You are currently viewing our forums as a guest, which gives you limited access to view most discussions and access our other features. By joining our community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join the Ford-Trucks Forums community today!





 
Reply
 
LinkBack Thread Tools Search this Thread
  #1 (permalink)  
Old 03-02-2006, 06:15 PM
cpe41 cpe41 is offline
Senior User
 
Join Date: Apr 2004
Location: north central Indiana
Posts: 339
cpe41 is starting off with a positive reputation.
Ground Rod....How Deep is Deep Enough?

I'd very much like to install a ground rod for my garage's electrical system (since the previous owner didn't have it done) but I have a concern. I've been told that the ground rod should be driven into the ground to a depth of about 8 feet. Is this basically the minimum depth?

My concern is that the entire area I live in is sitting on fairly shallow limestone, and I very well may hit limestone before getting anywhere near 8 feet. When the PO had a septic tank installed they had to put a small mound of earth over it because they couldn't get it any deeper into the ground.

If I strike rock at, say, 4 or 5 feet will be that be deep enough to be effective, or am I just wasting my time? Is there a standard procedure for a situation of this kind?

Any input appreciated!!
__________________
"Thinking is the hardest work there is, which is probably why so few engage in it"....Henry Ford
Reply With Quote
  #2 (permalink)  
Old 03-02-2006, 06:31 PM
trike1946's Avatar
trike1946 trike1946 is offline
Postmaster
 
Join Date: Apr 2004
Location: NJ where fun comes to die
Posts: 3,982
trike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud oftrike1946 has much to be proud of
I think 8' is standard. You can try using an electric roto hammer that will also just hammer. Just stick it over the rod. It might work.

I can't say if 4' is enough. I am not an electrician. If you hooked it to a water pipe, it would probably be no more than 4' down. Maybe it is enough. I'm sure someone else will come along who knows. Good luck with it.
__________________
Bob
www.oneminutejesus.com
90 E350, 7.3 IDI Diesel, Auto
99 Expedition 4.6, 4x4
2001 F250 SD 7.3, 4x4, CC, LB, SRW, Auto
2001 F350 SD 7.3, 4x4, CC, LB, DRW, Auto
Reply With Quote
  #3 (permalink)  
Old 03-02-2006, 06:49 PM
PupnDuck PupnDuck is offline
Senior User
 
Join Date: Jul 2005
Location: Staten Island, NY
Posts: 385
PupnDuck is gaining momentum as a positive member of FTE.
As a rule, the electrical code only allows ONE ground point in a distribution system and that is located at the main service entrance panel. Even if your garage is detatched from the main building, it relies on the main service entrance ground. Aside from safety issues, multiple ground locations can cause ground loop currents to flow on the grounding conductors in the building. Some electronic equipment will go nuts under those conditions.

Having said that, if you can only get down 4 feet then use multiple rods in a "ground field", put ground rod clamps on the top of the rods and tie them all together with some #4 bare copper wire. It's not how deep you go but rather how much surface area of the grounding rods are in contact with the earth.

But I'd still check your local electrical code first.
Reply With Quote
  #4 (permalink)  
Old 03-02-2006, 10:32 PM
Ford_Six's Avatar
Ford_Six Ford_Six is offline
Super Moderator
 
Join Date: Oct 2002
Location: Washington
Posts: 16,252
Ford_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputationFord_Six has a superb reputation
Code here says a max of 35' from a ground to the furthest point in the system. Also, 4' minimum depth IIRC.
__________________
Jared
Real trucks have the key on the left
FTE Guidelines
Reply With Quote
  #5 (permalink)  
Old 03-03-2006, 08:06 AM
GLR's Avatar
GLR GLR is offline
Post Fiend
 
Join Date: Sep 2003
Location: NY and VA
Posts: 18,345
GLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputationGLR has a superb reputation
An extra ground won't hurt. If there is a damp area, put it there. 8' is the norm, sometimes driving at an angle will help. A post driver helps (used for driving metal posts) hint: put the ground wire clamp on first before driving the rod it is kind of hard to get on if the rod gets "mushroomed".
__________________
[/SIGPIC]George 54 F100, 78 F150, 79 F150, 86 F250, 87 F250 Member #5 Boy you ain't Right Club Official Slackmaster #15
Reply With Quote
  #6 (permalink)  
Old 03-03-2006, 08:23 AM
fefarms fefarms is offline
Elder User
 
Join Date: Sep 2004
Posts: 941
fefarms is gaining momentum as a positive member of FTE.fefarms is gaining momentum as a positive member of FTE.
The NEC requires EACH detached building to have a grounding electrode system. The code encourages the connection of the grounded conductor (the neutral) to the grounding electrode system at only one point (the service disconnect), but there is an exception that allows for a 3 wire connection between buildings in some cases. (It is that arrangement that leads to questions of ground loops, not the presense of multiple grounding electrodes at multiple buildings).

Ground rods are typically driven at an angle if a straight down connection cannot be accomplished. Most of the time you will have to use the "two electrodes 8 feet apart" rule when you do this, because neither ground rod will acheive the 25 ohm resistance requirement. (And even the pair in parallel probably won't, if the soil is dry and the underlying limestone is porous).

Rebar in a footer works a lot better than ground rods, at least in terms of resistance to ground.
Reply With Quote
  #7 (permalink)  
Old 03-04-2006, 08:07 AM
Pro-Street/StateTK's Avatar
Pro-Street/StateTK Pro-Street/StateTK is online now
Posting Guru
 
Join Date: Nov 2003
Location: East Flat Rock NC
Posts: 1,230
Pro-Street/StateTK is gaining momentum as a positive member of FTE.
If you have trouble driving your ground rod, try putting a( big hammer drill)
on the end of the ground rod, it will drive it right though rock every time!







Wally


P.S. I have been in this trade for many years, and use to drive them with
a big hammer untill some one showed me this trick! Let me know how it works
for you!
__________________
"Failure is an opportunity to begin again more intelligently" Henry Ford


My Pro-Street Article
Reply With Quote
  #8 (permalink)  
Old 03-04-2006, 09:45 AM
Dave Sponaugle's Avatar
Dave Sponaugle Dave Sponaugle is offline
Post Fiend
 
Join Date: Nov 2003
Location: Nutter Fort, WV
Posts: 21,266
Dave Sponaugle is a splendid one to beholdDave Sponaugle is a splendid one to beholdDave Sponaugle is a splendid one to beholdDave Sponaugle is a splendid one to beholdDave Sponaugle is a splendid one to beholdDave Sponaugle is a splendid one to beholdDave Sponaugle is a splendid one to behold
Water pipe grounds are not really any good any more.
Most underground water pipes are now plastic which does not conduct electricity.
If you have copper pipe inside the building and use the water piping for a ground, during electrical fault conditions the entire water system becomes electrically hot.
We bond the interior water piping to the ground rods to prevent this from happening which is required in NEC 250-80 (a)
Also any other metal piping that may become energized shall be bonded to ground. NEC 250-80 (b)
Also structural steel buildings shall be bonded to ground. NEC 250-80 (c)

The NEC does require a ground rod for seperate buildings unless the 4 wire system is used to supply the building or if there is only one branch circuit supply to the building.
But the neutral and ground shall not be bonded together. NEC 250-24 (a)

The NEC also allows for the ground rods to be driven at a max angle of 45 degrees.
But it also allows for the ground rods to be installed flat in the bottom of a ditch that is a minimum od 2.5 feet deep.(NEC 250-83 (c)(3) and does call for the upper end of the electrode to be flush or below ground level unless provisions for protection are met.

There is also a grounding ring electrode that can be burried at a depth of not less than 2.5 feet and a minimum of at least 20 feet of #2 bare copper wire to be burried in a ditch. (NEC 250-81(d))
Here in WV we have a lot of rock that makes ground rods inpossible to install in many occasions.
__________________
86 F250 HD 6.9 IDI ATS turbo "not exactly" stock 4x4 T19 BW1345 3.55LS both ends D60 front, 10.25" Sterling rear, ram air, dual stacks.

"I dig dirt"

FTE Guidelines

FTE Moderator IDI diesel forum

WV Chapter Member
Reply With Quote
  #9 (permalink)  
Old 03-04-2006, 10:00 AM
deidoman deidoman is offline
New User
 
Join Date: Feb 2006
Posts: 3
deidoman is starting off with a positive reputation.
deido

drive at a angel put two about 6to8feet apart that will ground the shop
run groung wire continoesly from one rod to next to box
use groun wire bare big strand and the rite nuts to atach wireto rods
Reply With Quote
  #10 (permalink)  
Old 03-05-2006, 05:18 PM
Howdy Howdy is offline
Posting Guru
 
Join Date: Jun 1999
Location: Oregon
Posts: 2,007
Howdy has a good reputation on FTE.Howdy has a good reputation on FTE.Howdy has a good reputation on FTE.
The basic rule as already posted is to drive the rod straight down. If it won't go straight down, drive at 45 deg. If you can't do that, bury horizontal.

I once spent an hour driving a rod down and it seemed to be going fine, other than really slow. I got done and turned around, then tripped on the point of the rod sticking straight up behind me. The rod went down a foot and ended up doing a 180, after hitting rock.

Too many times ground rods are cut at 4', (or less), because someone didn't work at it hard enough. (I'm sure I'm not the only one that's pulled up a two foot ground rod.) Sometimes they just won't go, granite and sandstone are two examples I can think of where they won't. Sometimes the ground just isn't very conductive.

One option is to use a chemical ground. You can buy them, but I've probably built a half dozon of them over the years. Pretty straight forward. I get the cad-weld/wire at the electrical supply and the pipe and bentonite from a pipe supply. I've used rock salt to fill.
http://www.erico.com/products/ChemRod.asp

http://www.pd-engineers.com/hicon.html

Last edited by Howdy; 03-05-2006 at 05:28 PM.
Reply With Quote
Old 03-05-2006, 05:18 PM
Reply

Go Back   Ford Truck Enthusiasts Forums > General > Garage & Workshop

Tags
bury, dakota, deep, drive, electrical, grouding, ground, grounding, horizontal, install, metal, pole, put, rod, south

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On
Forum Jump



All times are GMT -5. The time now is 12:02 AM.


Powered by vBulletin® Version 3.7.5
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.5.2 ©2010, Crawlability, Inc.
Advertising - Terms of Use - Privacy Statement - Jobs
This forum is owned and operated by Internet Brands, Inc., a Delaware corporation. It is not authorized or endorsed by the Ford Motor Company and is not affiliated with the Ford Motor Company or its related companies in any way. FordŽ is a registered trademark of the Ford Motor Company.

vbulletin Admin Backup