AC low side high pressure

Finally got to the 89 bronco's ac. Whole system was replaced 3 years ago and converted to 134a about 3 summers ago. Wasn't working this year so I put gauges on and got low pressures, as soon as I put a can of 134a on, low side pressures shot up well over 100, compressor would pump for a second or two, the low side would hike up, then compressor would shut off and low side would come down to about 70-100. High side when pump engaged would be 150-200 then drop below 100 when disengaged. I checked the orifice tube, there was a bit of sediment, not black, more greyish. Flushed air and solvent through the low line from condenser to orifice tube, then backflushed the evaporator and blew it out well. No blockages or dirt. Replaced the accumulator and orifice tube, pulled a vacuum for several hours, then tried to refill, same thing, it wouldn't even take a 12oz can before pressures on low side would shoot up. Think it is the compressor or the suction lines blocked?
 
Reply
Old Jun 14, 2017 | 06:24 PM
  #2  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
Do you have the high side valve on the manifold gauge properly closed? Sounds like it's cross-circuiting in the manifold.
 
Reply
Old Jun 15, 2017 | 09:57 PM
  #3  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Originally Posted by projectSHO89
Do you have the high side valve on the manifold gauge properly closed? Sounds like it's cross-circuiting in the manifold.
No. I took the compressor off and you can spin it by hand with almost no resistance so it's obviously shot. Got another at a local store. Hooked everything back up, pulled a vacuum. Put a can of 134a on and it shot the low pressure up to about 75psi but high pressure is still reading 0. Jumped the pressure switch and doesn't do much so there must be restriction in the evaporator? Weird because I blew that out with air and it seemed fine. Or could it be the condenser?
 
Reply
Old Jun 16, 2017 | 04:25 AM
  #4  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
The reaction of the low side gauge is normal, you're reading the pressure from the can.

If your high side gauge is reading zero, either the gauge is defective, that hose's valve is turned off, or the connector/coupler/valve is defective. Both sides should read the same when the supply is first connected and before the compressor activates.

When you charged into a vacuum, that first can or so of refrigerant should pretty much jump into the system without even turning it on. If you pre-warm the can, it goes faster. I used to put the cans in a bucket of hot water or leave them in the sunlight for a while to speed it up.
 
Reply
Old Jun 16, 2017 | 04:49 AM
  #5  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Originally Posted by projectSHO89
The reaction of the low side gauge is normal, you're reading the pressure from the can.

If your high side gauge is reading zero, either the gauge is defective, that hose's valve is turned off, or the connector/coupler/valve is defective. Both sides should read the same when the supply is first connected and before the compressor activates.

When you charged into a vacuum, that first can or so of refrigerant should pretty much jump into the system without even turning it on. If you pre-warm the can, it goes faster. I used to put the cans in a bucket of hot water or leave them in the sunlight for a while to speed it up.
Thanks I appreciate your help. The problem is it is only accepting the first burst from the can. It won't take anymore. I also changed the hose from the evaporator to the compressor and condenser. I didn't check that for any kind of restrictions since it was brand new. I just can't think of what is restricting the Freon from going through the system
 
Reply
Old Jun 16, 2017 | 06:29 AM
  #6  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
You still haven't explained why both gauges do not read the same static pressure before the compressor is activated. That's either a problem with your manifold set, how it is being used, or a connection isn't open.
 
Reply
Old Jun 16, 2017 | 06:54 AM
  #7  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Originally Posted by projectSHO89
You still haven't explained why both gauges do not read the same static pressure before the compressor is activated. That's either a problem with your manifold set, how it is being used, or a connection isn't open.
I understand that. That's what's confusing me as well. But doesn't the fact that very little can go into the system point to some sort of restriction? I have a can with maybe 2 oz in it hooked up and it wont drain it. Both gauge lines are hooked up and opened at the Schrader valves, manifold is turned off at high side, I open low only to put Freon in. When I manually engaged the compressor (jumped the switch), the high side pressure would raise just a little, but go back to 0 when off.
 
Reply
Old Jun 16, 2017 | 07:38 AM
  #8  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
Do this: Engine OFF.

Open BOTH valves on the manifold and allow the can's contents to be directly exposed to both ports. Allow equilibrium to be reached. Both gauges should read the same, roughly static pressure based on your local ambient temp. If they don't, you have a problem with the manifold gauge set.

But doesn't the fact that very little can go into the system point to some sort of restriction?
Could be a number of things. Like I said previously, a fully vacuumed system in which vacuum integrity was maintained should allow a full can to go into the system without ever starting the engine. Di you verify that the system HOLDS vacuum after it was vacuumed?

BTW, did you flush or blow air through the condenser to verify it's not restricted?
 
Reply
FTE Stories

Ford Trucks for Ford Truck Enthusiasts

story-0

Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

 Verdad Gallardo
story-1

Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

 Joe Kucinski
story-2

2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

 Brett Foote
story-3

Top 10 Ford Truck Tragedies

 Joe Kucinski
story-4

AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

 Brett Foote
story-5

Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

 Michael S. Palmer
story-6

Ford's 2001 Explorer Sportsman Concept Looks For a New Home

 Verdad Gallardo
story-7

10 Best Ford Truck Engines We Miss the Most!

 Joe Kucinski
story-8

2026 Shelby F-150 Off-Road: Better Than a Raptor R?

 Brett Foote
story-9

2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

 Michael S. Palmer
Old Jun 16, 2017 | 07:43 AM
  #9  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Yes it held vacuum. I had the engine running with AC on max when I was trying to add Freon. Does that matter? I did blow air through the condenser and air did come out. I did not flush it.
 
Reply
Old Jun 16, 2017 | 08:29 AM
  #10  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
Do the engine off check, you have to verify your manifold and gauges are working correctly.
 
Reply
Old Jun 16, 2017 | 04:47 PM
  #11  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Originally Posted by projectSHO89
Do the engine off check, you have to verify your manifold and gauges are working correctly.
Did the engine off test. Both sides came up to a little over 70 psi. Closed off both lines, started engine and turned ac on. Compressor engaged for a brief second then shut off continually. The pressure on the high side would rise to about 110 but the low side did not move. I turned the can on and opened up the low side. It increased its pressure to about 100, but high side stayed about the same (70 until compressor kicked on, would raise then drop back down when compressor turned off) and the compressor still briefly engaging. So I'm assuming restriction between low side and compressor? With a new hose to AC manifold can only think it would be the evaporator or could it still be the condensor? Like I said originally I flushed the evaporator and blew air through, didn't seem restricted. I blew air only through the condensor and air came out, but not as much as the evaporator, I'm assuming because the smaller lines.
 
Reply
Old Jun 16, 2017 | 09:33 PM
  #12  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
I turned the can on and opened up the low side. It increased its pressure to about 100, but high side stayed about the same (70 until compressor kicked on, would raise then drop back down when compressor turned off) and the compressor still briefly engaging.
Sounds pretty normal for a system with hardly any refrigerant in it. It takes patience to charge the system from scratch.
 
Reply
Old Jun 17, 2017 | 03:18 PM
  #13  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Originally Posted by projectSHO89
Sounds pretty normal for a system with hardly any refrigerant in it. It takes patience to charge the system from scratch.
Shouldnt the low side drop when the compressor is on though? It was going for about 20 minutes and took less than half a can.
 
Reply
Old Jun 18, 2017 | 07:23 AM
  #14  
projectSHO89's Avatar
projectSHO89
Hotshot
20 Year Member
Photogenic
Photoriffic
Shutterbug
Joined: Jan 2004
Posts: 19,762
Likes: 1,079
From: St Louis
You might have a bad valve on the low side of your manifold connection. You have to turn the valve off from the supply (can) in order to see the low side pressure drop when the compressor engages. Otherwise, what you are seeing is the can's pressure which, due to its proximity to the gauge relative to the suction port of the compressor, is basically right on top of the gauge.

More patience while charging.........

Put the can in a bucket of HOT water, it will speed things up.. unless you feel lucky and want to try tipping the can and sucking in liquid which runs the risk of compressor damage. Those are the only ways you're going to speed up the process.
 
Reply
Old Jun 18, 2017 | 09:38 AM
  #15  
srwven's Avatar
srwven
Thread Starter
|
New User
Joined: Jun 2017
Posts: 9
Likes: 0
Originally Posted by projectSHO89
You might have a bad valve on the low side of your manifold connection. You have to turn the valve off from the supply (can) in order to see the low side pressure drop when the compressor engages. Otherwise, what you are seeing is the can's pressure which, due to its proximity to the gauge relative to the suction port of the compressor, is basically right on top of the gauge.

More patience while charging.........

Put the can in a bucket of HOT water, it will speed things up.. unless you feel lucky and want to try tipping the can and sucking in liquid which runs the risk of compressor damage. Those are the only ways you're going to speed up the process.
yeah even turning the valve from the can off- the low never moves. Got the can in hot water rpms about 1400. Low is staying at 115 psi while high is about 115 and hits 150 momentarily while compresir runs. Rock steady this way for 15 minutes.
 
Reply



All times are GMT -5. The time now is 08:58 PM.

story-0
Rezvani's Latest Post-Apocalytic Monster Is a Ford F-150 Raptor Underneath

Slideshow: Called the Fortress, the 850-horsepower pickup combines Raptor underpinnings with military-inspired features, survival equipment, and a starting price of $285,000.

By Verdad Gallardo | 2026-05-30 18:33:59


VIEW MORE
story-1
Top 10 Most Expensive Ford Trucks Ever Sold on Bring a Trailer

Slideshow: 10 most expensive Ford trucks ever sold on Bring a Trailer.

By Joe Kucinski | 2026-05-27 16:24:34


VIEW MORE
story-2
2027 Ford Super Duty Buyer's Guide (Every Model, Engine, & Package)

Here's everything that has changed for the latest model year.

By Brett Foote | 2026-05-27 16:17:28


VIEW MORE
story-3
Top 10 Ford Truck Tragedies

Slideshow: Top 10 Ford truck tragedies.

By Joe Kucinski | 2026-05-18 19:34:33


VIEW MORE
story-4
AEV FXL Super Duty - the Super Duty Raptor Ford Doesn't Make

And it might be even better than that.

By Brett Foote | 2026-05-18 19:26:42


VIEW MORE
story-5
Lobo Vs Lobo: Proof the F-150 Lobo Should Be Even Lower!

Slideshow: Does lowering an F-150 Lobo RUIN the ride quality?

By Michael S. Palmer | 2026-05-18 19:20:37


VIEW MORE
story-6
Ford's 2001 Explorer Sportsman Concept Looks For a New Home

Slideshow: Ford's bizarre fishing-themed Explorer concept has resurfaced after spending decades largely forgotten.

By Verdad Gallardo | 2026-05-12 18:07:46


VIEW MORE
story-7
10 Best Ford Truck Engines We Miss the Most!

Slideshow: The 10 best Ford truck engines we miss the most.

By Joe Kucinski | 2026-05-12 13:09:47


VIEW MORE
story-8
2026 Shelby F-150 Off-Road: Better Than a Raptor R?

Slideshow: first look at the 810 hp 2026 Shelby F-150 Off-Road!

By Brett Foote | 2026-05-12 12:50:07


VIEW MORE
story-9
2027 Super Duty Carhartt Package First Look: 12 Things You NEED to Know!

Slideshow: Everything You Need to Know about the 2027 Super Duty Carhartt Package!

By Michael S. Palmer | 2026-05-07 17:51:06


VIEW MORE