hour of running the generator. This surprised me because I figured the tree was a foot away most of the heat would spread out and not be focused on the tree, but apparently that wasn't the case. So tomorrow, the little tree goes. It's half-dead anyway. I just find it amusing that the exhaust port and the skinny tree truck lined up perfectly by accident. Figures, right?

I do think the intake ports aren't big enough though, because there's still enough suction to pull the doors closed tight if I close them. I can open them, there's not that much suction, but the left door has a slight warp in it because it got wet before I painted it, and that slight warp gets "sucked flat" so maybe instead of moving the intake ports I should just add another set on the bottom and call it a day.

I like the idea of filtering the intake air a bit as to keep debris and bugs out - certainly I want the generator to not be traumatized while operating it in the shed for durability reasons. Maybe I can use door screen material in a frame or possible sections of furnace filters or something like that. Whatever I end up using needs to stay put though.

A friend who looked at it a week ago suggested instead of having the generator suck in ambient air from inside the generator hut, maybe I should consider ducting from the air filter box in the center of the engine (v-twin) to the opposite wall of as to where the exhaust goes since it's right there, thus using the coolest air possible to feed the engine. That will require a little fangling since the airbox draws through large holes in the bottom, flows through the oval filter, then into the throat of the two barrel carb. This makes sense since the measured temperature inside is hotter than outside.

Thanks again!
 
Reply
Old Jan 9, 2012 | 10:50 AM
  #23  
Beechkid's Avatar
Beechkid
Moderator
20 Year Member
Liked
Loved
Community Favorite
Joined: Aug 2002
Posts: 6,099
Likes: 379
From: Southern California
Club FTE Gold Member
Originally Posted by frederic
Okay, just a catch-up. Thank you for the feedback... very much appreciated.

I ran the generator yesterday for an hour, with the load I intend to power with this fully on, and the inside temperature of the genshed hovered around 80 degrees, with the outside temperature only being 47. A 33 degree increase in temperature in a lot of BTU for sure, because the fan is sucking most of it out. I may close up the vents on the back of the shed and move them to the floor underneath the generator to encourage less trapping of heat. It might also be where I measured the heat which was in the far back corner opposite the side where the exhaust port is. This kind of stuff is not my forte (thermodynamics, airflow, et al) and I free admit that. I'm more of a monkey ;-)

The fan isn't stamped, certified or marked as an explosion proof fan however it's a synchronous motor which doesn't have brushes, so there's no sparks in the housing to ignite fuel vapor. Unless I'm missing something, that should be okay, right? Not necessarily from an "official" standpoint, but in concept at least?

Aside from the kinds of concerns you'all kindly pointed out, there is one design flaw on my part which didn't become apparent until yesterday - there's a skinny little tree about a foot away from the generator hut and it worked out the exhaust port blows right on that tree. So, the bark was cinged after an hour of running the generator. This surprised me because I figured the tree was a foot away most of the heat would spread out and not be focused on the tree, but apparently that wasn't the case. So tomorrow, the little tree goes. It's half-dead anyway. I just find it amusing that the exhaust port and the skinny tree truck lined up perfectly by accident. Figures, right?

I do think the intake ports aren't big enough though, because there's still enough suction to pull the doors closed tight if I close them. I can open them, there's not that much suction, but the left door has a slight warp in it because it got wet before I painted it, and that slight warp gets "sucked flat" so maybe instead of moving the intake ports I should just add another set on the bottom and call it a day.

I like the idea of filtering the intake air a bit as to keep debris and bugs out - certainly I want the generator to not be traumatized while operating it in the shed for durability reasons. Maybe I can use door screen material in a frame or possible sections of furnace filters or something like that. Whatever I end up using needs to stay put though.

A friend who looked at it a week ago suggested instead of having the generator suck in ambient air from inside the generator hut, maybe I should consider ducting from the air filter box in the center of the engine (v-twin) to the opposite wall of as to where the exhaust goes since it's right there, thus using the coolest air possible to feed the engine. That will require a little fangling since the airbox draws through large holes in the bottom, flows through the oval filter, then into the throat of the two barrel carb. This makes sense since the measured temperature inside is hotter than outside.

Thanks again!
With regards to the fan, because of the materials the fan blade itself are constructed of, that will produce more than enough static charge to provide a substantial ignition source. Even if the motor has no brushes, etc, all of the wiring connection points are considered "exposed" (even if they are attached with a twist nut & placed inside a covered junction box).....the power cord itself is the same....an ignition source......

If you take a look at any spray booth (they are easiet to view), even the electrical conduit is sealed at every connection point, every light bulb inside the booth is sealed from the air & the booth is electrically bonded & grounded.

Regarding the exhaust- yeah, the temp should be around 600-1000 degrees....and the carbon that builds up on any surface becomes "highly flammable" (literally like gasoline) over time.

and yes, fresh air intake (metal) is a definite.....just like any commercial building.......
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-1

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-2

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-3

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-4

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-5

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-6

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-7

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
story-8

Top 10 Ford Trucks Coming to Mecum Indy 2026

 Brett Foote
story-9

5 Best / 5 Worst Ford Truck Wheels of All Time

 Joe Kucinski
Old Jan 13, 2012 | 04:53 PM
  #24  
monckywrench's Avatar
monckywrench
Cargo Master
20 Year Member
Liked
Loved
Community Favorite
Joined: Apr 2001
Posts: 2,220
Likes: 26
Off-road spark arrestors are an option for the end of the pipe. If there's a lot of leaves etc and you live in a dry area that could be a good thing.
 
Reply
Old Jan 21, 2012 | 10:25 PM
  #25  
cigarxtc's Avatar
cigarxtc
Postmaster
25 Year Member
Joined: Apr 2000
Posts: 2,881
Likes: 1
From: North of Tulsa, Oklahoma
wow, you put a lot of work into that hut. I can't tell by the pics, how do you connect all the electrical devices to it, when you need to use the generator? Do you have to run cords thru the open doors to the outlets in the pic?
 
Reply
Old Jan 22, 2012 | 11:29 AM
  #26  
Ford_Six's Avatar
Ford_Six
Hotshot
Joined: Oct 2002
Posts: 18,488
Likes: 22
From: The Big, Oregon
Club FTE Gold Member
Post one says he ran conduit and wire.
 
Reply
Old Jan 22, 2012 | 02:06 PM
  #27  
monckywrench's Avatar
monckywrench
Cargo Master
20 Year Member
Liked
Loved
Community Favorite
Joined: Apr 2001
Posts: 2,220
Likes: 26
Don't forget a UPS at your computer etc to condition voltage and protect the equipment.

That's a good idea no matter where your power comes from.
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
EightySecond
2017 - 2022 Super Duty
40
Dec 2, 2016 06:34 AM
ihcc104
1961 - 1966 F-100 & Larger F-Series Trucks
5
Aug 21, 2016 08:58 AM
Ibuildmyown
1948 - 1956 F1, F100 & Larger F-Series Trucks
15
Feb 6, 2015 09:05 PM
Sgt93
6.7L Power Stroke Diesel
3
May 16, 2011 01:23 PM
wreckinball
Pre-Power Stroke Diesel (7.3L IDI & 6.9L)
18
May 29, 2010 09:13 PM




All times are GMT -5. The time now is 06:10 PM.

story-0
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-1
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-2
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-3
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-4
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-5
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-6
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-7
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE
story-8
Top 10 Ford Trucks Coming to Mecum Indy 2026

Slideshow: Here are the top 10 Fords coming to Mecum Indy 2026.

By Brett Foote | 2026-05-04 13:49:49


VIEW MORE
story-9
5 Best / 5 Worst Ford Truck Wheels of All Time

Slideshow: The 5 best and 5 worst Ford truck wheels of all time

By Joe Kucinski | 2026-04-29 16:49:01


VIEW MORE