putting in a dryer plug

i bought new maytags for christmas.

the old dryer doesn't have a plug. the electrical cable goes from the breaker panel right into the back of the dryer. no plug.

i bought a plug and a box to plug the dryer and i'm gonna put a new cable with 4 wires to ground it.

the current breaker is 30. the guy at home depot said i should put in a 40 but i wanted to see what i had first. can i leave the 30 or should i change the breaker to a 40 as well? it's a regular washer/dryer, not one of those big front loader ones

merry christmas/happy holidays
john
 
Reply
Old Dec 24, 2006 | 01:47 PM
  #2  
Greg 79 f150's Avatar
Greg 79 f150
Postmaster
Joined: Feb 2003
Posts: 2,848
Likes: 1
From: Kentucky
no, leave it 30 amp.
 
Reply
Old Dec 24, 2006 | 01:52 PM
  #3  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
http://www.codecheck.com/eleccode.htm#generalpurpose
 
Reply
Old Dec 24, 2006 | 02:37 PM
  #4  
conger's Avatar
conger
Posting Guru
Joined: May 2006
Posts: 1,028
Likes: 0
From: Edmonton, AB.
Leave the breaker as a 2P-30. The spec plate on the dryer should show what it's load is. All you have to do is use the same wire that ran to your old dryer from the panel. Install a 4 11/16" box at the the end of that wire. Fasten the new box too the wall and add staples to support the wire. Home depot sells a book CEC simplified for about $16.00. It's a good investment for the home owner to do a little wiring. Go buy a dryer receptacle and cover. Red and black go to the 2 side terminals, white to the center, and the ground to the pin. Make sure you ground the box as well. If the wire is running on the surface of the wall you will have to use a piece of 1/2" emt pipe and a connector to the ceiling space or to where-ever it goes into the wall. I'm assuming the the dryer is in a basement laundry room. If you pick up that book, it explains it with pix and it's easy to follow. Or you can pay a guy like me, $90/hr to do it for you. Good luck, it not very hard.
 
Reply
Old Dec 24, 2006 | 07:22 PM
  #5  
websthes's Avatar
websthes
Thread Starter
|
Postmaster
Joined: Mar 2002
Posts: 2,680
Likes: 1
From: Montreal Canada
Originally Posted by Mil1ion
http://www.codecheck.com/eleccode.htm#generalpurpose

Laundry

* Separate 20 amp laundry circuit [210-4c] [4203]
* Laundry outlet must be <6ft. from washer/gas dryer [210-52f] [4203.3]
* Electric dryer min. feed 30-amp #10 THHN wire [220-18] [t 4204.3a]


i forgot all about the washer when the motor goes on, the upstairs lights dim out. all the house wiring is sitting on the same breaker. the plan is to add circuits as we renovate, and replace all that old wiring with seperate breakers for each part of the house.

if i make a new circuit for the washer, can i make one that will service an entire laundry room? or does the washer need a circuit all to itself and i have to make a different circuit for the lights?
 
Reply
Old Dec 24, 2006 | 08:00 PM
  #6  
conger's Avatar
conger
Posting Guru
Joined: May 2006
Posts: 1,028
Likes: 0
From: Edmonton, AB.
The washer should be on it's own circuit. It sounds like there has been some electrical work done by someone not to familiar with the CEC. You may want to get a journeyman electrician to check out your service panel and let you know what changes you need to make. As far as renovations are concerned, it will be better to do electrical & plumbing up-grades when walls are opened up. Anyone that you get advice from should be able to produce a licence to work in that trade. If your house is quite old (over 50 years) You may need a service up-grade. I don't know what your situation is, so I can only speculate.
 
Reply
Old Dec 24, 2006 | 08:10 PM
  #7  
ericsmith32's Avatar
ericsmith32
Elder User
Joined: Feb 2005
Posts: 549
Likes: 0
From: Kansas City, KS
For what I read you can have the washer on the laundry circuit, no limitations on the amount of plugins but it must be in the laundry room. Our washer used to dim the lights to which after I finally got off my lazy rear quarters to check it out used 18 gauge or something smaller wire. Old **** and tube stuff. I'm surprised that the old house didn't burn down, that and the live exposed electrical wire in the attic was enough to force me to redo the house. Our house has a shared neutral which makes it harder.. I have visions of a electrical shock or two .
 
Reply
Old Dec 24, 2006 | 09:24 PM
  #8  
conger's Avatar
conger
Posting Guru
Joined: May 2006
Posts: 1,028
Likes: 0
From: Edmonton, AB.
Originally Posted by ericsmith32
For what I read you can have the washer on the laundry circuit, no limitations on the amount of plugins but it must be in the laundry room. Our washer used to dim the lights to which after I finally got off my lazy rear quarters to check it out used 18 gauge or something smaller wire. Old **** and tube stuff. I'm surprised that the old house didn't burn down, that and the live exposed electrical wire in the attic was enough to force me to redo the house. Our house has a shared neutral which makes it harder.. I have visions of a electrical shock or two .
That's not right... In Canada, the Canadian Electrical code dictates the rules. The washer is to have it's own circuit. It must be minimum spec 14 AWG copper wire on a 1P-15 breaker. Anytime that wiring is tampered with, the change must meet the standards of the CEC of today, not when the house was built. Think of it like this. If you have a fire and you call in your insurance adjuster. Won't an insurance company try to find a reason not to pay for the loss. A code violation is just such a reason.
 

Last edited by conger; Dec 24, 2006 at 09:32 PM.
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-1

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-2

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-3

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-4

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-5

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-6

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-7

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-8

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-9

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
Old Dec 24, 2006 | 09:55 PM
  #9  
ericsmith32's Avatar
ericsmith32
Elder User
Joined: Feb 2005
Posts: 549
Likes: 0
From: Kansas City, KS
Okay now that I realized that he's in Canada I have no clue. But those are the US codes that I know.
 
Reply
Old Dec 24, 2006 | 10:19 PM
  #10  
conger's Avatar
conger
Posting Guru
Joined: May 2006
Posts: 1,028
Likes: 0
From: Edmonton, AB.
Originally Posted by ericsmith32
Okay now that I realized that he's in Canada I have no clue. But those are the US codes that I know.
Sorry... I thought you realized that "websthes" posed the question from Montreal. The "Canadian Electrical Code" is the same accross the country. If a Journeyman has an interprovincial, he can work in any province. Although I think Quebec is the exception. I'm from the west, so I'm not to familiar with the politics there. I know some other electricians who came from Ontario to work in Alberta, they said sometimes there's problems when you cross the Quebec border. But the code book is the same.
 
Reply
Old Dec 25, 2006 | 12:38 AM
  #11  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
Heck even I missed that

I found this for him though.

http://www.selfhelpforums.com/forumdisplay.php?f=5

Apparently the homeowner isn't allowed to do any wiring in his/her home.


I'm putting in the washer's own circuit when I get to that room.
I have to check on GFI plug for that as well.

My Canadian code book is downstairs.
 
Reply
Old Dec 25, 2006 | 01:52 AM
  #12  
conger's Avatar
conger
Posting Guru
Joined: May 2006
Posts: 1,028
Likes: 0
From: Edmonton, AB.
It does not have to be GFI. The home owner can do some limited wiring in their own house, but nothing that requires disconnection from the supply authority. If you take out a homeowners permit you can do things like add a basement rec room. The catch is that it must meet the standard of today and you are responsible. Inspectors tend look closer at do it yourselfers more than tradesmen. There are also a lot of people who do work without a permit. Most of the time it works out fine, other times not so good. I work almost entirely in commercial and industrial, but I get a lot of calls for advice or people who need to be bailed out. I try not to do many side jobs but once in a while I cave and do it. If I get too many I would have no free time at all. I almost always insist on a permit. Last summer had a friend of a friend call. Needed his central air condenser wired. Problem is, he left it until the basement was finished and the panel was on the opposite side of the house. Couldn't go through the house anymore so we had to pipe around the exterior of his house. It added $1100 to the cost simply because it wasn't done at the right time during the renovation. Had he taken out a permit, the inspector would have probadly pick it up when the walls and ceiling were still open. My point is... make sure you have the right info. Mistakes can be costly. Dryer plug and washer plug, real simple stuff. That book from Home Depot is a good start. My code book is $120 and changes every four years. The Home Depot one is less than twenty bucks. If you have bigger issues, like too small a service panel in an old house, get a qualified electrician.
 
Reply
Old Dec 25, 2006 | 04:22 AM
  #13  
websthes's Avatar
websthes
Thread Starter
|
Postmaster
Joined: Mar 2002
Posts: 2,680
Likes: 1
From: Montreal Canada
this is so bad

the hot/cold water pipes are going over the finished wall. there's no vent for the dryer. no proper outlets. there's also an enormous freezer in between the washer and dryer so the washer can drain into the sink, and the dryer can vent out the window on the other side of the room? it all worked until you try and unplug a dryer and realize the whole thing is an ugly, dangerous mess. i'm just gonna tear it all out. it's too ugly and confusing to look at anymore. i'll feel better when i'm breaking something.
 
Reply
Old Dec 25, 2006 | 06:10 AM
  #14  
Torque1st's Avatar
Torque1st
Posting Legend
Joined: Sep 2001
Posts: 30,255
Likes: 37
Still sounds like you need an electrician to come in and give you a bid on electrical renovations. Get the job done right.
 
Reply
Old Dec 25, 2006 | 08:20 AM
  #15  
daddio360's Avatar
daddio360
Senior User
Joined: Jun 2006
Posts: 361
Likes: 0
just wanted to post about "**** & tube" wiring which many old houses in my area still have: It was a well-designed system & was not (nor is it currently) inherently unsafe.

This stuff has gotten a bum rap simply because at the time these houses were wired,
electricity was used mainly for lighting & small appliances like fans, etc. Consequently, there are not enough circuits and/or ample wire gauge to handle the loads required in a modern home. Whenever there is a fire in such a home, it is the "**** & tube" wiring that is blamed, not the inadequate circuits.

I had an home insurance agent who would not write policies if ANY **** & tube wiring was still in use. It's silly to rip up a ceiling or floor to replace K&T that is being used only for a lighting circuit, but this agent, with nearly zero electrical knowledge, knew better than my master electrician....

lesson: never argue with a fool...in no time you can't tell who's who!
 
Reply



All times are GMT -5. The time now is 10:10 AM.

story-0
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-1
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-2
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-3
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-4
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-5
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-6
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-7
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-8
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-9
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE