Electrical wiring question
1. How many 110 duplex outlets can you place on the same circuit 20 amp? I am thinking it is 4 since they are duplex. I am running 12/2 wire to all outlets.
2. How about 220, I have several tools that are mobile ie. Table saw and Radial arm saw and I am planning to rewire them to 220. I want to place several 220 outlets around the shop also appropiately marked or either 220 specific plugs, so I avoid someone pluging a 110 drill into the 220 and smoking it.
Any other I deas or tips for the wiring would be greatly appreciated.
Please don't do this. Just because it works, doesn't make it right. Over-current protection exists for a reason.Any contractor who creates such a system on the jobs I work on would get thrown off the site immediately.
Last edited by Ian F; Mar 3, 2006 at 02:48 PM.
2. How about 220, I have several tools that are mobile ie. Table saw and Radial arm saw and I am planning to rewire them to 220. I want to place several 220 outlets around the shop also appropiately marked or either 220 specific plugs, so I avoid someone pluging a 110 drill into the 220 and smoking it.
Any other I deas or tips for the wiring would be greatly appreciated.
See this: http://www.hubbellnet.com/max_htm/te...EMA/front.html
1. How many 110 duplex outlets can you place on the same circuit 20 amp? I am thinking it is 4 since they are duplex. I am running 12/2 wire to all outlets.
2. How about 220, I have several tools that are mobile ie. Table saw and Radial arm saw and I am planning to rewire them to 220. I want to place several 220 outlets around the shop also appropiately marked or either 220 specific plugs, so I avoid someone pluging a 110 drill into the 220 and smoking it.
Any other I deas or tips for the wiring would be greatly appreciated.
1. in order to place the maximum number of 110 outlets on one circuit, you have to know how many items are running at one time and the total amps they will draw. In order to max out a 20 amp circuit, the total amperage will have to be 20 amps. How many electrical devices can you plug in and actually operate at one time?
2. Rewiring a device to run from 110 on a 220 can't be done without using a stepdown transformer, or a bunch of resistors.
3. You would have to try pretty hard to plug a device wired for 110 into a 220 outlet.
4. Standard household outlets are 15 amp, though 20 amp outlets look similar, one of the spade slots looks like a sideways "T." A device that can be used in a 15 amp outlet, can also be used in a 20 amp outlet with out damaging it.
5. Code requires 12/2 wire for 15 or 20 amp outlets, lights require 14/2 wire
Commercial installations use an assumption of 180 VA per receptacle. If you then de-rate the circuit to 80% of capacity, a 15 amp circuit is limited to 8 receptacles and a 20 amp circuit to 10 or 11.
(The above assumes that these receptacles are not serving equipment that is fixed in place, for which a load can then be calculated.)
Except for kitchens, bathrooms, and laundries, the NEC does NOT require 20 amp circuits nor does it require 12 AWG wire for receptacles. You can use 14 AWG wire on 15 amp circuits in your shop (or living room) if you want to. Personally, I wouldn't want to for work done on my own property. Electrical contractors working to a fixed price bid will be pushed towards 14 AWG wherever they can use it by the current price of copper. It is possible there are local codes requiring 12 AWG wire, but the NEC does not.
You can run a 240 volt circuit around your shop and put as many receptacles as you like on it. Just make sure they are proper NEMA receptacles for 240 volts (there are several choices) and that it is not possible to plug a 120 volt appliance into them. The wire needs to be sized for the overcurrent protection you provide. It is a good idea to size the wiring for the kind of receptacle you provide -- 20 amp receptacles get 12 AWG, 30 amp receptacles get 10 AWG, etc.
For a situation with modest sized table saws and radial arm saws, I would suggest a 20 amp 240 volt circuit and NEMA 6-20 cords and plugs. These are inexpensive, fit in ordinary device boxes, and the overcurrent protection is appropriate for the demand of the saw and the size of its attachment cord.
If you have heavier use equipment, the next step up is NEMA 14-30 plugs/receptacles, a 30 amp circuit, and 10 AWG wire.
Trending Topics
The more outlets on a single circuit the more likely you will trip the circuit.
Always leave room for later expansion of the electrical system.
A couple hundred dollars spent in a larger system than is needed at the time can save a thousand or so when you buy a new tool later.
And also an overbuilt electrical system is cheaper than replacing the building because an overloaded circuit caught fire.
We are building a shop right now. Each outlet circuit has two duplex outlets per circuit.
Why? Look at a circular saw amp requirements, it will be in the 15 amp range.
Now look at a 1/2" drill which will be in the 6 amp range.
If you plug both of them in the same circuit and try to run both of them at the same time you will trip the 20 amp breaker since the load would be 21 amps. This could be done in one duplex outlet.