I think we all went way beyond the original question, which was "when I'm working on a house ..."

That means to me, anything he does will be a temporary solution. But no, better to leave well enough alone or do it the right way.
 
Reply
Old Sep 13, 2005 | 07:15 PM
  #17  
alchymist's Avatar
alchymist
"Mifflin Clay"
Joined: Jul 2005
Posts: 3,177
Likes: 4
From: Mifflin, PA
Club FTE Silver Member

Originally Posted by PupnDuck
Whether you go the transfer switch route of just run a bunch of extension cords around, most generators have a ground lug on them somewhere. It's there for a reason. Run a hunk of 6 ga. from it to a good earth ground (like the one the house's main service panel is connected to). The butt you DON'T fry could be yours.
You might also consider a GCFI - they come in a 3 foot extension cord type just made for portable gen use - I have several, and use one anytime I'm outside without a known GCFI outlet to plug in to.
 
Reply
Old Sep 13, 2005 | 09:41 PM
  #18  
GotLift's Avatar
GotLift
Thread Starter
|
Elder User
Joined: Feb 2004
Posts: 717
Likes: 0
Thanks for the input guys. I think I will go with the extension cords. I wouldn't be in the house for more than a few hours and I wouldn't even have to use the generator for more than an hour at most.
 
Reply
Old Sep 13, 2005 | 09:47 PM
  #19  
"Beemer Nut"'s Avatar
"Beemer Nut"
Post Fiend
Joined: Dec 2003
Posts: 6,658
Likes: 4
From: "Islander"
It's a Federal Offense to connect a generator to any house that has a service drop connected without a Auto Transfer switch. To add a double male plug and generator to a 120 plug or 230 volt dryer plug can mean jail time and fine. A small low current auto transfer switch of 40-50 amps can be had around $150. You must notify your local utility company that you have a auto transfer system and generator before hard wiring it in.
.....=o&o>.....
 
Reply
Old Sep 14, 2005 | 04:06 AM
  #20  
alchymist's Avatar
alchymist
"Mifflin Clay"
Joined: Jul 2005
Posts: 3,177
Likes: 4
From: Mifflin, PA
Club FTE Silver Member

Originally Posted by Beemer Nut
It's a Federal Offense to connect a generator to any house that has a service drop connected without a Auto Transfer switch. To add a double male plug and generator to a 120 plug or 230 volt dryer plug can mean jail time and fine. A small low current auto transfer switch of 40-50 amps can be had around $150. You must notify your local utility company that you have a auto transfer system and generator before hard wiring it in.
.....=o&o>.....
Not to mention how it's going to feel if you unplug the dryer end before the generator end. There is an easier way to connect for a permanent install - Get a subpanel - sized with as many breakers as you want emergency circuits. Disconnect every circuit you want/need to run from the generator from the main breaker box, and wire into the sub panel. Install a dryer outlet on the main breaker box next to the subpanel. Also install one from the genset. (LABEL EACH ONE). Now, equip your subpanel with a dryer plug - and simply plug subpanel into whichever source yo want to use. Switching is then a simple unplug/plug step. If you have a genset and emergency load above 30 amps, use a range plug and receptacles.
 
Reply
Old Sep 14, 2005 | 04:50 AM
  #21  
Torque1st's Avatar
Torque1st
Posting Legend
Joined: Sep 2001
Posts: 30,255
Likes: 37
Originally Posted by alchymist
Not to mention how it's going to feel if you unplug the dryer end before the generator end. There is an easier way to connect for a permanent install - Get a subpanel - sized with as many breakers as you want emergency circuits. Disconnect every circuit you want/need to run from the generator from the main breaker box, and wire into the sub panel. Install a dryer outlet on the main breaker box next to the subpanel. Also install one from the genset. (LABEL EACH ONE). Now, equip your subpanel with a dryer plug - and simply plug subpanel into whichever source yo want to use. Switching is then a simple unplug/plug step. If you have a genset and emergency load above 30 amps, use a range plug and receptacles.
I don't know much about all the electrical codes but this does not sound like it would pass electrical code. Maybe someone will know.
 
Reply
Old Sep 14, 2005 | 04:55 AM
  #22  
alchymist's Avatar
alchymist
"Mifflin Clay"
Joined: Jul 2005
Posts: 3,177
Likes: 4
From: Mifflin, PA
Club FTE Silver Member

Talking

Originally Posted by Torque1st
I don't know much about all the electrical codes but this does not sound like it would pass electrical code. Maybe someone will know.
I don't think there is anything in the NEC prohibiting it........and it's A LOT SAFER than the double plug system! But I'm sure someone will jump in quoting achapter & paragraph if there is....
 
Reply
Old Sep 15, 2005 | 10:44 AM
  #23  
cgl's Avatar
cgl
Posting Guru
25 Year Member
Joined: Apr 2000
Posts: 1,345
Likes: 0
From: NorCal
Originally Posted by Beemer Nut
It's a Federal Offense to connect a generator to any house that has a service drop connected without a Auto Transfer switch. To add a double male plug and generator to a 120 plug or 230 volt dryer plug can mean jail time and fine. A small low current auto transfer switch of 40-50 amps can be had around $150. You must notify your local utility company that you have a auto transfer system and generator before hard wiring it in.
.....=o&o>.....
Where did you hear this? I'm curious to read up on it. All of my transfer switches are manual and the PG&E engineer said he didn't need to know if we had a transfer switch installed. As long as you have a service transfer switch installed correctly, the utility will never know it's there. So why would they need to know if you have one? It is true, if you didn't use some sort of isolation and energize the drop which could possibly energize the transformer and main lines, that you could be fined and persecuted. Especialy if a lineman is workin on it.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

10 Ugly Ford Trucks That We Still Kinda Love

 Joe Kucinski
story-1

10 Things Every Truck Owner NEEDS (2026 Edition)

 Michael S. Palmer
story-2

Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-3

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-4

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-5

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-6

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-7

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-8

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-9

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
Old Sep 15, 2005 | 08:58 PM
  #24  
krewat's Avatar
krewat
FTE Leadership Emeritus
Joined: Jul 2002
Posts: 42,561
Likes: 423
From: Long Island USA
Club FTE Gold Member
Originally Posted by cgl
Where did you hear this? I'm curious to read up on it. All of my transfer switches are manual and the PG&E engineer said he didn't need to know if we had a transfer switch installed. As long as you have a service transfer switch installed correctly, the utility will never know it's there. So why would they need to know if you have one? It is true, if you didn't use some sort of isolation and energize the drop which could possibly energize the transformer and main lines, that you could be fined and persecuted. Especialy if a lineman is workin on it.
It means if your house is on fire, and the fire department cuts the electricity, that your generator is going to fire up and continue providing electricity to the house.

I think they have to note it somewhere, so that when the fire dept calls the utility, they know you have an auto transfer switch. Or, the utility notifies the fire dept and they keep it on file. I don't know.

It's one of those things they do ...
 
Reply
Old Sep 15, 2005 | 11:58 PM
  #25  
Torque1st's Avatar
Torque1st
Posting Legend
Joined: Sep 2001
Posts: 30,255
Likes: 37
I remember reading something about cord connected (plug in) devices only being allowed for a temporary installation. Any permanent circuits could not be cord connected. It has been a while since I did any extensive reading of the NEC.
 
Reply
Old Sep 16, 2005 | 06:33 AM
  #26  
alchymist's Avatar
alchymist
"Mifflin Clay"
Joined: Jul 2005
Posts: 3,177
Likes: 4
From: Mifflin, PA
Club FTE Silver Member

Originally Posted by Torque1st
I remember reading something about cord connected (plug in) devices only being allowed for a temporary installation. Any permanent circuits could not be cord connected. It has been a while since I did any extensive reading of the NEC.
Guess that means your dryer and range must be gas.....
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
91Fbody
1948 - 1956 F1, F100 & Larger F-Series Trucks
7
Apr 5, 2015 03:13 PM
Scratcher
Garage & Workshop
12
Dec 14, 2011 04:45 PM
transam525
1948 - 1956 F1, F100 & Larger F-Series Trucks
10
Feb 8, 2010 11:14 PM
pud
Alternative Fuels, Hybrids & Mileage
9
May 21, 2009 09:58 PM
dinosaurfan
General NON-Automotive Conversation
9
Dec 23, 2001 10:32 PM




All times are GMT -5. The time now is 08:44 PM.

story-0
10 Ugly Ford Trucks That We Still Kinda Love

Slideshow: 10 ugly Ford trucks that we still kinda love.

By Joe Kucinski | 2026-06-03 09:51:16


VIEW MORE
story-1
10 Things Every Truck Owner NEEDS (2026 Edition)

Slideshow: the best gifts for dads & grads

By Michael S. Palmer | 2026-06-03 15:43:58


VIEW MORE
story-2
Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-06-03 11:38:36


VIEW MORE
story-3
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-4
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-5
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-6
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-7
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-8
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-9
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE