Wiring for welder

Well, i'm looking to buy a hobart 180 to use at home in my garage, right now i only have a 120v mig and it's not cutting it. I do not currently have 220v in the garage and was wondering what i would need to set it up and what i would need If i wanted to run it off an extension cord. I have a sub pannel that I am going to add, right now the garage is running off the house breaker.
 
Reply
Old Nov 11, 2004 | 09:08 PM
  #2  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
This machine takes a minimum of a number 12 wire but if the cord is very long a 10 is better and useful in the future for larger machines. It will run from a dryer recept and is rated to run from a 20A breaker but will run from up to 50A due to the fact it has its own internal thermal overload protection. For the ground wire, on a main entrance service panel it can run to the neutral bar or a equipment ground bar. On a sub it should run from the equipment bar only. That machine takes a 6-50-R recept.
 
Reply
Old Nov 11, 2004 | 09:10 PM
  #3  
FordPerf300's Avatar
FordPerf300
Thread Starter
|
Posting Guru
Joined: Apr 2002
Posts: 1,187
Likes: 0
From: CT
I was doing some research, i'm going to go with a 50A breaker in the pannel and use 8/3 for the extension cord, incase i ever want to go bigger.
 
Reply
Old Nov 11, 2004 | 09:19 PM
  #4  
ford390gashog's Avatar
ford390gashog
Fleet Owner
20 Year Member
Liked
Loved
Community Favorite
Joined: Jan 2004
Posts: 26,007
Likes: 575
From: Brentwood,CA
Club FTE Gold Member
i had my garage rewired and they put in some hefty wires my house was rated for 300 amps and after the new cable was run it has a capacity of 600 300 for the house and 300 for the shop with 5 special 3 phase 240 outlets and 35 120's and 15 240's works good but wasn't cheap
 
Reply
Old Nov 12, 2004 | 10:58 AM
  #5  
zuikoman's Avatar
zuikoman
Senior User
Joined: Oct 2004
Posts: 125
Likes: 0
I got pretty much the same machine (Hobart Handler 175) and I run it off a 12 gauge extension cord I made. I took a regular 12ga 110v extension cord and cut off the ends, then put new 220v dryer plug and receptacle ends on it. Cost me about $15 including the cord. It works pretty well.

If you wanted to use it in the mean time (until you get an outlet in the garage) it will plug into some dryer outlets. That should be a 30amp circuit so you should have plenty of power there.

Good luck with that machine, I like mine quite a bit.
 
Reply
Old Nov 12, 2004 | 11:07 AM
  #6  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
Did you use a dryer recept on the end of the cord? The recept itself is different than a welding recept in the sense that the ground terminal isnt bonded to the recept yoke or to the backing plate of a surface mount type. When using these as cords you should run a jumper wire from the ground pin to the box if it is steel or to the backing plate of a surface mount. Personally I would rather use a recept that matches the welder than modify the cord and they are already bonded correctly.
 
Reply
Old Nov 12, 2004 | 11:12 AM
  #7  
zuikoman's Avatar
zuikoman
Senior User
Joined: Oct 2004
Posts: 125
Likes: 0
This particular welder comes with a dryer style (50 amp) plug even though it only requires 20 amps. The surface mount boxes are automatically grounded when you connect the ground wire to the ground pin, at least on any I have ever seen. There is a physical connection built into the box.
 
Reply
Old Nov 12, 2004 | 11:19 AM
  #8  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
That is a welding recept, it has a U shaped or round ground pin, a dryer has a flat or usually a L shaped. A 3 wire dryer is not internally bonded as it is used for multi voltage connections by bonding the neutral to ground within the machine. They changed this in the 96 code I think and new ones are now 4 wire with seperate grounding. Yes, the HH comes with a 50A plug and they do allow them to be plugged into 50A welding circuits but if I was making a circuit for it I would tend to tailor the breaker to closer match the machine and you just dont need that heavy of wire anyway. A 10/30 circuit is fine for them and I see the new 180's have upped the recommended breakers a bit. The instruction manual is slightly confusing for these machines as far as max breakers go. The minimum wire size is 14 and the max breaker is 20 for a 175, but that doesnt actually mean it cant be plugged into a 50A circuit. What it means is if you are using the 14 wire the max breaker has to be followed. It has a number 12 cord on the machine and that is allowed to be plugged into 50A circuits. Wires down to number 12 are the minimum that can be used on a 50A circuit. Confused yet??? ha You can put number 12 wire (single circuit in pipe) to a welder recept with a 50A recept and a 50A breaker on it for some machines, like a AC225 buzz box, but its not really a good idea to always follow the minimum allowable. There were millions of recepts installed with 10/50 setups back in the day especially from old fuse panels for running those machines. Its a good thing to check a 50A circuit when using it for something other than a welder or compressor to verify what wire is in them, especially if you were to hook up something like a pottery kiln that runs continious to one. Most equipment like a kiln doent even come with a plug and thats good, means the installer can visually verify the wire size.
 

Last edited by Sberry27; Nov 12, 2004 at 11:35 AM.
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-1

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-2

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-3

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-4

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-5

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-6

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-7

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-8

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-9

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
Old Nov 12, 2004 | 11:22 AM
  #9  
zuikoman's Avatar
zuikoman
Senior User
Joined: Oct 2004
Posts: 125
Likes: 0
Ahh ok, you are right about the dryer thing. I might have been thinking of the 3 wire electric range receptacles.
 
Reply
Old Nov 12, 2004 | 11:59 AM
  #10  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
Range recepts are the same way, they often used 120V circuits in them for clocks. Remember, the neutral wire is serving as the ground in these cases and is a current carrying conductor, they dont want currents on any exposed metal parts so it is unbonded in these type of recepts. I think any new ones that use dual voltage are 4 wire now. They elemnated the internal bonding except when using existing circuits. Any new ones need to be 4 wire when using multi voltage appliances. I can add some more confusion. The recept must always be rated equel to the breaker size, but the wire doesnt always have to match the breaker,,, depending on what is going to be plugged in. There are a couple exceptions, one being for small 120V welders. They do allow 30A on 20A recepts but they only allow a 12 wire, not a 10,,, (been some time since I read the details though) they limit the conductor size in that application. Its to protect the recept itself (the wire itself becomes a limiting factor)and to avoid tripping problems and this is only on a dedicated circuit with a single recept. Just for the heck of it take an ohm meter and check the different types of recepts. 3 wire dryer and ranges are unbonded while welders are bonded.
 
Reply
Old Nov 12, 2004 | 12:16 PM
  #11  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
I know this whole thing can be clear as mud and thats why so much hearsay surrounds the issue and why often it is implied you need a number 6 wire for a 50A circuit. Using it does eliminate a lot of confusion and take the chance of error from improper calculations out of it. But what it is based on is similar to a light fixture and to some extent using extension cords. The light fixture has number 16 wires in it and is allowed to be hooked to a 20A circuit. The breakers only function is to provide overload protection in the event that too many lights would be hooked up and to provide for short circuit protection, a 16 wire will trip the 20 in the event of a short but the overload protection for the fixture wires are protected by the fact that only so big of a lamp can be screwed into it, for example a 100 watt bulb will not overload a 16 wire. Welding machines are somewhat the same way, they are rated for their duty cycle. (it would make sense to me to require some thermal on small stick machines but they dont), they assume you are going to follow the 20% rating I guess, but these small feeders do have internal thermal in them and it will trip before it overloads the incoming wiring so the wire can be downsized or they can be plugged in to circuits with larger breakers. This is partially the reason we say number 8 is adequate for buzz boxes and a 6 is not needed, you would overwork the machine to meltdown before you would overheat the incoming wire. When you did it would short and trip the breaker. An AC225 like a lot of guys have here works well with a number 10 for cords and the ratings allowing for it are for wide open operation, at 225, most of the time they are run at 120A or so and the cord barely gets warm even if running them hard. It cools while you are changing rods, chipping, fabricating, etc.
 
Reply
Old Nov 12, 2004 | 12:29 PM
  #12  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
The use of extension cords is somewhat similar. A number 16 cord has a rating of 1200 watts continious, like with an electric heater, but there is not a problem with using it on a skil saw where the load exceeds that because the load is short term. As long as the voltage drop doesnt effect the tool its great. If you plugged 2 heaters in to this cord on a 20A circuit there could be a problem, it would overload it before it tripped the breaker.
 
Reply
Old Nov 13, 2004 | 05:59 PM
  #13  
Guy's Avatar
Guy
Senior User
25 Year Member
Joined: Mar 2000
Posts: 167
Likes: 1
From provincial codes up here, they say 14 gauge wire rated for 15 amps, 12 gauge rated for 20 ams, 10 gauge rated for 30 amps. Use the wire rated for the size of breaker you are using. The codes may be a little different in your area but I would bet not much. If you use a 50 amp breaker for 12 gauge wire rated for 20 amps chances are with that welder you may not have a problem but then again, if the wire overheats due to being overloaded and a fire starts, you better have good insurance.
Just my two cents.
I just wired my garage for the hobart handler 180 using 12/2 BX and double 20 amp breaker. So far I haven't gone over the first voltage tap for what I am welding. Just scratching the surface.
Guy
 

Last edited by Guy; Nov 13, 2004 at 06:03 PM.
Reply
Old Nov 14, 2004 | 12:20 PM
  #14  
Sberry27's Avatar
Sberry27
Tuned
Joined: Sep 2003
Posts: 483
Likes: 1
You are correct about the ampacity ratings for those wires on general purpose circuits. There are exceptions for specific equipment. Welding machines are one type as are certain motor circuits. The intent of my post wasnt to tell anyone to undersize wsires as much as to help a little with the understanding of how the current reacts in these circuits. This woud be very useful when sizing cords for these machines. We dont always need to go with a super heavy cord for some of them, its expensive, bulky and just not needed.
 

Last edited by Sberry27; Nov 14, 2004 at 12:24 PM.
Reply
Old Nov 17, 2004 | 11:37 PM
  #15  
"Beemer Nut"'s Avatar
"Beemer Nut"
Post Fiend
Joined: Dec 2003
Posts: 6,658
Likes: 4
From: "Islander"
Welding conductors and overcurrent protection

Per N E C, National Electrical Code, conductors for portable welders that operate at different values or duty cycles (manual welders) is 50% of rated welder primary amperage (630-31. A (2). A welder shall have overcurrent protection rated or set at not more than 200% of rated primary current of welder (630-12 A). NEC. Had to chime in. Carl, I.B.E.W. 595. .......o&o>.........
 
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
mustang_gt_350
General NON-Automotive Conversation
44
Mar 11, 2013 03:19 PM
JohnAW
General Automotive Discussion
4
Mar 30, 2008 08:32 AM
69crewcab
Garage & Workshop
10
Feb 26, 2006 10:16 PM
kc2006
Garage & Workshop
10
Jan 24, 2005 02:20 PM
Opiewan
Garage & Workshop
42
Jan 22, 2004 07:18 AM




All times are GMT -5. The time now is 04:25 AM.

story-0
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-1
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-2
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-3
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-4
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-5
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-6
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-7
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-8
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-9
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE