Washing Machine is shocking me

I was trying to wiggle a shim under there to level the thing while it was on spin when it tickled me with a little jolt of electricity.

I suspect the outlet isn't grounded. I asked my father-in law to help me rewire a few weeks ago, but when I was putting the face plates on I noticed a lot of the green screws on the receptacles were not connected to anything.

I want to know if I can ground the green screw on the receptacle to the back of the metal box? Or do I need to run a whole new circuit to the breaker panel?
 
Reply
Old Feb 17, 2008 | 03:37 PM
  #2  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
Yes,you can add a wire from the green screw to the box.

Normally the ground wire is long enough that is gets fastened down to the box then continues on to the green screw on the receptacle instead of thinking just the mounting of the receptacle to the box is good enough.
 
Reply
Old Feb 17, 2008 | 03:54 PM
  #3  
websthes's Avatar
websthes
Thread Starter
|
Postmaster
Joined: Mar 2002
Posts: 2,680
Likes: 1
From: Montreal Canada
There is no ground wire. My house was built in 1959 and much of the house hasn't been re-wired. My father in law did some re-wiring when we re-modeled the kitchen, but other rooms he just swapped out the old 2-hole receptacles with new three holed ones and grounded it on the metal box. Can I do the same for the washer, put in a new receptacle and ground it on the metal box instead of running a new wire all the way to the breaker panel?
 
Reply
Old Feb 17, 2008 | 04:24 PM
  #4  
tjc transport's Avatar
tjc transport
i ain't rite
Joined: Mar 2005
Posts: 65,623
Likes: 5,633
From: Marlboro Mental Hospital.
Club FTE Gold Member
you can, but it will not do anything.
if there is no ground wire in the system(2 wire system)
there is no ground. period.
 
Reply
Old Feb 17, 2008 | 04:38 PM
  #5  
Snowbunny's Avatar
Snowbunny
Post Fiend
Joined: Mar 2007
Posts: 8,770
Likes: 14
From: The Great North~West!
I would take this as a sign to never do laundry again!!!
 
Reply
Old Feb 17, 2008 | 05:05 PM
  #6  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
I suspect that wire is cloth wrapped then.

Is there a galvanized metal water source pipe near by ?

you can ground it to that .
 
Reply
Old Feb 17, 2008 | 05:27 PM
  #7  
70blue's Avatar
70blue
Logistics Pro
20 Year Member
Joined: Apr 2005
Posts: 4,447
Likes: 0
From: Georgia
Originally Posted by Snowbunny
I would take this as a sign to never do laundry again!!!
I like the way your thinking.

Seriously I would replace those old wires with grounded ones. You could make it safer by getting a roll of ground wire and running it from the ground strip in your box to your ungrounded outlets but I would prefer replacing the obsolete wiring in the system especially if its the cloth covered stuff. You should really let your local codes decide the remedy. If you want to ground that washer hard fast and ugly right now till you can run proper grounds attach a 12 gauge wire on the washer with one of the case screws and run it to the nearest metal water pipe that has a continuos run to earth. I would also get to the bottom of why the washer is shocking you. Even without a proper ground it should not have current in the case.
 
Reply
Old Feb 17, 2008 | 11:51 PM
  #8  
ford2go's Avatar
ford2go
Cargo Master
20 Year Member
Photogenic
Liked
Loved
Joined: Apr 2003
Posts: 3,476
Likes: 224
From: Frequently frozen MN
I agree with fix the problem soon -- for safety's sake. Even if you quit doing the laundry you might touch the machine --if you happen to use it to store empty beer cans

As for why you're getting shocked -- most likely it's because you're somehow connecting the hot line from your outlet to the ground side of your washer. Not hard to have that happen in your setup. I would recommend that you get all of your outlets straightened out somehow. Your setup sounds very dangerous.

good luck,

ford2go
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

10 Ways Ford is LOSING to the Competition

 Joe Kucinski
story-1

Top 6 Best Deals Available on New Fords & Lincolns Right Now

 Brett Foote
story-2

This Hennessey Takes the Expedition Tremor's Off-Roading Capability to the Next Level

 Verdad Gallardo
story-3

Top 10 Fords at 2026 Carlisle Ford Nationals

 Joe Kucinski
story-4

3 Best / 3 Worst Parts of Modern Ford Ownership

 Brett Foote
story-5

10 Amazing Upgrades That Solve Common Ford Truck Owner Headaches

 Pouria Savadkouei
story-6

Every 2026 Ford Engine Explained

 Brett Foote
story-7

10 Ugly Ford Trucks That We Still Kinda Love

 Joe Kucinski
story-8

10 Things Every Truck Owner NEEDS (2026 Edition)

 Michael S. Palmer
story-9

Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
Old Feb 18, 2008 | 08:18 AM
  #9  
jimdandy's Avatar
jimdandy
Posting Guru
Joined: Feb 2006
Posts: 1,448
Likes: 1
Connecting electrical wiring to water pipes is a no-no. If you wind up with a "floating neutral" you can turn your faucets into death traps. For 120 circuits, there are three wires involved, a black, white, and bare copper. The bare copper is grounded to a ground rod at the transformer pole. The black is hot, and the white is neutral or ac ground. The neutral and ground are tied together somewhere in the system, usually at the transformer pole. If this connection gets broken, you wind up with a floating neutral, a very dangerous situation. If the black and white get reversed somewhere in the wiring, you have a dangerous situation. I would get some input from an electrician before electrocuting the entire household. jd
 
Reply
Old Feb 18, 2008 | 08:46 AM
  #10  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,768
Likes: 1,082
From: St Louis
In the meantime, you can install a GFCI outlet for the washer to protect whomever is going to be the guinea pig.

Yes, GFCI outlets will work even on a two-wire receptacle.

Stev
 
Reply
Old Feb 18, 2008 | 08:53 AM
  #11  
Lead Head's Avatar
Lead Head
Lead Driver
15 Year Member
Photogenic
Joined: Jul 2007
Posts: 7,868
Likes: 9
From: Rhode Island
Originally Posted by jimdandy
Connecting electrical wiring to water pipes is a no-no. If you wind up with a "floating neutral" you can turn your faucets into death traps. For 120 circuits, there are three wires involved, a black, white, and bare copper. The bare copper is grounded to a ground rod at the transformer pole. The black is hot, and the white is neutral or ac ground. The neutral and ground are tied together somewhere in the system, usually at the transformer pole. If this connection gets broken, you wind up with a floating neutral, a very dangerous situation. If the black and white get reversed somewhere in the wiring, you have a dangerous situation. I would get some input from an electrician before electrocuting the entire household. jd
Not sure about you, but in my house, which was built in 1990, and is to spec, the groudning strap is connected to both the copper water lines, and a spike outisde the house.
 
Reply
Old Feb 18, 2008 | 09:09 AM
  #12  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,768
Likes: 1,082
From: St Louis
deleted - duplicate
 
Reply
Old Feb 18, 2008 | 09:14 AM
  #13  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,768
Likes: 1,082
From: St Louis
Jimdandy is correct.

Simply tying a ground wire to any cold water line, under NEC for those under its jurisdiction, is strictly verboten.

See NEC Sec 250-130(c) for permissible connection points.

Yes, both your water lines are connected to the ground electrode system (also a requirement), but it is not permissible to use them to extend the grounding system.

It is simplest to follow my suggestion with is fully allowed under NEC.

Steve
 
Reply
Old Feb 18, 2008 | 09:17 AM
  #14  
tewferford's Avatar
tewferford
Post Fiend
Joined: Oct 2006
Posts: 7,269
Likes: 0
From: Where's my map???
Originally Posted by Lead Head
Not sure about you, but in my house, which was built in 1990, and is to spec, the groudning strap is connected to both the copper water lines, and a spike outisde the house.
What your saying is fine if everything is wired correctly. If it is not, and the hot wire is switched to the nuetral side. You could get electricuted just by turning on a faucet. I would run a new line from the breaker/fuse box to the washer with a GFCI outlet.
 
Reply
Old Feb 18, 2008 | 09:22 AM
  #15  
Lead Head's Avatar
Lead Head
Lead Driver
15 Year Member
Photogenic
Joined: Jul 2007
Posts: 7,868
Likes: 9
From: Rhode Island
OffTopic: Something in my basement seems to be leaking quite a bit of power to ground. Between the ground prong, and my basement floor, reads around 20-30 vAC. Kind of odd.
 
Reply



All times are GMT -5. The time now is 02:57 PM.

story-0
10 Ways Ford is LOSING to the Competition

Slideshow: 10 ways Ford is losing to the competition

By Joe Kucinski | 2026-06-15 09:52:01


VIEW MORE
story-1
Top 6 Best Deals Available on New Fords & Lincolns Right Now

Some great targets in today's expensive world.

By Brett Foote | 2026-06-15 09:35:19


VIEW MORE
story-2
This Hennessey Takes the Expedition Tremor's Off-Roading Capability to the Next Level

Slideshow: The VelociRaptor Expedition gains a lift, upgraded suspension, Brembo brakes, and trail-ready equipment while retaining the stock 440-horsepower EcoBoost V6.

By Verdad Gallardo | 2026-06-12 11:01:55


VIEW MORE
story-3
Top 10 Fords at 2026 Carlisle Ford Nationals

Slideshow: Top 10 Fords at 2026 Ford Nationals

By Joe Kucinski | 2026-06-09 11:10:08


VIEW MORE
story-4
3 Best / 3 Worst Parts of Modern Ford Ownership

Based on years of owning multiple modern Ford products.

By Brett Foote | 2026-06-09 10:53:36


VIEW MORE
story-5
10 Amazing Upgrades That Solve Common Ford Truck Owner Headaches

SPONSORED: From muddy boots to rain-soaked cargo, these upgrades address some of the most common frustrations Ford truck owners face every day.

By Pouria Savadkouei | 2026-06-08 18:50:34


VIEW MORE
story-6
Every 2026 Ford Engine Explained

Here's everything you need to know about every Ford engine available for the 2026 model year.

By Brett Foote | 2026-06-05 12:58:01


VIEW MORE
story-7
10 Ugly Ford Trucks That We Still Kinda Love

Slideshow: 10 ugly Ford trucks that we still kinda love.

By Joe Kucinski | 2026-06-03 09:51:16


VIEW MORE
story-8
10 Things Every Truck Owner NEEDS (2026 Edition)

Slideshow: the best gifts for dads & grads

By Michael S. Palmer | 2026-06-03 15:43:58


VIEW MORE
story-9
Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-06-03 11:38:36


VIEW MORE