Powerboost 7.2kw generator

I have the new Powerboost with the 7.2kw generator. I have a plug in my home electrical panel to run my house off my stand alone generator. It works great, but when I try to run my house off the F150's generator, the message center says ground fault, and it wont power the house. Both generator's are the same wattage. The plug's are the same. Anyone have any ideas? Attached is a pic of the plug in my house. The truck generator powers an RV just fine, so I know it works.

 
Reply
Old Mar 31, 2021 | 12:10 PM
  #2  
NoImMad's Avatar
NoImMad
Junior User
Joined: Feb 2021
Posts: 63
Likes: 9
The Propower is "also likely a floating ground" WRONG ! and the house not. The RV would likely be a floating ground as well.
I am not knowledgeable enough to tell you what to do about it, I know just enough to know that I do not fully understand the grounding requirements,
MAKE SURE that you have the correct isolating hardware when you use a generator, any generator, even your truck, on any house connected to the grid.
It is extremely DANGEROUS not to
 

Last edited by NoImMad; Apr 19, 2021 at 05:29 PM. Reason: bad info
Reply
Old Apr 16, 2021 | 04:43 PM
  #3  
UFMCGATOR's Avatar
UFMCGATOR
New User
Joined: Apr 2021
Posts: 1
Likes: 0
Literally having the same problem with the ground fault. Any help here would be great!!
 
Reply
Old Apr 16, 2021 | 05:40 PM
  #4  
Ford75115's Avatar
Ford75115
Thread Starter
|
Trailering
Joined: Sep 2010
Posts: 16
Likes: 1
An electrician told me to try running a wire from the frame to a ground rod in the ground. Still get the same error. Guess I'll have to have them come out and see what they come up with.
 
Reply
Old Apr 19, 2021 | 04:03 PM
  #5  
seventyseven250's Avatar
seventyseven250
Lead Driver
20 Year Member
Community Favorite
Joined: Jun 2005
Posts: 8,463
Likes: 724
From: Calgary Canada
Something to do with grounding/bonding I'm sure.
 
Reply
Old Apr 19, 2021 | 04:22 PM
  #6  
ford390gashog's Avatar
ford390gashog
Fleet Owner
20 Year Member
Liked
Loved
Community Favorite
Joined: Jan 2004
Posts: 26,007
Likes: 575
From: Brentwood,CA
Club FTE Gold Member
Well the truck is being too cautious. This problem is because the neutral and ground are bonded at the service entrance and in the truck. You need to lose the ground wire that goes back to the truck. These trucks are setup to be OSHA GFCI compliant.
 
Reply
Old Apr 19, 2021 | 04:27 PM
  #7  
ford390gashog's Avatar
ford390gashog
Fleet Owner
20 Year Member
Liked
Loved
Community Favorite
Joined: Jan 2004
Posts: 26,007
Likes: 575
From: Brentwood,CA
Club FTE Gold Member
Originally Posted by Ford75115
An electrician told me to try running a wire from the frame to a ground rod in the ground. Still get the same error. Guess I'll have to have them come out and see what they come up with.
Concerned a electrician said this. A ground rod is strictly to provide a electrical path to dissipate a static discharge voltage (which can be lightning or other forms of static electricity) to the earth.
 
Reply
Old Apr 19, 2021 | 04:35 PM
  #8  
muhford's Avatar
muhford
Fleet Mechanic
10 Year Member
Liked
Loved
Community Favorite
Joined: Mar 2014
Posts: 1,268
Likes: 127
From: Missouri
Originally Posted by ford390gashog
Well the truck is being too cautious. This problem is because the neutral and ground are bonded at the service entrance and in the truck. You need to lose the ground wire that goes back to the truck. These trucks are setup to be OSHA GFCI compliant.
This would be my best guess too. Most generators come bonded and you can't bond your neutral twice. A good generator will let you remove the bond. Hopefully Ford was smart enough to include this feature.

Originally Posted by NoImMad
MAKE SURE that you have the correct isolating hardware when you use a generator, any generator, even your truck, on any house connected to the grid.
It is extremely DANGEROUS not to
Ditto. You can kill a lineman pretty quickly.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-1

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-2

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-3

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-4

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-5

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-6

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-7

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-8

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-9

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
Old Apr 19, 2021 | 04:47 PM
  #9  
Ford75115's Avatar
Ford75115
Thread Starter
|
Trailering
Joined: Sep 2010
Posts: 16
Likes: 1
Am electrician set up my home to run it off a backup gen and has worked fine for years.
 
Reply
Old Apr 19, 2021 | 05:26 PM
  #10  
NoImMad's Avatar
NoImMad
Junior User
Joined: Feb 2021
Posts: 63
Likes: 9
worth a read to any wishing to understand the issue a little better

https://www.electricgeneratorsdirect...d-Neutral.html
 
Reply
Old Apr 19, 2021 | 05:46 PM
  #11  
Ford75115's Avatar
Ford75115
Thread Starter
|
Trailering
Joined: Sep 2010
Posts: 16
Likes: 1
Ford's product specialist is supposed to get in contact with me to see what is needed. I'll post when I get it resolved.
 
Reply
Old Apr 19, 2021 | 06:17 PM
  #12  
NoImMad's Avatar
NoImMad
Junior User
Joined: Feb 2021
Posts: 63
Likes: 9
Originally Posted by Ford75115
Ford's product specialist is supposed to get in contact with me to see what is needed. I'll post when I get it resolved.
to plug the truck directly to the house you will need a transfer switch, BUT the correct kind, GFI protected
The Propower to my understanding was specifically designed with contractors in mind and needs to comply with certain codes to be kosher, hence the GFCI protected outlets on the truck, which are the source of your problems.
A simple way around it, is just use extension cords from the truck to the items you want to run in the house.
THE proper way is the correctly installed transfer switch
MY WAY, specific to my personal needs and I am not vouching for it, was a heavy duty full sub panel, breakers and all, on 40 feet of appropriately sized cable that I plugged into the 240 V outlet on my construction grade generators. Then I powered what I wanted off of that panel. The advantage being no spaghetti of cables coming from generator and a set up that I could use on any of the multitude of generators I had over the years. Still have the cable and panel and I now use it as a sub panel in the garage that I can plug into the 240 volt plug for my hybrid car plug in charger.
Most important, get right ! don't cut corners with electricity
 
Reply
Old Apr 19, 2021 | 06:29 PM
  #13  
muhford's Avatar
muhford
Fleet Mechanic
10 Year Member
Liked
Loved
Community Favorite
Joined: Mar 2014
Posts: 1,268
Likes: 127
From: Missouri
Originally Posted by NoImMad
to plug the truck directly to the house you will need a transfer switch, BUT the correct kind, GFI protected
The Propower to my understanding was specifically designed with contractors in mind and needs to comply with certain codes to be kosher, hence the GFCI protected outlets on the truck, which are the source of your problems.
A simple way around it, is just use extension cords from the truck to the items you want to run in the house.
THE proper way is the correctly installed transfer switch
MY WAY, specific to my personal needs and I am not vouching for it, was a heavy duty full sub panel, breakers and all, on 40 feet of appropriately sized cable that I plugged into the 240 V outlet on my construction grade generators. Then I powered what I wanted off of that panel. The advantage being no spaghetti of cables coming from generator and a set up that I could use on any of the multitude of generators I had over the years. Still have the cable and panel and I now use it as a sub panel in the garage that I can plug into the 240 volt plug for my hybrid car plug in charger.
Most important, get right ! don't cut corners with electricity
GFIs aren't a be all end all. They are only required because manufacturers and the city make money by doing so.

Is your sub panel properly bonded?
 
Reply
Old Apr 19, 2021 | 06:51 PM
  #14  
ponykilr's Avatar
ponykilr
Posting Guru
Joined: Jan 2015
Posts: 1,001
Likes: 8
From: NC Mountains
Originally Posted by muhford
GFIs aren't a be all end all. They are only required because manufacturers and the city make money by doing so.

Is your sub panel properly bonded?
Sub panels are never to be bonded in the panel, all bonding must take place in the main panel/service entrance. Neutrals and grounds must be separate in any sub panel.

Some/most generators have a floating neutral. It is explained here much better than I can. Depending on which you have the wiring will have to be matched. I do not know how the Ford truck is set up but since it was designed for contractors I would say it is a bonded neutral.

https://generatorbible.com/blog/bond...ating-neutral/
 
Reply
Old Apr 19, 2021 | 06:57 PM
  #15  
muhford's Avatar
muhford
Fleet Mechanic
10 Year Member
Liked
Loved
Community Favorite
Joined: Mar 2014
Posts: 1,268
Likes: 127
From: Missouri
Originally Posted by ponykilr
Sub panels are never to be bonded in the panel, all bonding must take place in the main panel/service entrance. Neutrals and grounds must be separate in any sub panel.

Some/most generators have a floating neutral. It is explained here much better than I can. Depending on which you have the wiring will have to be matched. I do not know how the Ford truck is set up but since it was designed for contractors I would say it is a bonded neutral.

https://generatorbible.com/blog/bond...ating-neutral/
My comment wasn't referring to OP. It was referring to the comment that I quoted.
 
Reply



All times are GMT -5. The time now is 11:33 AM.

story-0
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-1
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-2
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-3
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-4
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-5
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-6
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-7
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-8
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-9
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE