Originally Posted by blckjck
I am experienced licensed electrician in both industrial and residential applications. I have been an electrician for over 20 years. This sounds like someone trying to explain something without enough knowledge. As said above, they measure the line current going to and from the hot/neutral. If the receptacle is not seeing the same load on both sides of the circuit, it assumes a problem and trips. The history of them not playing well together comes down to wet plugs, faulty wiring, faulty components, undersized GFCI. If all the equipment is in good shape, the resistive load of the heating element will not trip the GFCI.
Completely agree!

Steve
 
  #17  
Old 12-15-2016, 07:32 AM
JayTheCPA's Avatar
JayTheCPA
JayTheCPA is offline
Laughing Gas
Join Date: May 2007
Posts: 793
Likes: 0
Received 29 Likes on 21 Posts
Originally Posted by twigsV10
An electrician gave me his theory which could be bogus, the heating element draws enough current in a loop that it creates a small Magnetic induced electrical charge to the truck.... Just enough to play havoc with a GFCIs outlet?

Does that sound like a possible explanation or just writing something off he couldn't explain?
Last I checked, this only happens with DC systems. The block heater is using AC. Agree with others where it is unlikely that this is causing the GFCI to trip.

As noted, the most likely explanation is that some current is escaping from the system and going elsewhere (not returning back to the outlet). Once the electricity leaves the wiring, it will want to return 'home' which is probably the closest electrical transformer and anybody in the path (however the current decides to get there (which is not always a straight path)) is at risk. The GFCI is tripping as it senses the issue and is doing its job of preventing somebody from getting a shock.

Probably a good idea to get a setup that does not trip the GFCI as, if the electrical leak is in the truck somewhere, aside from a possible shock hazard, it might lead to corrosion depending on where the leak is occurring. Search on stray current electrolysis for more details.

For reference, one of my block heaters continually tripped the GFCI but would work on a standard outlet. The cord and element were clearly recently replaced by the PO when I bought the truck. A new heater element cured the GFCI's tripping.
 
  #18  
Old 12-15-2016, 07:40 AM
bigb56's Avatar
bigb56
bigb56 is offline
Cargo Master

Join Date: Aug 2009
Location: Arizona
Posts: 3,381
Received 219 Likes on 149 Posts
Originally Posted by blckjck
I am experienced licensed electrician in both industrial and residential applications. I have been an electrician for over 20 years. This sounds like someone trying to explain something without enough knowledge. As said above, they measure the line current going to and from the hot/neutral. If the receptacle is not seeing the same load on both sides of the circuit, it assumes a problem and trips. The history of them not playing well together comes down to wet plugs, faulty wiring, faulty components, undersized GFCI. If all the equipment is in good shape, the resistive load of the heating element will not trip the GFCI.
What do you mean by "undersized GFCI"?
 
  #19  
Old 12-15-2016, 11:19 AM
blckjck's Avatar
blckjck
blckjck is offline
Senior User
Join Date: Dec 2012
Location: Ottawa
Posts: 235
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by bigb56
What do you mean by "undersized GFCI"?
Using a 15A GFCI when a 20A or larger would be needed. In this case it should be a 20A circuit with a 20GFCI
 
  #20  
Old 12-15-2016, 11:39 AM
knottyrope's Avatar
knottyrope
knottyrope is offline
Lead Driver
Join Date: Apr 2016
Location: Bahstun
Posts: 5,869
Received 874 Likes on 665 Posts
1 GFCI is bad
2 Salt, water, rust, crud on cord end or the heater on the block
3 your heater is faulty, need a meter to measure resistance on all three terminals


I tripped my GFCI once and my extension cord to camper was in a puddle, son moved it to use his go cart
 
  #21  
Old 12-15-2016, 04:42 PM
Rikster-7700's Avatar
Rikster-7700
Rikster-7700 is offline
Fleet Mechanic
Join Date: Aug 2006
Location: Jacksonville, FL
Posts: 1,465
Likes: 0
Received 16 Likes on 10 Posts
Originally Posted by blckjck
Using a 15A GFCI when a 20A or larger would be needed. In this case it should be a 20A circuit with a 20GFCI
Why would they need a 20A circuit?

Per the code, you can load a circuit up 80%, 80% of a 15A circuit is 12A, which has more than enough capacity to power the less than 8.5A these block heater pull......
 
  #22  
Old 12-15-2016, 05:14 PM
bigb56's Avatar
bigb56
bigb56 is offline
Cargo Master

Join Date: Aug 2009
Location: Arizona
Posts: 3,381
Received 219 Likes on 149 Posts
Originally Posted by blckjck
Using a 15A GFCI when a 20A or larger would be needed. In this case it should be a 20A circuit with a 20GFCI
I don't see why that would make a difference, GFCI receptacles are not over current protection devices, a 15 amp GFCI will happily deliver more than 15 amps till it melts if there is no ground fault.

I agree it's always nice to have a 20 amp circuit but the block heater only uses about 8, so even sizing the circuit at 125% (which isn't even required) a 15 amp circuit would suffice if it were not loaded down with other things.

Some argument could be made that a dedicated 15 amp circuit would be better as it would protect the 13 and 15 amp extension cords that most people use.
 
  #23  
Old 12-15-2016, 05:32 PM
blckjck's Avatar
blckjck
blckjck is offline
Senior User
Join Date: Dec 2012
Location: Ottawa
Posts: 235
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by Rikster-7700
Why would they need a 20A circuit?

Per the code, you can load a circuit up 80%, 80% of a 15A circuit is 12A, which has more than enough capacity to power the less than 8.5A these block heater pull......
You are correct on the loading of a circuit. I recommend 20A circuits for garage outlets even if not required by code because of the typical loads put on them. For specific code requirements, I would need to know more about the whole setting. Age when built, detached or attached garage, etc. For example, frequently detached garages have a single circuit run to them. People add in drill chargers, garage door openers, exterior and interior lighting, etc.

There are some code requirements that do require that circuit in certain circumstances. There are circuits recommended above code requirements based on experience of normal usage.
 
  #24  
Old 12-15-2016, 05:43 PM
FarmingF250's Avatar
FarmingF250
FarmingF250 is offline
Senior User
Join Date: Oct 2011
Location: Nova Scotia, Canada
Posts: 398
Likes: 0
Received 1 Like on 1 Post
I had the same issue, block heater tripped my GFCI, but only when things were wet (think rain or freezing rain then temps fall well below freezing)

Would not kick out normal 15 AMP breaker, just the GFCI.

Found out my cord was no good, was pinched sort of between the fender well and frame, bare wire.

I put a new cord on, no issues with 15 AMP GFCI kicking out again.

Replace cord before cord causes replacement of truck.....
 
  #25  
Old 12-15-2016, 05:58 PM
blckjck's Avatar
blckjck
blckjck is offline
Senior User
Join Date: Dec 2012
Location: Ottawa
Posts: 235
Likes: 0
Received 0 Likes on 0 Posts
In the third post he said one was ordered. I'd say lets see what happens after it's replaced.

Originally Posted by exbxtoy
cool, I've got a new cord ordered and on its way.
 
  #26  
Old 12-15-2016, 09:23 PM
Rikster-7700's Avatar
Rikster-7700
Rikster-7700 is offline
Fleet Mechanic
Join Date: Aug 2006
Location: Jacksonville, FL
Posts: 1,465
Likes: 0
Received 16 Likes on 10 Posts
Originally Posted by blckjck
You are correct on the loading of a circuit. I recommend 20A circuits for garage outlets even if not required by code because of the typical loads put on them. For specific code requirements, I would need to know more about the whole setting. Age when built, detached or attached garage, etc. For example, frequently detached garages have a single circuit run to them. People add in drill chargers, garage door openers, exterior and interior lighting, etc.

There are some code requirements that do require that circuit in certain circumstances. There are circuits recommended above code requirements based on experience of normal usage.
But this is not how you stated it in your post.....

The way your post read, he would have to have a 20A circuit and GFCI installed for his block heater.

I was trying to save the OP some worry and potential spending of unnecessary funds to fix a non-issue.
 
  #27  
Old 12-15-2016, 09:57 PM
Karlow's Avatar
Karlow
Karlow is offline
More Turbo
Join Date: Nov 2016
Location: SGV SoCal
Posts: 545
Likes: 0
Received 2 Likes on 2 Posts
Hey sometimes the info online is worth what you pay for it! I'm to the electrician. He has it right, the GFI senses an imbalance in the Hot and neural lines. I am not sure how well they work without grounds. Your issue is most likely leakage current. My background is in electronics. The block heater is a restive device. Longer power cords, or small gauge wire will result in less power delivered to the heater and lower power consumption. The I^2R losses in the cable will result is lower voltage at the heater. OK
Something is wet, contaminated, or the insulation failing. It's not the cord or and its likely not the GFI. You can likely measure it with your ohm meter.
 
  #28  
Old 12-15-2016, 10:49 PM
twigsV10's Avatar
twigsV10
twigsV10 is offline
Cargo Master
Join Date: Jun 2010
Location: Iowa
Posts: 2,113
Likes: 0
Received 3 Likes on 3 Posts
Originally Posted by Karlow
Hey sometimes the info online is worth what you pay for it! I'm to the electrician. He has it right, the GFI senses an imbalance in the Hot and neural lines. I am not sure how well they work without grounds. Your issue is most likely leakage current. My background is in electronics. The block heater is a restive device. Longer power cords, or small gauge wire will result in less power delivered to the heater and lower power consumption. The I^2R losses in the cable will result is lower voltage at the heater. OK
Something is wet, contaminated, or the insulation failing. It's not the cord or and its likely not the GFI. You can likely measure it with your ohm meter.
I've been doing some reading on this and Karlow nailed how the GFI works and what will actually trip it.... Now that I'm a "self taught Internet expert" on GFI's, what dose the GFI do if you plug in a known good electrical load of similar amperage?.... GFI's do occasionally go bad apparently, it would be a cheep way to test it but the advice above my post is most likely your issue.
 
  #29  
Old 12-16-2016, 02:30 AM
blckjck's Avatar
blckjck
blckjck is offline
Senior User
Join Date: Dec 2012
Location: Ottawa
Posts: 235
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by bigb56
I don't see why that would make a difference, GFCI receptacles are not over current protection devices, a 15 amp GFCI will happily deliver more than 15 amps till it melts if there is no ground fault.
Happily delivering current until something melts is the exact reason for the code to begin with.

While I did not state my advice on a larger circuit was based on usage patterns over what code requires, it does not change my advice.
For the same reason that a 14g extension cord is rated at 15a and could carry the load, but many, including myself, recommend a 12g. It is for safety and long term use.
 
  #30  
Old 12-16-2016, 05:25 AM
Whitey Ford's Avatar
Whitey Ford
Whitey Ford is offline
FTE-Spread The Knowledge

Join Date: Feb 2008
Posts: 2,173
Received 144 Likes on 82 Posts
No need to over think this one! The solution should be quite easy to achieve due to the simplistic nature of the components involved.