Household wiring question

Gentlemen,

I'm renovating the basement and had an electrician do the wiring. I had him leave three outlets with the wires just hanging in the wall box (Marretted) instead of installing the outlets (so I could build around them). Now has come time to install the outlets and I've hit a mystery.

He's used four-conductor cable. Red, black, white, and bare copper ground wire. A standard outlet only needs three wires. So I've got an extra wire.

Now, I checked and there's continuity between the copper ground wire and the white wire. Back at the breaker box, the copper wire is connected directly to the breaker box itself, and the white wire is connected to the grounding bar, so, no surprise they're connected to each other.

So, do I just have two grounds, both of which are meant to be connected to th eground screw on the outlets? Seems odd to me.

I'd ask my electrician, but he's away on holidays for a month. Is this some standard wiring method I've just never seen before?

Thanks.
 
Reply
Old Jun 15, 2005 | 10:32 AM
  #2  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
The white wire at the box ?
Is that hooked to the same bar with all the other white wires ?

If so,the white is the *Common Circuit*

at the box:

Bare goes to ground
White goes to Common
Black goes to breaker

at the receptacle
Bare wire goes to ground screw & green screw on the plug-in
White goes to silver screw on plug-in
Black goes to gold screw on plug-in


AFAIK, The red gets snipped and taped
 
Reply
Old Jun 15, 2005 | 10:41 AM
  #3  
fred_79f250's Avatar
fred_79f250
Thread Starter
|
Posting Guru
Joined: Jun 2005
Posts: 1,254
Likes: 0
From: Location, Location.
Yes, at the breaker box, white is to the common. Copper is to ground.

I'm familiar with wiring the three - black, white, copper.

So, what you're saying is that my electrician had run out of three-conductor cable and used four-conductor instead. SOB - could have just gone to get the right cbale.

Anyway - just cut and Marrette the red and forget about it. It's simple - I like it. We'll see what the electrical inspector says about these dangling red wires.....
 
Reply
Old Jun 15, 2005 | 10:48 AM
  #4  
53wa2fl's Avatar
53wa2fl
Elder User
Joined: Sep 2004
Posts: 525
Likes: 0
From: Floriduh
the insphincter wont lik the extra wire I'm sure....It raises to many eyebrows. But he may go for it. I would hook up the receptacles and try to pass it. As for your electrician, thats what they do. It would be TOO easy to just get the right wire.
 
Reply
Old Jun 15, 2005 | 10:49 AM
  #5  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
That's what I'm assuming.

Can you see where the red is running to confirm what is up with it ?

When covering a dangling wire first a Marrette & then Tape it up.

That red is usually for 2-way lighting.
But it can also be for wiring other circuits or replacing either the black or white if they should go bad.
 
Reply
Old Jun 15, 2005 | 10:55 AM
  #6  
Bigham's Avatar
Bigham
Senior User
Joined: May 2004
Posts: 166
Likes: 0
From: NJ
It is probably a standard outlet hook up. The Copper wire gets hooked up to the green screw on the outlet, The white gets hooked up to the silver screw on the outlet and the black goes to the brass screw on the outlet. The black wire at the panel gets hooked to a breaker and snapped in. I would not cut the red wire just put a wire nut on it and tape it. If you ever break the black wire you could use the red to supply power to the outlet.

Eddie
 
Reply
Old Jun 15, 2005 | 11:04 AM
  #7  
cjstang's Avatar
cjstang
Senior User
Joined: Jan 2005
Posts: 136
Likes: 0
Before you do any 'cutting', where do the black and red wires go in the box??
Don't know why he'd do this in your case, but it's possible that the red is hot also.
Do you have an AC voltmeter or test light to check if the black and/or red are hot?
[And a side note, I assume the breaker(s) are not Ground Fault Interrupts (GFI's) - if they are, the white (neutral) would connect to the breaker also. If you connect the white wire to the buss, any current draw greater than ~ .005 amps (5mA) better trip the GFI. This happened at my house, knew just what it was when it happened, but left it so I could explain to the electrician how to wire it - scary ain't it. . .]
 
Reply
Old Jun 15, 2005 | 11:10 AM
  #8  
buffalobob's Avatar
buffalobob
Senior User
Joined: Jul 2004
Posts: 376
Likes: 0
I would check voltage between red and white wires...what you described is commonly done to provide two circuits ...using one wire. If Im correct...there is 220 volts between the black and the red. Soooo take black and white for one 110 v circuit and red and white for circuit #2....which also has 110 volts.....easy to tell if this is the case by looking at the breaker.....is it a double pole breaker?....if so.....thats what electrician did
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-1

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-2

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-3

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-4

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-5

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-6

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-7

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-8

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-9

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
Old Jun 15, 2005 | 11:12 AM
  #9  
fred_79f250's Avatar
fred_79f250
Thread Starter
|
Posting Guru
Joined: Jun 2005
Posts: 1,254
Likes: 0
From: Location, Location.
OK, I think this is cleared up. But just to tie up loose ends and questions:

In the breaker box:
breakers are not GFI
copper is to ground
white is to common
black & red are dangling

At the outlet box:
currently all are dangling.

At the breaker box I'm going to connect the black to a breaker, and Marrette & tape the red.

At the outlet box, I'm going to connect the outlet as usual, and Marrette and tape the red.

If the inspector asks, I'll tell him it's foresight in case some day the black breaks.

Thanks everyone for your help.
 
Reply
Old Jun 15, 2005 | 11:18 AM
  #10  
buffalobob's Avatar
buffalobob
Senior User
Joined: Jul 2004
Posts: 376
Likes: 0
Talking

after reading what I wrote .....a short footnote:...its entirely possible that the electrician used 2- single pole breakers and everything else as in my posting above...the voltage test between white and red (110 volts) is key to this question of what "red" is.....good luck!
 
Reply
Old Jun 15, 2005 | 11:31 AM
  #11  
fred_79f250's Avatar
fred_79f250
Thread Starter
|
Posting Guru
Joined: Jun 2005
Posts: 1,254
Likes: 0
From: Location, Location.
Except there's no voltage between red and black or red/black and anything, because they're both just floppin' in the breeze inside the breaker box, not connected to anything at this point. They can become what I want.... although now that you metion it, the only remaining breakers left are two double-breakers. And there are two cables, each with four conductors. But this is just a little kitchen island. It woudln't seem reasonable to imagine the electrician had planned four outlets for this little thing.
 
Reply
Old Jun 15, 2005 | 11:41 AM
  #12  
cjstang's Avatar
cjstang
Senior User
Joined: Jan 2005
Posts: 136
Likes: 0
The elctrician I used did what buffalobob described - used a 4-conductor wire for 2 'hot' circuits. I personally don't like this as they share the neutral (not a big deal), but if they (the black and red) are on adjacent breakers, they are on two different circuits (phases) and I'd much prefer NOT to have a common neutral for two different phases - will work for sure, but I'd use two seperate 3-conductor wires. Even seperate circuits on the same phase should have its own neutral IMO. More work, but its much easier to follow, and if you ever do want a GFI breaker, forget about it!

Question: does two phases (or 2 circuits of the same phase) sharing a common neutral comply with electrical wiring codes??
 
Reply
Old Jun 15, 2005 | 11:56 AM
  #13  
Mil1ion's Avatar
Mil1ion
New User
Joined: Jan 2008
Posts: 0
Likes: 24
Unless the electrician has set something else in mind without telling the owner,
The question was answered on Post #5
 
Reply
Old Jun 15, 2005 | 01:23 PM
  #14  
loudfords's Avatar
loudfords
FTE Chapter Leader
25 Year Member
Photogenic
Community Builder
Community Influencer
Joined: Sep 2000
Posts: 3,862
Likes: 5
From: Beachville, Ontario
Club FTE Silver Member

I think cjstang has the answer here, you could wire them up as split receptacles on 2 breakers. My kitchen is wired with split receptacles but I never asked the previous owner if he used 2-3 conductor wires or if he used the 4 conductor wire. If you look at the electrical outlet, there should be 2 screws on either side, 2 for black wire, 2 for white wire, and a tab between the screws that can be broken out should you choose to go the split receptacle route.

BTW, 4 conductor wiring is handy for ceiling fans with light fixtures, then you can have the fan and light on separate switches, instead of having to pull the chain to turn the light off with the fan on. My master bedroom is this way, but not the kitchen. Stupid previous owner......
 
Reply
Old Jun 15, 2005 | 01:25 PM
  #15  
sierraben's Avatar
sierraben
Post Fiend
Joined: Mar 2004
Posts: 24,418
Likes: 3
From: San Francisco, Ca.
Club FTE Silver Member

And I thought wiring was easy.

Ever deal with 3 phase delta?

DON'T--$$$---LOL
 
Reply



All times are GMT -5. The time now is 01:29 PM.

story-0
Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-05-30 18:33:59


VIEW MORE
story-1
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-2
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-3
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-4
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-5
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-6
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-7
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-8
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-9
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE