Ground Rod....How Deep is Deep Enough?
My concern is that the entire area I live in is sitting on fairly shallow limestone, and I very well may hit limestone before getting anywhere near 8 feet. When the PO had a septic tank installed they had to put a small mound of earth over it because they couldn't get it any deeper into the ground.
If I strike rock at, say, 4 or 5 feet will be that be deep enough to be effective, or am I just wasting my time? Is there a standard procedure for a situation of this kind?
Any input appreciated!!
I can't say if 4' is enough. I am not an electrician. If you hooked it to a water pipe, it would probably be no more than 4' down. Maybe it is enough. I'm sure someone else will come along who knows. Good luck with it.
Having said that, if you can only get down 4 feet then use multiple rods in a "ground field", put ground rod clamps on the top of the rods and tie them all together with some #4 bare copper wire. It's not how deep you go but rather how much surface area of the grounding rods are in contact with the earth.
But I'd still check your local electrical code first.
Ground rods are typically driven at an angle if a straight down connection cannot be accomplished. Most of the time you will have to use the "two electrodes 8 feet apart" rule when you do this, because neither ground rod will acheive the 25 ohm resistance requirement. (And even the pair in parallel probably won't, if the soil is dry and the underlying limestone is porous).
Rebar in a footer works a lot better than ground rods, at least in terms of resistance to ground.
on the end of the ground rod, it will drive it right though rock every time!
Wally
P.S. I have been in this trade for many years, and use to drive them with
a big hammer untill some one showed me this trick! Let me know how it works
for you!
Trending Topics
Most underground water pipes are now plastic which does not conduct electricity.
If you have copper pipe inside the building and use the water piping for a ground, during electrical fault conditions the entire water system becomes electrically hot.
We bond the interior water piping to the ground rods to prevent this from happening which is required in NEC 250-80 (a)
Also any other metal piping that may become energized shall be bonded to ground. NEC 250-80 (b)
Also structural steel buildings shall be bonded to ground. NEC 250-80 (c)
The NEC does require a ground rod for seperate buildings unless the 4 wire system is used to supply the building or if there is only one branch circuit supply to the building.
But the neutral and ground shall not be bonded together. NEC 250-24 (a)
The NEC also allows for the ground rods to be driven at a max angle of 45 degrees.
But it also allows for the ground rods to be installed flat in the bottom of a ditch that is a minimum od 2.5 feet deep.(NEC 250-83 (c)(3) and does call for the upper end of the electrode to be flush or below ground level unless provisions for protection are met.
There is also a grounding ring electrode that can be burried at a depth of not less than 2.5 feet and a minimum of at least 20 feet of #2 bare copper wire to be burried in a ditch. (NEC 250-81(d))
Here in WV we have a lot of rock that makes ground rods inpossible to install in many occasions.
Ford Trucks for Ford Truck Enthusiasts
I once spent an hour driving a rod down and it seemed to be going fine, other than really slow. I got done and turned around, then tripped on the point of the rod sticking straight up behind me. The rod went down a foot and ended up doing a 180, after hitting rock.
Too many times ground rods are cut at 4', (or less), because someone didn't work at it hard enough. (I'm sure I'm not the only one that's pulled up a two foot ground rod.) Sometimes they just won't go, granite and sandstone are two examples I can think of where they won't. Sometimes the ground just isn't very conductive.
One option is to use a chemical ground. You can buy them, but I've probably built a half dozon of them over the years. Pretty straight forward. I get the cad-weld/wire at the electrical supply and the pipe and bentonite from a pipe supply. I've used rock salt to fill.
http://www.erico.com/products/ChemRod.asp
http://www.pd-engineers.com/hicon.html