220volt compressor wiring

Okay I'll try to make this brief. I recently purchased a 220 volt 5hp 2-stage 60gal Eaton compressor. The company saidit needs to run on a 40amp breaker. So I had a 40 amp outlet and breaker installed However when the compressor arrived the mag stater where the wiring for the plug goes says not to exceed 10-14 ga wire. But a plug for a 40 amp receptacle needs at least 8ga. Eaton also ran 10 ga wire from the mag starter/pressure switch(they use a condor MDR3 which serves as both) to the motor. I am confused, it is my impression that 10 ga wire is only rated up to 30 amps, therefore, running this wire on a 40 amp breaker is a hazard as the wire would burn up before the breaker tripped if the motor pulled to much amperage??????
I.E. The motor is a Baldor single phase 23.5amps
Please help................Thanks
 
Reply
Old Aug 30, 2009 | 07:05 AM
  #2  
sdetweil's Avatar
sdetweil
Hotshot
25 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Nov 2000
Posts: 11,591
Likes: 14
From: Pflugerville, tx
Club FTE Silver Member

Originally Posted by bltemple
Okay I'll try to make this brief. I recently purchased a 220 volt 5hp 2-stage 60gal Eaton compressor. The company saidit needs to run on a 40amp breaker. So I had a 40 amp outlet and breaker installed However when the compressor arrived the mag stater where the wiring for the plug goes says not to exceed 10-14 ga wire. But a plug for a 40 amp receptacle needs at least 8ga. Eaton also ran 10 ga wire from the mag starter/pressure switch(they use a condor MDR3 which serves as both) to the motor. I am confused, it is my impression that 10 ga wire is only rated up to 30 amps, therefore, running this wire on a 40 amp breaker is a hazard as the wire would burn up before the breaker tripped if the motor pulled to much amperage??????
I.E. The motor is a Baldor single phase 23.5amps
Please help................Thanks
yeh yeh what do they know..

you could have done this on a 30 amp circuit.. you are ok..
5HP will never be over 30 amps.. better bigger wire than smaller.

Sam
 
Reply
Old Aug 30, 2009 | 07:09 AM
  #3  
tinman52's Avatar
tinman52
Welder User
15 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Feb 2009
Posts: 5,269
Likes: 50
From: northwest MT
Club FTE Silver Member

Can you explain "had a 40 amp outlet and breaker installed" ? What is the source of power? Why use an outlet and plug? Usually they are wired direct or to junction box. Maybe ask an electrician?. T/M
 
Reply
Old Aug 30, 2009 | 07:31 AM
  #4  
sdetweil's Avatar
sdetweil
Hotshot
25 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Nov 2000
Posts: 11,591
Likes: 14
From: Pflugerville, tx
Club FTE Silver Member

I installed a plug on mine.. that way I can disconnect it easily to move or clean or whatever.

I ran 10ga for my compressor, and 6 ga for my large Miller Tig welder.
(wish I had thought ahead on the 10ga, as I almost had a 7.5hp compressor which would have required 8ga).

sam
 
Reply
Old Aug 30, 2009 | 08:09 AM
  #5  
AXracer's Avatar
AXracer
Hotshot
20 Year Member
Liked
Joined: Oct 2004
Posts: 15,882
Likes: 88
From: Durham NC
I wired mine with a plug as well. Bought a pigtail with attached plug to match outlet (either a range or dryer pigtail ?) at my local DIY store. It had proper sized wire already attached.
Here's an aside suggestion: Buy new hockey pucks for under the feet. Drill and countersink (I used a spade bit to countersink, they drill as easily as wood) in center for appropriate sized bolt and bolt to feet. It will cut down on noise dramatically and the compressor will not "walk" from vibration.
 
Reply
Old Aug 30, 2009 | 10:13 AM
  #6  
flamebuster's Avatar
flamebuster
Posting Guru
Joined: Jan 2009
Posts: 1,321
Likes: 0
From: Mattawa Washington.
By excedding they mean don't go smaller. The longer the distance of the wire the larger it needs to be due to resistance. That is why theres is only 10 ga. it is a short distance to motor. yours has to be larger because it is further from the motor.. Hope this helps explain it.
 
Reply
Old Aug 30, 2009 | 10:29 AM
  #7  
Julies Cool F1's Avatar
Julies Cool F1
Post Fiend
Joined: May 2008
Posts: 7,641
Likes: 21
From: Poway, Ca.
If the length of the run of the "wire" (more like cable at 8 AWG) was more than 30 feet then 8 gauge was correct for a 40 amp 220 Volt circuit. That is the same set up as an electric oven/range in the house. If it goes over 60 feet it should be 6 AWG. As a matter of fact the plug installed is probably the kind used on electric stoves - bottom tang verticle, two top tangs diagonal pointing outward at the top.

Whether it needed to be 30 or 40 amps is determined by the manufacturers requirements, but if 30 was all that is required, then 40 will be fine. That doesn't mean it will draw the full 40 amps, it just means your wiring, breaker and plug will handle 40 amps safely (and a certain margin) if it pulls that much.

And flamebuster is correct the higher the AWG the smaller the wire. So in exceeding 10-14 AWG you will be getting too small. And in my honest opinion, 14 is too small as well. The directions are oxymoronic..but you are ok.

If you need to find a chord and plug, an electric range chord and plug will work nicely - Home Depot - $12.95 - just put a new one in my house.
 
Reply
Old Aug 30, 2009 | 05:06 PM
  #8  
flamebuster's Avatar
flamebuster
Posting Guru
Joined: Jan 2009
Posts: 1,321
Likes: 0
From: Mattawa Washington.
Originally Posted by Julies Cool F1
If the length of the run of the "wire" (more like cable at 8 AWG) was more than 30 feet then 8 gauge was correct for a 40 amp 220 Volt circuit. That is the same set up as an electric oven/range in the house. If it goes over 60 feet it should be 6 AWG. As a matter of fact the plug installed is probably the kind used on electric stoves - bottom tang verticle, two top tangs diagonal pointing outward at the top.

Whether it needed to be 30 or 40 amps is determined by the manufacturers requirements, but if 30 was all that is required, then 40 will be fine. That doesn't mean it will draw the full 40 amps, it just means your wiring, breaker and plug will handle 40 amps safely (and a certain margin) if it pulls that much.

And flamebuster is correct the higher the AWG the smaller the wire. So in exceeding 10-14 AWG you will be getting too small. And in my honest opinion, 14 is too small as well. The directions are oxymoronic..but you are ok.

If you need to find a chord and plug, an electric range chord and plug will work nicely - Home Depot - $12.95 - just put a new one in my house.
Sounds like a true electrician and better put than my description, well done.Julie...
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-1

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-2

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-3

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-4

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-5

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-6

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-7

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
story-8

Top 10 Ford Trucks Coming to Mecum Indy 2026

 Brett Foote
story-9

5 Best / 5 Worst Ford Truck Wheels of All Time

 Joe Kucinski
Old Aug 30, 2009 | 05:57 PM
  #9  
3golfjack's Avatar
3golfjack
Laughing Gas
15 Year Member
Joined: Nov 2006
Posts: 1,125
Likes: 4
From: Olive Branch,Ms
Club FTE Silver Member

You need to go by the manufacturers requirements for the circuit breaker. If it says 30 amps you need to go with a 30 amp breaker. The breaker safe guards against possibly doing damage to your compressor and electrical components. For instance if it is rated at 30 amp if you have bearing failure instead of amping up to 40 amps and triping out it will trip out at the 30 amp. With the additional 10 amps before it trips out you probably will be replacing the bearings and the motor.
 
Reply
Old Aug 30, 2009 | 11:04 PM
  #10  
Julies Cool F1's Avatar
Julies Cool F1
Post Fiend
Joined: May 2008
Posts: 7,641
Likes: 21
From: Poway, Ca.
Originally Posted by 3golfjack
You need to go by the manufacturers requirements for the circuit breaker. If it says 30 amps you need to go with a 30 amp breaker. The breaker safe guards against possibly doing damage to your compressor and electrical components. For instance if it is rated at 30 amp if you have bearing failure instead of amping up to 40 amps and triping out it will trip out at the 30 amp. With the additional 10 amps before it trips out you probably will be replacing the bearings and the motor.
Jack, that's not true at all. A rating is a requirement, and performance figure, not a destruction limit. When these components are built and tested, they are subjected to far more than the rated power, at a proof level of 125% and a burst level of 150-200%. That momentary 10 amp spike isn't going to destroy anything - especially on a 220 volt motor.

In this case the rating provides an indicator as to the MINIMUM circuitry required to support the motor. Going stronger will not hurt the compressor. It's gonna draw what it needs to operate.

The circuit breaker is used to prevent an overdraw of specified amps through a given gauge of wire and is installed solely as a safety device for the house wiring - not the appliance. The compressor motor will have a separate breaker on it that will prevent damage to it if it sees an amperage overload or overheat, and is that sensative to current or heat.

Under normal operation, the motor is going to draw well below 40 or even 30 amps - with a good 220 volts. But if that voltage (in the summer - air on) slips down to say 205, then the extra wire thickness and higher rated breaker will actually prevent damage to the motor or compressor mechanism from poor quality power, or shutting down frequently in the middle of running.

At 220 Volts, if the compressor motor has a failure that causes it to clamp up and draw 40 amps, the physical damage to the machine has already occured. If it is such that it causes a high draw, it will be instantaneous, and it will trip the breaker in a millisecond. In your scenario, the purpose of the distribution panel circuit breaker is to prevent damage or fire in the house wiring given too high a draw not protect the compressor.

And if you have that catastrophic a circumstance, you are going to be replacing parts anyway, and not because of electricity.
 
Reply
Old Aug 31, 2009 | 01:21 AM
  #11  
wmjoe1953's Avatar
wmjoe1953
Cargo Master
20 Year Member
Photogenic
Joined: Sep 2004
Posts: 2,906
Likes: 82
From: Oregon
Yeah. I wired my compressor into my house 240 myself (they're 240, not 220). There is a overload breaker on the compressor. I don't think there are any 240 Volt compressors that don't have an overload breaker. Mine has 12 ga from the switch box to the motor, it's factory. Mine has a pig tail cord that I installed from the switch box to my 240 Volt extension cord (it's the really heavy 6 ga type for my welder and stuff). I plug into the end of that, and that heavy cord is hard wired right to a 40 amp breaker in my house panel. And no Julie, it's not a smoker...haha. I did a lot of searching the web and didfferent electrical sites before I installed mine. I had an electrician that was gonna do it, but he never showed, so I said screw it. It's not hard at all to do. Mine is actually wired in with a regular extension cord (the 3 prong grounded type plugs for 120 stuff) but it's a super heavy 8ga industrial type, so it works just fine, since my compressor has the two hots and a ground, instead of two hots, ground, and common. I had to do mine this way, because the house we're renting didn't have any 240 outlets in the garage (guess I'll get dinged on my deposit for the hole I cut in the drywall for shoving the heavy cord through), and I needed to be able to move my welder around, and wanted enough mobility to have my equipment usable at all times. Heck, (close your eyes Julie, don't read this part) I can be welding, and have the compressor running, and the wife inside cooking in the oven all at the same time, on the same 40 amp breaker, so I don't think you'll ever use 40 amps running a compressor.
 
Reply
Old Aug 31, 2009 | 10:08 AM
  #12  
AXracer's Avatar
AXracer
Hotshot
20 Year Member
Liked
Joined: Oct 2004
Posts: 15,882
Likes: 88
From: Durham NC
The heaviest draw of an electric motor is at the moment of startup, after that it takes many less amps to keep running. That's why it sometimes calls for a "slow blow" type breaker, to allow for that short duration heavy current surge without tripping.
 
Reply
Old Aug 31, 2009 | 11:01 AM
  #13  
Julies Cool F1's Avatar
Julies Cool F1
Post Fiend
Joined: May 2008
Posts: 7,641
Likes: 21
From: Poway, Ca.
Originally Posted by wmjoe1953
Yeah. I wired my compressor into my house 240 myself (they're 240, not 220). (ok if you want to be semantic, but the power porvided is phase A and C in a 110-120 volt rated supply "off the pole," the "220 to 240" uses both phases - iow it uses both 110-120 volt supplies to provide 220-240 power) There is a overload breaker on the compressor. I don't think there are any 240 Volt compressors that don't have an overload breaker. Mine has 12 ga from the switch box to the motor, it's factory. Mine has a pig tail cord that I installed from the switch box to my 240 Volt extension cord (it's the really heavy 6 ga type for my welder and stuff). I plug into the end of that, and that heavy cord is hard wired right to a 40 amp breaker in my house panel. And no Julie, it's not a smoker...haha. And hopefully you aren't either still! I did a lot of searching the web and didfferent electrical sites before I installed mine. I had an electrician that was gonna do it, but he never showed, so I said screw it. It's not hard at all to do. Mine is actually wired in with a regular extension cord (the 3 prong grounded type plugs for 120 stuff) but it's a super heavy 8ga industrial type, so it works just fine, since my compressor has the two hots and a ground, instead of two hots, ground, and common. (as long as we are being symantical Joe, the three terms associated with the house wiring are "Common" which is the power supply (black and red wires); "Neutral" which provides the return circuitry to the CB box (white wires); and, "Ground" which provides a redundant avenue for the power to flow back to the panel (bare copper). In most older homes, and a lot of folks don't know this, the ground wires connect to the same lug bar as the neutrals - which goes back out to the pole. In newer homes and some in states outside California (like my house in Missouri) the ground wires are required to go to a seperate lug bar in the panel and run to a literal ground - through the cold water piping in the house; plus, redundantly, a burried metal bar for lightning or storm protection) I had to do mine this way, because the house we're renting didn't have any 240 outlets in the garage (guess I'll get dinged on my deposit for the hole I cut in the drywall for shoving the heavy cord through), and I needed to be able to move my welder around, and wanted enough mobility to have my equipment usable at all times. Heck, (close your eyes Julie, don't read this part) I can be welding, and have the compressor running, and the wife inside cooking in the oven all at the same time, on the same 40 amp breaker, so I don't think you'll ever use 40 amps running a compressor.
Sure Joe no problem with the welding and cooking on the 40 amp circuit. Remember, just because something is rated at a given amperage, doesn't mean it's going to use every bit of it. And unless you do, your breaker won't trip, and the circuit is safe.

Your machine requirements said to use a 40 amp breaker, then use a 40 amp breaker. Use it with 8 ga wire for up to 30 feet of run and 6 ga wire for over 30 ft of run. Use a 40 amp plug. From th eplug to the compressor you can use a 12 ga appliance cord rated for a 40 amp appliance - like an oven.

Remember folks amperage again is an inaccurate term. The electrical draw is actually measured in watts (and billed in Killowatt hours). Amperage being a function or wattage is what is used because it indicated volume not heat (work). And, remember also that electricity is drawn through the working appliance not forced to it. If the work the appliance is trying to do it will require more amps to supply the needed watts and the breaker will trip. The wiring will not experience the higher wattage in the circuit (heat) and will be kept safe from overheating.

It sounds lie a good set up Joe. The 12 Ga wire for the final short distance is perfectly acceptable (though 12 guage would not be for the long run - in the house - from the box - distance being a key factor). The appliance cord I suggested is only 12 ga. - but more than sufficient with a 5 foot run.
 
Reply
Old Aug 31, 2009 | 03:26 PM
  #14  
B/B ford's Avatar
B/B ford
Clean & Classy
20 Year Member
Joined: Dec 2004
Posts: 1,656
Likes: 20
From: Riverside CA..
Club FTE Silver Member

Good info Julie, only exception is that "common" and "Neutral" are different terms for the same wire, also known as the "identified conductor" or "grounded conductor" which is identified by the color white or slate grey.
 
Reply
Old Aug 31, 2009 | 03:33 PM
  #15  
Julies Cool F1's Avatar
Julies Cool F1
Post Fiend
Joined: May 2008
Posts: 7,641
Likes: 21
From: Poway, Ca.
I stand corrected! Thanks!
 
Reply



All times are GMT -5. The time now is 09:25 PM.

story-0
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-1
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-2
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-3
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-4
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-5
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-6
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-7
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE
story-8
Top 10 Ford Trucks Coming to Mecum Indy 2026

Slideshow: Here are the top 10 Fords coming to Mecum Indy 2026.

By Brett Foote | 2026-05-04 13:49:49


VIEW MORE
story-9
5 Best / 5 Worst Ford Truck Wheels of All Time

Slideshow: The 5 best and 5 worst Ford truck wheels of all time

By Joe Kucinski | 2026-04-29 16:49:01


VIEW MORE