electrical question, & I'll actually ASK it!

OK, this time, no endless wait for the question:

Why do they crimp the ground & neutral together on many 240V appliances?
If your power source has four wires (separate neutral & ground), isn't it better to make the four separate connections?

After all, most 240 V appliances (like ranges, wall ovens, cooktops) use 120 for the lights, clocks, etc... so the neutral has current running through it (or am I wrong?).

Thanks, I know just enough about electric to be dangerous!
 
Reply
Old Feb 22, 2008 | 10:56 AM
  #2  
freirefishing's Avatar
freirefishing
Postmaster
15 Year Member
Joined: Sep 2006
Posts: 4,982
Likes: 1
From: Clearwater, Fl
is it plugging into a gfi?
 
Reply
Old Feb 22, 2008 | 10:58 AM
  #3  
tjc transport's Avatar
tjc transport
i ain't rite
Joined: Mar 2005
Posts: 65,507
Likes: 5,563
From: Marlboro Mental Hospital.
Club FTE Gold Member
because in a single phase 240 volt system, the ground and neutral are both connected to ground in the power panel.
 
Reply
Old Feb 22, 2008 | 12:22 PM
  #4  
SpringerPop's Avatar
SpringerPop
Hotshot
Veteran: Air Force
20 Year Member
Liked
Community Favorite
Joined: Jan 2002
Posts: 17,988
Likes: 207
From: La La Land
Club FTE Silver Member

Daddy,

I'd guess your understanding of electrical systems is pretty spot-on, from what you said.

There is no power running through the neutral or ground wires in most 220 volt systems. An example might be an electric kitchen cook top. Those usually have no white.

However, there may be times when current does flow. An example might be a 220 volt oven that also has a 110 volt clock in it. The amount of current to run the clock would run in the white wire, and one leg of the 220 would have the additional current to run the clock. It's kinda' uncommon, but it happens.

The green should be separate, connected to the metal chassis, and run all the way back to the Ground buss bar in the breaker box. If present, the neutral (white) should be run all the way back to the Neutral buss bar in the breaker box.

The only place the whites and greens should be tied is within the main breaker box when those buss bars are tied. Even sub-boxes should have separate green and whites running separately through them, and the two busses left untied.

So the answer to your question is: electrician is lazy, cheap, unschooled, or any combination of those.

Pop
 
Reply
Old Feb 22, 2008 | 01:56 PM
  #5  
jroehl's Avatar
jroehl
Post Fiend
Joined: Apr 2004
Posts: 6,473
Likes: 4
From: Lafayette, IN
+1 on what Pop said. He nailed it. If your 240V appliance does not need a neutral for 120V features, then the receptacle and male cord end should be changed to 3-prong. The white should then be capped off in the box behind the receptacle. If the 240V appliance DOES use 120V, then the neutral should absolutely NOT be tied to the ground wire for safety reasons--that ground wire is not to carry normal current.

Jason
 
Reply
Old Feb 22, 2008 | 03:08 PM
  #6  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
240V kitchen and laundry appliances have two hot legs and a neutral that is grounded at the service panel.

If it is being installed in an older three-wire home, the case/cabinet is electrically tied to the neutral terminal effectively grounding it (assuming the connection in the panel is correct).

If the appliance is being installed into a newer 4-wire installation, the neutral and ground are separate at the appliance. The neutral and ground are still required to be connected at the service panel.

I peddle appliances and have never seen one that had the neutral and ground connected at the appliance except with an easy to remove jumper or strap, never have seen one crimped.

Steve
 
Reply
Old Feb 23, 2008 | 04:10 PM
  #7  
daddio360's Avatar
daddio360
Thread Starter
|
Senior User
Joined: Jun 2006
Posts: 361
Likes: 0
Well, I guess I did have it right then.

I have two wall ovens that I am fairly certain use 110 for the interior light and the digital keypad controls but on both the white & ground wires are crimped together by the factory, not the electrician...just trying to figure out why?
 
Reply
Old Feb 23, 2008 | 06:11 PM
  #8  
tewferford's Avatar
tewferford
Post Fiend
Joined: Oct 2006
Posts: 7,269
Likes: 0
From: Where's my map???
In a single phase, the ground and nuetral are one in the same. They are crimped to make sure the unit is infact grounded. Trace the green wire, and you will see it is grounded to the body of the unit.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-1

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-2

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-3

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-4

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-5

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-6

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-7

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-8

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-9

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
Old Feb 23, 2008 | 06:29 PM
  #9  
jroehl's Avatar
jroehl
Post Fiend
Joined: Apr 2004
Posts: 6,473
Likes: 4
From: Lafayette, IN
Frank, from a pure electrical point of view, you are correct. However, electrical code is very clear on this that the ONLY place the two are to be bonded is at the main service panel. This is for safety reasons and to prevent the ground wire (bare or green jacket) from carrying the normal "return" current. There are a number of bad scenarios that can arise from current flowing in the ground wire in non-fault situations. Not to mention, the ground wire is often sized smaller than the current-carrying conductors, so if a break occurred in the neutral, the ground would carry the full current, and if that current were close to the rating of the hot wire, the ground could overheat.

Jason
 
Reply
Old Feb 23, 2008 | 06:42 PM
  #10  
tewferford's Avatar
tewferford
Post Fiend
Joined: Oct 2006
Posts: 7,269
Likes: 0
From: Where's my map???
Jason, I agree with what you are saying but, a house that was wired 5 or more years ago never had that extra ground wire. So when you disconnect your old stove, oven or whatever and replace it with a newer model. You are left with the same wiring, or if it's a plug in. you don't have the options as the new codes require. No?
Just asking, cause now I am confused.
 
Reply
Old Feb 23, 2008 | 07:08 PM
  #11  
daddio360's Avatar
daddio360
Thread Starter
|
Senior User
Joined: Jun 2006
Posts: 361
Likes: 0
I'll agree Frank, & if it's a hot water heater, it makes no diffo anyway.

But my original question was, if the appliance uses any 120, even the small amount a light bulb draws, why wouldn't it be better to use the four separate wires if you have them? That's why I don't understand why the factory crimps those wires.
 
Reply
Old Feb 23, 2008 | 09:20 PM
  #12  
tewferford's Avatar
tewferford
Post Fiend
Joined: Oct 2006
Posts: 7,269
Likes: 0
From: Where's my map???
Okay now i got cha. If you have four wires, then yes separate them and hook them up independently. How does it feel to be the minority? hehehe
 
Reply
Old Feb 23, 2008 | 09:44 PM
  #13  
rangerfan's Avatar
rangerfan
Posting Guru
Joined: Jul 2005
Posts: 1,958
Likes: 0
From: Southeastern Indiana
Originally Posted by jroehl
Frank, from a pure electrical point of view, you are correct. However, electrical code is very clear on this that the ONLY place the two are to be bonded is at the main service panel. This is for safety reasons and to prevent the ground wire (bare or green jacket) from carrying the normal "return" current. There are a number of bad scenarios that can arise from current flowing in the ground wire in non-fault situations. Not to mention, the ground wire is often sized smaller than the current-carrying conductors, so if a break occurred in the neutral, the ground would carry the full current, and if that current were close to the rating of the hot wire, the ground could overheat.

Jason
That caused a friend of mines house to burn down cause by what you described on their dryer.
 
Reply
Old Feb 24, 2008 | 04:34 PM
  #14  
jroehl's Avatar
jroehl
Post Fiend
Joined: Apr 2004
Posts: 6,473
Likes: 4
From: Lafayette, IN
Originally Posted by tewferford
Jason, I agree with what you are saying but, a house that was wired 5 or more years ago never had that extra ground wire. So when you disconnect your old stove, oven or whatever and replace it with a newer model. You are left with the same wiring, or if it's a plug in. you don't have the options as the new codes require. No?
Just asking, cause now I am confused.
One possibility that is less than ideal is that the wiring to the stove receptacle is say, 6/3--meaning it has two hots and a neutral. In that case, bonding the ground and the neutral at the stove is not ideal, but doable. There would just be a chance that in a fault condition, the stove case could become energized. The no-no is 6/2 with ground (two hots and a ground) and having the ground and neutral bonded at the stove.

Jason
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
scottie2hottie
General NON-Automotive Conversation
29
Sep 7, 2008 04:14 PM
ag-ford-4x4
General NON-Automotive Conversation
13
Dec 22, 2006 09:56 PM
53wa2fl
General NON-Automotive Conversation
15
Sep 30, 2005 03:27 PM
psychlopath
General NON-Automotive Conversation
20
Feb 17, 2005 12:10 PM




All times are GMT -5. The time now is 07:07 PM.

story-0
Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-05-30 18:33:59


VIEW MORE
story-1
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-2
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-3
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-4
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-5
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-6
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-7
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-8
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-9
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE