First, why is it empty, for how long has it been empty, and was it open to the atmosphere in the meantime? Evacuating is done to remove old refrigerant, and moisture from the system. It can also serve as an indication as to whether you will be wasting your money dumping refrigerant into a system with a leak.
First, why is it empty, for how long has it been empty, and was it open to the atmosphere in the meantime? Evacuating is done to remove old refrigerant, and moisture from the system. It can also serve as an indication as to whether you will be wasting your money dumping refrigerant into a system with a leak.
Right now it is at 50-55psi. It is still cycling on and off. Posted in Ranger Forum. Should have brought that one over here.
50 is actually a little high, unless the ambient temperature is very high. 35-40 would be better. Three things come to mind: bad pressure switch, over charged, or airflow restricted. I'd lean toward the pressure switch if you have to jumper it to even get the compressor to run at all, but you should check high side pressure also.
To answer, yes the system should still shut off at the switch even with the pressure switch jumpered.
An overcharge, especially if there is also a restriction in the system can cycle the compressor off via the high pressure safety switch. High side generally should be under 225-250 or so. Mine runs about 200 on the high side and 36 on the low side at 92 degrees outside. The vent temp comes down to 38 F on max.