running wire for welder and compressor

Hey everyone ...need alittle help here please. Im running more electrical in my garage before I sheetrock. I plan on buying a Miller 175 welder and I currently have a 60 gallon (230v) craftsman compressor. My question is which is the proper wire to run for each piece of equipment. I have been told 10/3 or 10/4 will be fine. Is this correct? Thanks for any and all response
 
Reply
Old Apr 4, 2006 | 09:21 AM
  #2  
LilDuke's Avatar
LilDuke
Elder User
Joined: May 2004
Posts: 790
Likes: 0
From: Danville, Pa
Well, the miller requires 19.5A@ 230V and your compressor requires (if it's 3.2 Hp) 15A@ 230V. For the miller you are required to run 12-2 on a 2 pole 20 amp breaker. For the craftsman your are only required 14-2 on a 2 pole 15 amp breaker. Howerever For the craftsman I would also run 12-2 on 20A , plus I don't recomend running anything less than 12-2. Now if the run from the Sub panel is farther than 100 feet, go up one gauge to counteract the 5% voltage drop to make sure you have enough power. I.e. 12-2 -> 10-2 ect.

Btw, when buying NM-B 12-2 refers to 2 wires + ground = 3 wire romex. If your running MC (Metal Clad I think) then get 12-3.
 
Reply
Old Apr 4, 2006 | 04:52 PM
  #3  
rclarke's Avatar
rclarke
Posting Guru
Joined: May 2003
Posts: 1,525
Likes: 3
19.5 amps should be on a 30 amp 10awg cct. It is generally recommended to never run more than 80% of a circuit capacity. The 15 amp compressor should be on a 20 amp circuit.
 
Reply
Old Apr 4, 2006 | 06:20 PM
  #4  
fefarms's Avatar
fefarms
Elder User
Joined: Sep 2004
Posts: 941
Likes: 4
There is a special section of the electrical code just for welders. (Article 630). The nameplate rating of the welder can be adjusted by the nameplate duty cycle when determining the ampacity of the branch circuit conductors. The Miller 175 probably has a duty cycle no more than 30 percent. The adjustment factor is 0.55 for this case, making the "effective" amps only 11.

You could run 14AWG to the welder and be code compliant. The 80 % rule does not apply to electric welders. Voltage drop is not much of a problem with a MIG welder, since the machine is constantly adjusting its output to hold a constant output voltage, regardless of the amount of current flowing (or input voltage)

That said, I would not bother with smaller than 10 AWG wire for a new welder circuit. The breaker, connectors, and effort to run the wire costs much more than more robust wiring. You never know what machine you will buy next.
 
Reply
Old Apr 4, 2006 | 09:41 PM
  #5  
Torque1st's Avatar
Torque1st
Posting Legend
Joined: Sep 2001
Posts: 30,255
Likes: 37
Originally Posted by fefarms
...That said, I would not bother with smaller than 10 AWG wire for a new welder circuit. The breaker, connectors, and effort to run the wire costs much more than more robust wiring. You never know what machine you will buy next.
I may be crazy but that is the reason I wire for the outlet ampacity. If it is a 50A receptacle I wire the circuit for 50A. I never know when my father may come thru with his RV and want to plug in to my 50A welder outlet or when I might upgrade!
 
Reply
Old Jun 8, 2006 | 08:31 AM
  #6  
sdetweil's Avatar
sdetweil
Hotshot
25 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Nov 2000
Posts: 11,591
Likes: 14
From: Pflugerville, tx
Club FTE Silver Member

so, I am wiring for a Miller SD 180.

the manual (http://www.millerwelds.com/om/o360j_mil.pdf) says

All values calculated at 40% duty cycle.
Input Amperes At Rated Output - 54
Max Recommended Standard Fuse or circuit breaker Rating In Amperes
Time-Delay - 60
Normal Operating - 80
Min Input Conductor Size In AWG - 8
Min Grounding Conductor Size In AWG - 8

that sounds a lot bigger than for the 200 above..

The manual also says that the cord comes without plug, but as I recall (its at my sons house), this has a 4 prong plug on the end, but the cable is only supposed to have three wires.. 2 hot and 1 ground.

so do I really need 8ga from the panel to the wall plug?

Sam
 
Reply
Old Jun 9, 2006 | 08:23 PM
  #7  
stryder's Avatar
stryder
Fleet Mechanic
25 Year Member
Joined: Jul 2000
Posts: 1,493
Likes: 346
From: SE Iowa
Originally Posted by sdetweil
so, I am wiring for a Miller SD 180.

the manual (http://www.millerwelds.com/om/o360j_mil.pdf) says

All values calculated at 40% duty cycle.
Input Amperes At Rated Output - 54
Max Recommended Standard Fuse or circuit breaker Rating In Amperes
Time-Delay - 60
Normal Operating - 80
Min Input Conductor Size In AWG - 8
Min Grounding Conductor Size In AWG - 8

that sounds a lot bigger than for the 200 above..

The manual also says that the cord comes without plug, but as I recall (its at my sons house), this has a 4 prong plug on the end, but the cable is only supposed to have three wires.. 2 hot and 1 ground.

so do I really need 8ga from the panel to the wall plug?

Sam

For your welder, it should be a 3 prong plug. My Millermatic 251 has a 3 prong. As far as wire size. The Miller site is correct. You only need to run 8/2 wire (if its a 3 prong) and 8/3 if its a 4 prong. I do however agree with Torque1st. If a manual calls for a 50amp breaker, I wire it for a 50amp breaker. In this case, 50amp calls for 6ga. wire. Saves a lot a hassle down the road if you upgrade to a bigger welder or maybe even a plasma cutter or TIG welder. Depending on your garage setup, I'd look at running metal conduit and using THHN wire. The price of copper is getting insane, and this may save you a few dollars. Figure cost of either conduit vs. Romex and see which one wins.


Stryder
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
Jim59
Garage & Workshop
22
Feb 22, 2008 12:14 PM
oldcoupe42
Garage & Workshop
23
Nov 23, 2005 08:58 AM
gbrett
Garage & Workshop
3
Oct 20, 2005 09:34 PM
bob-63-292
Garage & Workshop
38
Jul 11, 2004 06:00 PM
rj haug
Paint & Bodywork
4
Dec 22, 2002 12:06 AM




All times are GMT -5. The time now is 03:06 PM.

story-0
10 Ugly Ford Trucks That We Still Kinda Love

Slideshow: 10 ugly Ford trucks that we still kinda love.

By Joe Kucinski | 2026-06-03 09:51:16


VIEW MORE
story-1
10 Things Every Truck Owner NEEDS (2026 Edition)

Slideshow: the best gifts for dads & grads

By Michael S. Palmer | 2026-06-03 15:43:58


VIEW MORE
story-2
Rezvani's Latest Post-Apocalyptic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-06-03 11:38:36


VIEW MORE
story-3
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-4
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-5
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-6
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-7
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-8
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-9
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE