Window A/C Connection Question

A friend on mines wife just bought him an wiindow a/c unit inwhich he installed.

The problem is that the 3 prong outlet is NOT grounded.

His son was barefooted on the cement slab outside and touched the a/c unit and got a slight tingling sensation.

We got his pen type non-contact tester and put it near the a/c unit.

It lit up.

There's a ground wire disconnected inside his electrical panel.

I won't go inside to re-attach it because there's no main breaker to shut off the power.

Maybe I'll run a ground wire from the outlet to the nearest cold water pipe.

Would that help?

Is there a danger of a severe electrical shock if the a/c unit is ungrounded ?
 

Last edited by sierraben; Jul 3, 2005 at 11:08 PM. Reason: add
Reply
Old Jul 4, 2005 | 09:06 AM
  #2  
Crash687's Avatar
Crash687
Posting Guru
Joined: Mar 2004
Posts: 1,321
Likes: 2
From: MI
yes there is a danger of electrical shock if there is no ground. you should only have to turn off that circut, but first test it for ground/shorts using an multi-meter before connecting the ground. if you are not sure of what to do call a licensed electrician.
 
Reply
Old Jul 4, 2005 | 09:36 AM
  #3  
Greg 79 f150's Avatar
Greg 79 f150
Postmaster
Joined: Feb 2003
Posts: 2,848
Likes: 1
From: Kentucky
Originally Posted by sierraben
A friend on mines wife just bought him an wiindow a/c unit inwhich he installed.

The problem is that the 3 prong outlet is NOT grounded.

His son was barefooted on the cement slab outside and touched the a/c unit and got a slight tingling sensation.

We got his pen type non-contact tester and put it near the a/c unit.

It lit up.

There's a ground wire disconnected inside his electrical panel.

I won't go inside to re-attach it because there's no main breaker to shut off the power.

Maybe I'll run a ground wire from the outlet to the nearest cold water pipe.

Would that help?

Is there a danger of a severe electrical shock if the a/c unit is ungrounded ?

Holy Moly ! Yes as said above , get a circuit to it that carrys a equipment grounding conductor in it. I would recommend shutting that ac down now, it may go full voltage to the frame at any time, and will not trip the fuse/breaker.. The equipment ground is meant to take any fault current in an appliance to earth ground, causing a overcurrent draw which will then trip the circuit protection. That unit has a serious voltage to ground fault in it now, which is probaly as high as 90 volts, if a neon test light lit, and a human felt it also. I can feel 50 volt ac in my hand when grounded,
 

Last edited by Greg 79 f150; Jul 4, 2005 at 09:40 AM.
Reply
Old Jul 4, 2005 | 09:45 AM
  #4  
220k-f-150's Avatar
220k-f-150
Senior User
Joined: Apr 2003
Posts: 243
Likes: 0
I am not an electrician, but I don't believe a new a/c should be giving any shock, unless its not wired correctly. Is it 110 or 220? Check to make sure that the outlet and A/c pigtail are wired correctly. I would get an electrician if your that uncomfortable. There are too many things that we cannot see that could be doing this.
 
Reply
Old Jul 4, 2005 | 10:02 AM
  #5  
TigerDan's Avatar
TigerDan
Hotshot
Joined: May 2004
Posts: 12,170
Likes: 5
From: The hills of No. Calif.
Club FTE Gold Member
First of all Ben, what are you doing with A/C in the Bay Area? Did it get up to a scorching 80 degrees there and you guys are all burning up?

Seriously, you need to get that ground wire hooked up, and soon! If you can see it disconnected in the main panel, then it's easy to see where it goes but I have to wonder whay it was disconnected in the first place. Maybe there's a short and it trips the breaker, and that was someone's idea of a quick fix.

Anyway, some good advice above, if you're not comfortable messing with it, have your friend get someone who is. If you like, I can PM you with a contact for an old friend down there who has a home fix-it type of business and does that sort of thing all the time. Let me know, -TD
 
Reply
Old Jul 4, 2005 | 12:04 PM
  #6  
rebocardo's Avatar
rebocardo
Post Fiend
Joined: Jun 2002
Posts: 13,873
Likes: 3
From: Atlanta GA
> Maybe there's a short and it trips the breaker, and that was someone's idea of a quick fix

I agree. Plus, you may have another device that is actually at fault on that circuit causing the problem since the A/C unit is new.

On a house I am buying, not only was the bathroom circuit not GFCI, it was hot/neu. reversed

When you see one bozo fix you have to assume it is done throughout the house.
 
Reply
Old Jul 4, 2005 | 02:13 PM
  #7  
sierraben's Avatar
sierraben
Thread Starter
|
Post Fiend
Joined: Mar 2004
Posts: 24,418
Likes: 3
From: San Francisco, Ca.
Club FTE Silver Member

Originally Posted by TigerDan
First of all Ben, what are you doing with A/C in the Bay Area? Did it get up to a scorching 80 degrees there and you guys are all burning up?

Seriously, you need to get that ground wire hooked up, and soon! If you can see it disconnected in the main panel, then it's easy to see where it goes but I have to wonder whay it was disconnected in the first place. Maybe there's a short and it trips the breaker, and that was someone's idea of a quick fix.

Anyway, some good advice above, if you're not comfortable messing with it, have your friend get someone who is. If you like, I can PM you with a contact for an old friend down there who has a home fix-it type of business and does that sort of thing all the time. Let me know, -TD
A/C in S.F.? Un-heard of.

It's a buddy of mine in San Anselmo, Ca.

I'm going to forward these posts to him.

I'm just wondering why a ground wire was disconnected inside his circuit breaker box.

I never seen a circuit panel with NO main circuit breakers.

I guess he could pop off the meter. Naw!

I'll tell him to call an electrician instead.

A/C in S.F.? Un-heard of.

And thankyou everyone for your input on this serious matter.

I will call him tonight and tell him to unplug it and get it fixed right.
 
Reply
Old Jul 4, 2005 | 02:17 PM
  #8  
sierraben's Avatar
sierraben
Thread Starter
|
Post Fiend
Joined: Mar 2004
Posts: 24,418
Likes: 3
From: San Francisco, Ca.
Club FTE Silver Member

Originally Posted by 220k-f-150
I am not an electrician, but I don't believe a new a/c should be giving any shock, unless its not wired correctly. Is it 110 or 220? Check to make sure that the outlet and A/c pigtail are wired correctly. I would get an electrician if your that uncomfortable. There are too many things that we cannot see that could be doing this.
It's 110 and the outlet is wired correctly; just no ground. Most of the house has un-grounded outlets including their computers.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-1

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-2

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-3

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-4

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
story-5

Top 10 Ford Trucks Coming to Mecum Indy 2026

 Brett Foote
story-6

5 Best / 5 Worst Ford Truck Wheels of All Time

 Joe Kucinski
story-7

Ford Super Duty: 5 Things Owners LOVE, 5 Things They LOATHE!

 Joe Kucinski
story-8

Every 2026 Ford Truck Engine RANKED from WORST to FIRST!

 Michael S. Palmer
story-9

The Best F-150 Deal of Every Trim Level (XL through Raptor)

 Joe Kucinski
Old Jul 4, 2005 | 02:47 PM
  #9  
220k-f-150's Avatar
220k-f-150
Senior User
Joined: Apr 2003
Posts: 243
Likes: 0
What we are trying to say is the A/C, with or without the ground wire hooked up, should not be giving a shock. The ground is there in case there is a short somewhere in the A/C or outlet. As some pointed out earlier, why is the ground wire disconnected? There could also be a short in the run to the outlet or something else plugged into outlet. Is the A/C unit new or used? Gotta run. Finally getting some rain or at least a storm. Good Luck.
 
Reply
Old Jul 4, 2005 | 02:56 PM
  #10  
sierraben's Avatar
sierraben
Thread Starter
|
Post Fiend
Joined: Mar 2004
Posts: 24,418
Likes: 3
From: San Francisco, Ca.
Club FTE Silver Member

Originally Posted by 220k-f-150
What we are trying to say is the A/C, with or without the ground wire hooked up, should not be giving a shock. The ground is there in case there is a short somewhere in the A/C or outlet. As some pointed out earlier, why is the ground wire disconnected? There could also be a short in the run to the outlet or something else plugged into outlet. Is the A/C unit new or used? Gotta run. Finally getting some rain or at least a storm. Good Luck.
Friends A/C unit is new.

I to am also wondering why the ground wire is disconnected.

Previous owner did do some gonzo-bozo electrical work.
 
Reply
Old Jul 4, 2005 | 03:26 PM
  #11  
Greg 79 f150's Avatar
Greg 79 f150
Postmaster
Joined: Feb 2003
Posts: 2,848
Likes: 1
From: Kentucky
Originally Posted by sierraben
Friends A/C unit is new.

I to am also wondering why the ground wire is disconnected.

Previous owner did do some gonzo-bozo electrical work.


The oulet most assuredly needs checked out by a electrician and wired properly, if it is a new unit that is shocking people. Sounds like reversed polarity on the receptacle wiring, or a loose circuit neutral, a loose conductor or abraded insulation on a conductor in the AC that is touching the frame, or a, or a, on and on......... Hey, one more post and I got 1000 posts !!!
 

Last edited by Greg 79 f150; Jul 4, 2005 at 03:29 PM.
Reply
Old Jul 4, 2005 | 03:52 PM
  #12  
sierraben's Avatar
sierraben
Thread Starter
|
Post Fiend
Joined: Mar 2004
Posts: 24,418
Likes: 3
From: San Francisco, Ca.
Club FTE Silver Member

Originally Posted by Greg 79 f150
The oulet most assuredly needs checked out by a electrician and wired properly, if it is a new unit that is shocking people. Sounds like reversed polarity on the receptacle wiring, or a loose circuit neutral, a loose conductor or abraded insulation on a conductor in the AC that is touching the frame, or a, or a, on and on......... Hey, one more post and I got 1000 posts !!!
From what I understand, the new A/C unit shocks you if you ground yourself then touch the A/C unit. I heard it was more like a tingly sensation.

I'm just going to call him and advise him to call an electrician and fix the problem.
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
X-70STANG-F150
General NON-Automotive Conversation
6
Oct 24, 2008 04:49 PM
ag-ford-4x4
General NON-Automotive Conversation
13
Dec 22, 2006 09:56 PM
ag-ford-4x4
General NON-Automotive Conversation
8
Dec 13, 2006 02:20 PM
Shepard
General NON-Automotive Conversation
42
Feb 28, 2005 11:57 AM
TallPaul
General NON-Automotive Conversation
18
Aug 20, 2003 07:29 AM




All times are GMT -5. The time now is 09:24 AM.

story-0
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-1
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-2
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-3
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-4
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE
story-5
Top 10 Ford Trucks Coming to Mecum Indy 2026

Slideshow: Here are the top 10 Fords coming to Mecum Indy 2026.

By Brett Foote | 2026-05-04 13:49:49


VIEW MORE
story-6
5 Best / 5 Worst Ford Truck Wheels of All Time

Slideshow: The 5 best and 5 worst Ford truck wheels of all time

By Joe Kucinski | 2026-04-29 16:49:01


VIEW MORE
story-7
Ford Super Duty: 5 Things Owners LOVE, 5 Things They LOATHE!

Slideshow: Ranking the 5 things owners love about their Super Duty and 5 things they don't

By Joe Kucinski | 2026-04-29 16:36:49


VIEW MORE
story-8
Every 2026 Ford Truck Engine RANKED from WORST to FIRST!

Slideshow: Ranking all 12 Ford truck engines available in 2026.

By Michael S. Palmer | 2026-04-22 13:32:20


VIEW MORE
story-9
The Best F-150 Deal of Every Trim Level (XL through Raptor)

Slideshow: The best Ford F-150 deal for every trim level (XL through Raptor)

By Joe Kucinski | 2026-04-21 15:59:01


VIEW MORE