AC compressor cycling

Thread Tools
 
Search this Thread
 
Old Mar 24, 2018 | 10:55 AM
  #1  
Scott Morgan's Avatar
Scott Morgan
Thread Starter
|
New User
Joined: Mar 2018
Posts: 20
Likes: 0
From: League City Texas
AC compressor cycling

Hello Exmen!

I replaced my compressor and drier and filled the system with 14 oz of PAG Oil. I filled the system with refrigerant and the low side gage sits at about 60psi with high side gage at 60psi. The compressor keeps cycling every 3-4 seconds and wont stay on. I think I still have a small leak. Why is the compressor cycling so rapidly and wont stay on? What would be my next steps?
 
Attached Images  
Reply
Old Mar 24, 2018 | 07:09 PM
  #2  
01__Excursion's Avatar
01__Excursion
Cargo Master
Joined: Nov 2017
Posts: 3,096
Likes: 533
From: Rock Hill, SC
Do you have a front and rear system?
Did your new compressor come dry, with no oil?
Did you drain and measure the oil from your old compressor to determine that you needed 14oz?
Did you evacuate the system with a vacuum pump to 32 hg, or 800 or less microns?
How many pounds of Freon did you charge the system with?

Sorry for all the pointed questions, but all of them are pretty important, and the answers would paint a better picture on how you arrived where you are at...
 
Reply
Old Mar 25, 2018 | 07:42 AM
  #3  
Scott Morgan's Avatar
Scott Morgan
Thread Starter
|
New User
Joined: Mar 2018
Posts: 20
Likes: 0
From: League City Texas
Originally Posted by 01__Excursion
Do you have a front and rear system?
Did your new compressor come dry, with no oil?
Did you drain and measure the oil from your old compressor to determine that you needed 14oz?
Did you evacuate the system with a vacuum pump to 32 hg, or 800 or less microns?
How many pounds of Freon did you charge the system with?

Sorry for all the pointed questions, but all of them are pretty important, and the answers would paint a better picture on how you arrived where you are at...
I drained the new compressor and looked up the Ford spec for 14 oz of Pag oil with rear system.

I evacuated the system for 1 hr to 29”

I added 14oz of Pag 46 to new compressor and new drier.

i was able to put approx 24 oz of Freon in the system but it would not take more and the compressor started the rapid cycling. Spec for the system is 64oz.

Thank you for your reply!
 
Reply
Old Mar 25, 2018 | 08:23 AM
  #4  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,760
Likes: 1,079
From: St Louis
i was able to put approx 24 oz of Freon in the system but it would not take more and the compressor started the rapid cycling.
That would be completely normal up to that point as you're were charging into a vacuum, but it would be my opinion that you were not sufficiently patient.

Once the clutch starts short-cycling, it's pulling in a bit of refrigerant with each cycle. With sufficient patience, you would have noticed that the ON-portion of each cycle starts to get longer as the amount of refrigerant in the system increases.

Two common shortcuts include 1) warming the refrigerant (hot water bath or set it in the sunshine for a while) and 2) jumpering the low-pressure cycling switch to force the clutch into 100% duty cycle.
 
Reply
Old Mar 25, 2018 | 08:35 AM
  #5  
Scott Morgan's Avatar
Scott Morgan
Thread Starter
|
New User
Joined: Mar 2018
Posts: 20
Likes: 0
From: League City Texas
Originally Posted by projectSHO89
That would be completely normal up to that point as you're were charging into a vacuum, but it would be my opinion that you were not sufficiently patient.

Once the clutch starts short-cycling, it's pulling in a bit of refrigerant with each cycle. With sufficient patience, you would have noticed that the ON-portion of each cycle starts to get longer as the amount of refrigerant in the system increases.

Two common shortcuts include 1) warming the refrigerant (hot water bath or set it in the sunshine for a while) and 2) jumpering the low-pressure cycling switch to force the clutch into 100% duty cycle.

Good tips! I did let the compressor cycle for about 3-5 mins and stopped so I wouldn’t damage anything. The cycling did not increase and was on a consistent 5 second on......8 second off type pattern with no increase in on time. I tried this approach twice. I do believe I have a leak somewhere. Buying a new Evap and maybe Cindy tomorrow. I think I put too much Pag in as I only replace the dryer and compressor and I added 14oz as the truck has been sitting several months. If I had too much Pag would that limit the Freon qty I could add? How can I test the evap to see if it’s good. I pulled it yesterday. I appreciate your help sir!
 
Reply
Old Mar 25, 2018 | 03:43 PM
  #6  
01__Excursion's Avatar
01__Excursion
Cargo Master
Joined: Nov 2017
Posts: 3,096
Likes: 533
From: Rock Hill, SC
Originally Posted by projectSHO89
That would be completely normal up to that point as you're were charging into a vacuum, but it would be my opinion that you were not sufficiently patient.

Once the clutch starts short-cycling, it's pulling in a bit of refrigerant with each cycle. With sufficient patience, you would have noticed that the ON-portion of each cycle starts to get longer as the amount of refrigerant in the system increases.

Two common shortcuts include 1) warming the refrigerant (hot water bath or set it in the sunshine for a while) and 2) jumpering the low-pressure cycling switch to force the clutch into 100% duty cycle.
+1, that's exactly where I was headed next to advise.
 
Reply
Old Mar 25, 2018 | 03:51 PM
  #7  
01__Excursion's Avatar
01__Excursion
Cargo Master
Joined: Nov 2017
Posts: 3,096
Likes: 533
From: Rock Hill, SC
Originally Posted by Scott Morgan


I drained the new compressor and looked up the Ford spec for 14 oz of Pag oil with rear system.

I evacuated the system for 1 hr to 29”

I added 14oz of Pag 46 to new compressor and new drier.

i was able to put approx 24 oz of Freon in the system but it would not take more and the compressor started the rapid cycling. Spec for the system is 64oz.

Thank you for your reply!
How many ounces did you get from the compressor once drained?
It's a bit of a pain, but unless you did a full system flush/clean with a flushing product, and not Freon, and started with a dry compressor, then you would *** the factory spec 14oz. Otherwise without knowing how much drained from the compressor, and accumulator, you're not going to know how much over you are. A little bit over and you won't notice much, alot and you'll have performance issues. Since you're sealed, and at above atmospheric pressure, continue as above and go from there.
 
Reply
Old Mar 26, 2018 | 07:41 AM
  #8  
Oldguyfl's Avatar
Oldguyfl
Posting Guru
Joined: Sep 2015
Posts: 1,320
Likes: 9
From: Central Florida
Originally Posted by Scott Morgan
Hello Exmen!

I replaced my compressor and drier and filled the system with 14 oz of PAG Oil. I filled the system with refrigerant and the low side gage sits at about 60psi with high side gage at 60psi. The compressor keeps cycling every 3-4 seconds and wont stay on. I think I still have a small leak. Why is the compressor cycling so rapidly and wont stay on? What would be my next steps?
If your high side is only going to 60 PSI, your high pressure switch is not going to allow the compressor to cycle. By the numbers being equal, 60 and 60 it would appear that perhaps that:

1. you do not have enough freon in the system. It takes about 70-72 ounces to fill it with rear air. 6.5 12 oz cans. The pressure switch will not let it run longer.
2. Your new compressor is faulty.
3. One of your pressure switches are bad or the connection is faulty on one of them

On the ex, they have two pressure switches. Both are on the passenger side of the engine. One in the compressor line and one on the accumulator.

As it is short cycling like you describe, I would look for a full charge first, then at the pressure switches. You can jump each one with a paperclip to see which might be bad. Once you get the compressor to cycle then you can see if the pressures come up.
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-1

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-2

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-3

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-4

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-5

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-6

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
story-7

10 Most Surprising 2026 Ford Truck Features!

 Joe Kucinski
story-8

Top 10 Ford Trucks Coming to Mecum Indy 2026

 Brett Foote
story-9

5 Best / 5 Worst Ford Truck Wheels of All Time

 Joe Kucinski
Old Mar 26, 2018 | 08:12 AM
  #9  
mike71800b's Avatar
mike71800b
Senior User
Joined: Nov 2016
Posts: 144
Likes: 1
Just to be certain there isn't a mistake in procedure, the high side valve on the manifold was closed while charging yes?
This would cause equal pressure on both high and low side. Ive seen it happen before when the high side valve wasn't closed after pulling vacuum.
 
Reply
Old Mar 26, 2018 | 09:34 AM
  #10  
Toreador_Diesel's Avatar
Toreador_Diesel
FTE Leadership Emeritus
20 Year Member
Liked
Loved
Top Answer: 1
Joined: Sep 2003
Posts: 12,245
Likes: 758
From: Houston, Texas
Club FTE Gold Member
I agree with the others, but did you also replace the orifice tube?
 
Reply
Old Mar 26, 2018 | 10:50 AM
  #11  
Oldguyfl's Avatar
Oldguyfl
Posting Guru
Joined: Sep 2015
Posts: 1,320
Likes: 9
From: Central Florida
Originally Posted by Toreador_Diesel
I agree with the others, but did you also replace the orifice tube?
That will cause problems for sure. Every Ford I have owned has needed this replaced. It's on the low side though before the evap, he is not getting high pressure.
 
Reply
Old Mar 26, 2018 | 11:31 AM
  #12  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,760
Likes: 1,079
From: St Louis
If both the low and the high side readings are the same and are also at the static pressure for the ambient temperature (see a P-T chart!), it simply means that the compressor ain't running, nothing else. If the manifold's valves were left open, you'd usually see the compressor operating but the pressures on the two gauges would usually be different but the difference would be markedly attenuated (it depends on how far they're open plus a other variables like temperature). Also, the high-pressure bleeding bac into the low side would tend to keep the low pressure switch closed and the compressor clutch wouldn't be short-cycling.

If your high side is only going to 60 PSI, your high pressure switch is not going to allow the compressor to cycle.
Just to clarify, the high pressure switch is a normally closed switch that is designed to open up if the pressure hits the upper limit, usually in the 400-500 psi range. The high pressure switch will not disable compressor operation under low pressure conditions (unless defective), it's the job of the low pressure cycling switch to take care of that low end.

As it is short cycling like you describe, I would look for a full charge first
He doesn't have the necessary equipment to do a full refrigerant charge except by allowing the compressor to do the last 3/4 of the work. It takes highly specialized equipment (and expertise) to do a full charge on a system that is not yet functional. The factory, for example, does have that capability to charge the system without it being in operation.

It's on the low side though before the evap, he is not getting high pressure.
It's actually in the liquid line between the condenser and the input to the evaporator, usually right at the input to the evaporator. He's not seeing the gauges show a pressure differential because (1) the clutch isn't cycling ON long enough and 2) there's not much charge in the system yet.
 
Reply
Old Mar 26, 2018 | 12:40 PM
  #13  
Scott Morgan's Avatar
Scott Morgan
Thread Starter
|
New User
Joined: Mar 2018
Posts: 20
Likes: 0
From: League City Texas
Originally Posted by 01__Excursion
How many ounces did you get from the compressor once drained?
It's a bit of a pain, but unless you did a full system flush/clean with a flushing product, and not Freon, and started with a dry compressor, then you would *** the factory spec 14oz. Otherwise without knowing how much drained from the compressor, and accumulator, you're not going to know how much over you are. A little bit over and you won't notice much, alot and you'll have performance issues. Since you're sealed, and at above atmospheric pressure, continue as above and go from there.
There was less than an ounce in the compressor. I poured 8 ounces in the compressor and 6 ounces into the drier.
 
Reply
Old Mar 26, 2018 | 12:41 PM
  #14  
Scott Morgan's Avatar
Scott Morgan
Thread Starter
|
New User
Joined: Mar 2018
Posts: 20
Likes: 0
From: League City Texas
Yes i did replace the orifice tube. It had a little debris about the size of half a pencil eraser.
 
Reply
Old Mar 26, 2018 | 12:55 PM
  #15  
Scott Morgan's Avatar
Scott Morgan
Thread Starter
|
New User
Joined: Mar 2018
Posts: 20
Likes: 0
From: League City Texas
Originally Posted by mike71800b
Just to be certain there isn't a mistake in procedure, the high side valve on the manifold was closed while charging yes?
This would cause equal pressure on both high and low side. Ive seen it happen before when the high side valve wasn't closed after pulling vacuum.
i had the high side valve closed until the compressor kept cycling then I opened it to see what affect it would have. The high side pressure dropped.

I have taken out the evap and ordered a new one today. I will also flush what i can today and reinstall the new evap tomorrow when it arrives and follow the charging tips I have received on here.
 
Reply



All times are GMT -5. The time now is 12:23 AM.

story-0
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-1
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-2
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-3
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-4
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-5
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-6
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE
story-7
10 Most Surprising 2026 Ford Truck Features!

Slideshow: 10 most surprising Ford truck options/features in 2026.

By Joe Kucinski | 2026-05-05 11:17:22


VIEW MORE
story-8
Top 10 Ford Trucks Coming to Mecum Indy 2026

Slideshow: Here are the top 10 Fords coming to Mecum Indy 2026.

By Brett Foote | 2026-05-04 13:49:49


VIEW MORE
story-9
5 Best / 5 Worst Ford Truck Wheels of All Time

Slideshow: The 5 best and 5 worst Ford truck wheels of all time

By Joe Kucinski | 2026-04-29 16:49:01


VIEW MORE