Old Mar 2, 2006 | 06:15 PM
  #1  
cpe41's Avatar
cpe41
Thread Starter
|
Senior User
Joined: Apr 2004
Posts: 339
Likes: 1
From: north central Indiana
Ground Rod....How Deep is Deep Enough?

I'd very much like to install a ground rod for my garage's electrical system (since the previous owner didn't have it done) but I have a concern. I've been told that the ground rod should be driven into the ground to a depth of about 8 feet. Is this basically the minimum depth?

My concern is that the entire area I live in is sitting on fairly shallow limestone, and I very well may hit limestone before getting anywhere near 8 feet. When the PO had a septic tank installed they had to put a small mound of earth over it because they couldn't get it any deeper into the ground.

If I strike rock at, say, 4 or 5 feet will be that be deep enough to be effective, or am I just wasting my time? Is there a standard procedure for a situation of this kind?

Any input appreciated!!
 
Reply
Old Mar 2, 2006 | 06:31 PM
  #2  
trike1946's Avatar
trike1946
Logistics Pro
20 Year Member
Liked
Loved
Joined: Apr 2004
Posts: 4,292
Likes: 5
From: NJ where fun comes to die
Club FTE Silver Member

I think 8' is standard. You can try using an electric roto hammer that will also just hammer. Just stick it over the rod. It might work.

I can't say if 4' is enough. I am not an electrician. If you hooked it to a water pipe, it would probably be no more than 4' down. Maybe it is enough. I'm sure someone else will come along who knows. Good luck with it.
 
Reply
Old Mar 2, 2006 | 06:49 PM
  #3  
PupnDuck's Avatar
PupnDuck
Fleet Mechanic
20 Year Member
Joined: Jul 2005
Posts: 1,464
Likes: 104
From: Staten Island, NY
As a rule, the electrical code only allows ONE ground point in a distribution system and that is located at the main service entrance panel. Even if your garage is detatched from the main building, it relies on the main service entrance ground. Aside from safety issues, multiple ground locations can cause ground loop currents to flow on the grounding conductors in the building. Some electronic equipment will go nuts under those conditions.

Having said that, if you can only get down 4 feet then use multiple rods in a "ground field", put ground rod clamps on the top of the rods and tie them all together with some #4 bare copper wire. It's not how deep you go but rather how much surface area of the grounding rods are in contact with the earth.

But I'd still check your local electrical code first.
 
Reply
Old Mar 2, 2006 | 10:32 PM
  #4  
Ford_Six's Avatar
Ford_Six
Hotshot
Joined: Oct 2002
Posts: 18,488
Likes: 22
From: The Big, Oregon
Club FTE Gold Member
Code here says a max of 35' from a ground to the furthest point in the system. Also, 4' minimum depth IIRC.
 
Reply
Old Mar 3, 2006 | 08:06 AM
  #5  
GLR's Avatar
GLR
FTE Legend
20 Year Member
Liked
Loved
Community Favorite
Joined: Sep 2003
Posts: 53,997
Likes: 2,399
From: NY and VA
Club FTE Gold Member
An extra ground won't hurt. If there is a damp area, put it there. 8' is the norm, sometimes driving at an angle will help. A post driver helps (used for driving metal posts) hint: put the ground wire clamp on first before driving the rod it is kind of hard to get on if the rod gets "mushroomed".
 
Reply
Old Mar 3, 2006 | 08:23 AM
  #6  
fefarms's Avatar
fefarms
Elder User
Joined: Sep 2004
Posts: 941
Likes: 4
The NEC requires EACH detached building to have a grounding electrode system. The code encourages the connection of the grounded conductor (the neutral) to the grounding electrode system at only one point (the service disconnect), but there is an exception that allows for a 3 wire connection between buildings in some cases. (It is that arrangement that leads to questions of ground loops, not the presense of multiple grounding electrodes at multiple buildings).

Ground rods are typically driven at an angle if a straight down connection cannot be accomplished. Most of the time you will have to use the "two electrodes 8 feet apart" rule when you do this, because neither ground rod will acheive the 25 ohm resistance requirement. (And even the pair in parallel probably won't, if the soil is dry and the underlying limestone is porous).

Rebar in a footer works a lot better than ground rods, at least in terms of resistance to ground.
 
Reply
Old Mar 4, 2006 | 08:07 AM
  #7  
Pro-Street/StateTK's Avatar
Pro-Street/StateTK
Posting Guru
Joined: Nov 2003
Posts: 1,230
Likes: 0
From: East Flat Rock NC
If you have trouble driving your ground rod, try putting a( big hammer drill)
on the end of the ground rod, it will drive it right though rock every time!







Wally


P.S. I have been in this trade for many years, and use to drive them with
a big hammer untill some one showed me this trick! Let me know how it works
for you!
 
Reply
Old Mar 4, 2006 | 09:45 AM
  #8  
Dave Sponaugle's Avatar
Dave Sponaugle
Post Fiend
Joined: Nov 2003
Posts: 21,285
Likes: 16
From: Nutter Fort, WV
Club FTE Silver Member

Water pipe grounds are not really any good any more.
Most underground water pipes are now plastic which does not conduct electricity.
If you have copper pipe inside the building and use the water piping for a ground, during electrical fault conditions the entire water system becomes electrically hot.
We bond the interior water piping to the ground rods to prevent this from happening which is required in NEC 250-80 (a)
Also any other metal piping that may become energized shall be bonded to ground. NEC 250-80 (b)
Also structural steel buildings shall be bonded to ground. NEC 250-80 (c)

The NEC does require a ground rod for seperate buildings unless the 4 wire system is used to supply the building or if there is only one branch circuit supply to the building.
But the neutral and ground shall not be bonded together. NEC 250-24 (a)

The NEC also allows for the ground rods to be driven at a max angle of 45 degrees.
But it also allows for the ground rods to be installed flat in the bottom of a ditch that is a minimum od 2.5 feet deep.(NEC 250-83 (c)(3) and does call for the upper end of the electrode to be flush or below ground level unless provisions for protection are met.

There is also a grounding ring electrode that can be burried at a depth of not less than 2.5 feet and a minimum of at least 20 feet of #2 bare copper wire to be burried in a ditch. (NEC 250-81(d))
Here in WV we have a lot of rock that makes ground rods inpossible to install in many occasions.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

10 Ugly Ford Trucks That We Still Kinda Love

 Joe Kucinski
story-1

10 Things Every Truck Owner NEEDS (2026 Edition)

 Michael S. Palmer
story-2

Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-3

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-4

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-5

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-6

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-7

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-8

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-9

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
Old Mar 4, 2006 | 10:00 AM
  #9  
deidoman's Avatar
deidoman
New User
Joined: Feb 2006
Posts: 3
Likes: 0
deido

drive at a angel put two about 6to8feet apart that will ground the shop
run groung wire continoesly from one rod to next to box
use groun wire bare big strand and the rite nuts to atach wireto rods
 
Reply
Old Mar 5, 2006 | 05:18 PM
  #10  
Howdy's Avatar
Howdy
Posting Guru
25 Year Member
Joined: Jun 1999
Posts: 2,007
Likes: 0
From: Oregon
The basic rule as already posted is to drive the rod straight down. If it won't go straight down, drive at 45 deg. If you can't do that, bury horizontal.

I once spent an hour driving a rod down and it seemed to be going fine, other than really slow. I got done and turned around, then tripped on the point of the rod sticking straight up behind me. The rod went down a foot and ended up doing a 180, after hitting rock.

Too many times ground rods are cut at 4', (or less), because someone didn't work at it hard enough. (I'm sure I'm not the only one that's pulled up a two foot ground rod.) Sometimes they just won't go, granite and sandstone are two examples I can think of where they won't. Sometimes the ground just isn't very conductive.

One option is to use a chemical ground. You can buy them, but I've probably built a half dozon of them over the years. Pretty straight forward. I get the cad-weld/wire at the electrical supply and the pipe and bentonite from a pipe supply. I've used rock salt to fill.
http://www.erico.com/products/ChemRod.asp

http://www.pd-engineers.com/hicon.html
 

Last edited by Howdy; Mar 5, 2006 at 05:28 PM.
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
Cyrusjohn
1980 - 1986 Bullnose F100, F150 & Larger F-Series Trucks
13
Jun 24, 2017 08:30 AM
jaleus
Arkansas Chapter
0
Nov 13, 2016 06:11 AM
Bubba Jones
1994.5 - 1997 7.3L Power Stroke Diesel
5
May 19, 2016 09:08 AM
smashclash
1980 - 1986 Bullnose F100, F150 & Larger F-Series Trucks
3
Feb 23, 2012 06:34 PM
79FordBlake
1973 - 1979 F-100 & Larger F-Series Trucks
5
Jul 25, 2011 12:36 PM




All times are GMT -5. The time now is 08:17 PM.

story-0
10 Ugly Ford Trucks That We Still Kinda Love

Slideshow: 10 ugly Ford trucks that we still kinda love.

By Joe Kucinski | 2026-06-03 09:51:16


VIEW MORE
story-1
10 Things Every Truck Owner NEEDS (2026 Edition)

Slideshow: the best gifts for dads & grads

By Michael S. Palmer | 2026-06-03 15:43:58


VIEW MORE
story-2
Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-06-03 11:38:36


VIEW MORE
story-3
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-4
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-5
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-6
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-7
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-8
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-9
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE