Also, if one considers the pressure difference between a "perfect vacuum" (0 PSIA, which is actually unobtainable in the real world) versus 250 PSIG of nitrogen, well, we're talking a Delta of over 200 PSIG, and I'll take the pressure over the vacuum any day of the week!
In the past 30+ years I've worked for three different HVAC manufacturers, and all of them test for leaks using nitrogen. Of course this doesn't tell you if there's moisture in the system, but..."At least you know the moisture that's in there won't leak out", as one of my coworkers from Way Back used to say! (That was a joke, and no. We didn't ship anything with moisture in it!)
And on the moisture thing, other than replacing the dryer, isnt the fix to pull vacuum for many hours?
And on the moisture thing, other than replacing the dryer, isnt the fix to pull vacuum for many hours?
With regards to pulling a system into a vacuum, the amount of time doesn't matter as long as you're able to monitor the micron level (amount of vacuum), and make sure it's stable. Let me see if I can explain it this way: If, for example, you're located in Salt Lake City (very little humidity), and the system is only open for a short amount of time, very little moisture will gain access to the system, and the amount of time needed to pull a "deep vac" will be much less than a similar job being performed in, say, New Orleans, or Houston (much higher humidity). However, if that same system in Salt Lake City is left open to the atmosphere for a long period of time (an hour, a day, a week, etc), moisture will get into the system, and then a longer vacuum will be needed. How long? Who knows!
In other words, in order to do the job properly, it's not the amount of time that a system is put under vacuum, but the amount of moisture that's in the system that needs to be monitored, and thus the need for a micron gauge. Heck, I've worked on cars that only needed 45 minutes of vacuum, while on others I let it run overnight, and then had to change the oil in my vacuum pump so I could run it some more the next day. Everything is relative....
Now I know a lot of people here say, "I put it on a vacuum for (X) hours, and it's working just fine." Good for them, and I hope it runs that way forever!
But no one reports back here and admits they (unknowingly) left moisture in the system and scrambled a perfectly good compressor. Or worse.
With regards to pulling a system into a vacuum, the amount of time doesn't matter as long as you're able to monitor the micron level (amount of vacuum), and make sure it's stable. Let me see if I can explain it this way: If, for example, you're located in Salt Lake City (very little humidity), and the system is only open for a short amount of time, very little moisture will gain access to the system, and the amount of time needed to pull a "deep vac" will be much less than a similar job being performed in, say, New Orleans, or Houston (much higher humidity). However, if that same system in Salt Lake City is left open to the atmosphere for a long period of time (an hour, a day, a week, etc), moisture will get into the system, and then a longer vacuum will be needed. How long? Who knows!
In other words, in order to do the job properly, it's not the amount of time that a system is put under vacuum, but the amount of moisture that's in the system that needs to be monitored, and thus the need for a micron gauge. Heck, I've worked on cars that only needed 45 minutes of vacuum, while on others I let it run overnight, and then had to change the oil in my vacuum pump so I could run it some more the next day. Everything is relative....
Now I know a lot of people here say, "I put it on a vacuum for (X) hours, and it's working just fine." Good for them, and I hope it runs that way forever!
But no one reports back here and admits they (unknowingly) left moisture in the system and scrambled a perfectly good compressor. Or worse.
I know its not proper, but its unbearable in the summer when its wet and hot and being that it worked at all was enough for me to dothat lol.
My silverado works too, but the belt is slipping due to age and bad tensioner. gm wants almost 200 for a tensioner for a single belt. im gonna use a stretch belt to make that cheaper on me.
I am also gonna do the mod to turn off the heater core when the f150 ac is on, i also need to fix the check valve for the aC because it will periodically run out of vacuum at sustained throttle and i need to reset my switch when i let off to get it back
I know its not proper, but its unbearable in the summer when its wet and hot and being that it worked at all was enough for me to dothat lol.