When the power goes out I shut my main off & hook my gen to the 220 reciptical in my garage to power the house. It's a 6250 watt 10 horse. I have another gen a 5000 watt 10 horse. Can I hook the two together some way to get 11250 watts ? or would it burn them up ?
 
Reply
Old Oct 9, 2004 | 12:33 PM
  #2  
kotzy's Avatar
kotzy
Elder User
Joined: Apr 2004
Posts: 970
Likes: 3
You have a great question there? I don't know how you would get them in phase. This
calls for someone well versed in AC current.
 
Reply
Old Oct 9, 2004 | 01:23 PM
  #3  
Mike W's Avatar
Mike W
Post Fiend
Joined: Apr 2002
Posts: 7,157
Likes: 1
From: Central Kali
You really need a transfer switch to connect the generator to your house to be safe. Big generators have a means of getting them in sync for parallel operation. I would not attempt it with yours.
 
Reply
Old Oct 9, 2004 | 01:34 PM
  #4  
Old Fart's Avatar
Old Fart
Mountain Pass
Joined: Sep 2002
Posts: 161
Likes: 1
From: LAX, most of the time :)
Mike made a valid point - you really should be using a transfer switch to avoid accidentally backfeeding the utility. Not a good thing to do.

Paralleling isn't practical at this level - you're better off building a couple of small distribution panels and feeding the loads separately.
 
Reply
Old Oct 9, 2004 | 04:22 PM
  #5  
Torque1st's Avatar
Torque1st
Posting Legend
Joined: Sep 2001
Posts: 30,255
Likes: 37
Good points all. The two generators will fight each other. Not a good idea...
 
Reply
Old Oct 13, 2004 | 07:09 AM
  #6  
Ian F's Avatar
Ian F
Elder User
20 Year Member
Joined: Oct 2004
Posts: 512
Likes: 0
Yes, you would need a special controller to sync the generators' phase rotations. More or less, a phase monitor on both generator outputs will be linked to a throttle control on the secondary generator and adjust the engine speed to keep them in sync. Lot's of PLC programming involved (or you can spend mucho-$ to buy a pre-made control panel) and one generator would need to be fitted with an electronic speed control... As posted above, probably not practical for this application unless you are a computer hardware programmer or have access to someone who can do the programming.

By shutting your MCB off, you are in a sense creating a manual transfer switch which would prevent back-feeding. If you follow your SOP right, you won't have a problem. I've seen similar set-ups in commercial applications (and designed a few of them). Code would require it to be key-interlocked with a proper disconnect switch at the gen-set connection.

More importantly, what size receptacle are you plugging the generator into?
 
Reply
Old Oct 13, 2004 | 09:09 AM
  #7  
mark a.'s Avatar
mark a.
Thread Starter
|
Lead Driver
20 Year Member
Photogenic
Joined: Mar 2004
Posts: 8,922
Likes: 153
50 amp reciptical, 6 gage wire. One gen is 30 amp the other 20 amp.
 
Reply
Old Oct 14, 2004 | 06:37 AM
  #8  
jrs_big_ford_f150's Avatar
jrs_big_ford_f150
Posting Guru
Joined: Oct 2002
Posts: 1,301
Likes: 1
From: Dededo, Guam
I have to change the plug on my genset cord. Mine is a Generac 7550, 7550 continous running watts, 13,000 surge wattage. At 7550 watts by 240 volts that roughly equalls 33 amps of 240 VAC or 66 amps of 120 VAC. When our power goes out I turn off the main. I use a cord that connects the generator to the dryer outlet. Unfortunatly, the dryer outlet is only rated for 30 amps max. So I am going to buy a new plug to connect the genset to the stove outlet. That one is rated for 50 amps. It pays to be safe with electricity.

Mark, you would need some sort of device to synchonize both gensets. The smallest gensets I have seen that you could paralell are the diesel generators on a 110 foot Coast Guard Cutter. Each genset by itself is rated about 75 - 100 kW. If you do not have the gensets in phase you run a high risk of having one (or both) of your generators turning into the Spark-o-Matic. Not to mention you might fry some of your household devices, especially the electronic ones. I would follow Old Farts suggestion and install a couple of sub panels that would power seperate areas of your house while keeping the generators electrially isolated.

BTW here are some numbers for you on your generators. Calculated by using Ohm's Law.

Your 6250 watt genset :

MAximum genset output
240 Volts AC - 26 amps
120 Volts AC - 52 amps

Your 5000 Watt genset :

Maximum output
240 Volts AC - 20.8 Amps
120 Volts AC - 41.6 Amps

Hope this helps.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Fords at 2026 Carlisle Ford Nationals

 Joe Kucinski
story-1

3 Best / 3 Worst Parts of Modern Ford Ownership

 Brett Foote
story-2

10 Amazing Upgrades That Solve Common Ford Truck Owner Headaches

 Pouria Savadkouei
story-3

Every 2026 Ford Engine Explained

 Brett Foote
story-4

10 Ugly Ford Trucks That We Still Kinda Love

 Joe Kucinski
story-5

10 Things Every Truck Owner NEEDS (2026 Edition)

 Michael S. Palmer
story-6

Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-7

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-8

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-9

Top 10 Ford Truck Tragedies

 Joe Kucinski
Old Oct 14, 2004 | 09:11 AM
  #9  
Ian F's Avatar
Ian F
Elder User
20 Year Member
Joined: Oct 2004
Posts: 512
Likes: 0
Originally Posted by jrs_big_ford_f150
Unfortunatly, the dryer outlet is only rated for 30 amps max. So I am going to buy a new plug to connect the genset to the stove outlet. That one is rated for 50 amps. It pays to be safe with electricity.
I assume you're checking wire size?

A 30A receptacle would typically be wired with #10 AWG copper wire. A 50A receptacle would need #6's, although you can get away with #8's in a pinch.
 
Reply
Old Oct 14, 2004 | 02:16 PM
  #10  
f4fran's Avatar
f4fran
Senior User
25 Year Member
Joined: Aug 2000
Posts: 153
Likes: 0
From: Ossipee, NH
Originally Posted by jrs_big_ford_f150
I have to change the plug on my genset cord. Mine is a Generac 7550, 7550 continous running watts, 13,000 surge wattage....

Your 6250 watt genset :

MAximum genset output
240 Volts AC - 26 amps
120 Volts AC - 52 amps

Your 5000 Watt genset :

Maximum output
240 Volts AC - 20.8 Amps
120 Volts AC - 41.6 Amps

Hope this helps.
Mark a, as jrs_big_ford_f150 indicated above, his genset is double rated (continuous and surge). From all the research I've done regarding engine selection and generator output, you need to have 1 HP for every 500 continuous watts output. Based on this fact, you may actually have two 5000 continuous watt output generators. Often times the manufacturers get over zealous and show the surge rating (similar to air compressor manufacturers). That 6250 watt gen sounds about right for a surge rating for a 10 HP engine.

Fran
 
Reply
Old Oct 14, 2004 | 02:54 PM
  #11  
mark a.'s Avatar
mark a.
Thread Starter
|
Lead Driver
20 Year Member
Photogenic
Joined: Mar 2004
Posts: 8,922
Likes: 153
My mistake, the bigger one is 5250 running & 7350 surge. The other is 5000 running & 6250 surge. However they are both 10 horse. If I isolated them is it ok to run them into the same ground ? I want to be able to run the water heater & I'd use one for that & the other for the house.
 
Reply
Old Oct 14, 2004 | 03:04 PM
  #12  
Old Fart's Avatar
Old Fart
Mountain Pass
Joined: Sep 2002
Posts: 161
Likes: 1
From: LAX, most of the time :)
You actually are _required_ to run them to the same ground.
 
Reply
Old Oct 14, 2004 | 04:14 PM
  #13  
jrs_big_ford_f150's Avatar
jrs_big_ford_f150
Posting Guru
Joined: Oct 2002
Posts: 1,301
Likes: 1
From: Dededo, Guam
Originally Posted by Ian F
I assume you're checking wire size?

A 30A receptacle would typically be wired with #10 AWG copper wire. A 50A receptacle would need #6's, although you can get away with #8's in a pinch.
Oh yeah, the wire is 8 guage for the genset cord. If need be I will go buy some thicker cable. I am just getting the plug for now since my genset produces more amps than the current outlet I am using to tie in the genset can handle. The house receptacles are already wired. I am just changing which circuit that will backfeed my main breakers and power the house.

Mark,
The same ground is ideal. But if you can't get them to the same grounding point, remember a ground is better than no ground at all.
 
Reply
Old Oct 14, 2004 | 05:23 PM
  #14  
Lou Braun's Avatar
Lou Braun
Fleet Mechanic
20 Year Member
Joined: Nov 2003
Posts: 1,372
Likes: 14
From: West Cornwall, CT
Club FTE Gold Member
If you want to run both of your generators at the same time, it would be best to run each one on its own dedicated circuit. Don't try to run them in parallel on the same circuit.

Getting the two generators paralleled initially would be a bear. You need to have phase indicators for the two units and be able to close a breaker when the units are in phase. After paralleling, you would need to figure out how to make them share the AC load. The AC generators running in parallel would need to have almost identical speed and voltage droop characteristics to work well together. Most likely one of them would end up as a load on the other generator. File this one in the "too hard" category.

I'd just run the larger unit on the house and keep the second one as a spare.

Lou Braun
 
Reply
Old Oct 15, 2004 | 09:41 AM
  #15  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
File this under "unsafe" at best. Kill a lineman, go to jail.
 
Reply



All times are GMT -5. The time now is 05:42 AM.

story-0
Top 10 Fords at 2026 Carlisle Ford Nationals

Slideshow: Top 10 Fords at 2026 Ford Nationals

By Joe Kucinski | 2026-06-09 11:10:08


VIEW MORE
story-1
3 Best / 3 Worst Parts of Modern Ford Ownership

Based on years of owning multiple modern Ford products.

By Brett Foote | 2026-06-09 10:53:36


VIEW MORE
story-2
10 Amazing Upgrades That Solve Common Ford Truck Owner Headaches

SPONSORED: From muddy boots to rain-soaked cargo, these upgrades address some of the most common frustrations Ford truck owners face every day.

By Pouria Savadkouei | 2026-06-08 18:50:34


VIEW MORE
story-3
Every 2026 Ford Engine Explained

Here's everything you need to know about every Ford engine available for the 2026 model year.

By Brett Foote | 2026-06-05 12:58:01


VIEW MORE
story-4
10 Ugly Ford Trucks That We Still Kinda Love

Slideshow: 10 ugly Ford trucks that we still kinda love.

By Joe Kucinski | 2026-06-03 09:51:16


VIEW MORE
story-5
10 Things Every Truck Owner NEEDS (2026 Edition)

Slideshow: the best gifts for dads & grads

By Michael S. Palmer | 2026-06-03 15:43:58


VIEW MORE
story-6
Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-06-03 11:38:36


VIEW MORE
story-7
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-8
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-9
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE